Since I'm not a contractor I can't speak for our best practices regarding 
retroactive replacement of missing calc' cards but I can tell you that our firm 
does at least a half-dozen survey/re-calc exercises a year in order to 
establish the performance basis of existing systems.  Exclusively in HPS 
occupancies and at the direction of at least three local FDs (all muni) who 
rank the missing calc' card as a deficiency.

As a design firm, we do a LOT of work on existing systems, especially public 
buildings and institutional properties.  One would think that school districts, 
universities, government agencies, etc. would be better at 
acquiring/archiving/curating as-builts, especially for fire/life safety stuff, 
but they just aren't.   And they're no better at ITM; I'd say rate of 
compliance with CA requirements for NFPA 25 runs 10% or less.   Because plan 
review practices of state AHJ agencies are so strict, we unconditionally have 
to include exacting as-built information on our plans in order to submit and 
permit improvement projects.  If you expand the spectrum of "missing calc 
cards/no as-builts" beyond just inspection-related issues, we probably do 20 
survey and re-calc projects a year.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Wednesday, November 21, 2018 3:25 AM
To: [email protected]
Subject: Calculation Plates

I have been in this industry for 25 years. I believe every company I have ever 
worked at has done a hydraulic calculation when replacing Hydraulic Placards 
due to an inspection deficiency. But yesterday we were having a discussion here 
in the office as to whether or not the calculation was actually required per 
NFPA 25. There is no information on the plate that indicates whether or not the 
system even works ... just what is required. Does your company do a flow test 
and calculation when replacing missing plates? And if so, what happens when you 
discover that the system no longer works as originally designed?