Good afternoon.

Have you asked the local fire marshal’s office if stamped plans are available?  
If first answer is no ask if they’ve been scanned.

Best.

Bruce Verhei 

> On Nov 21, 2018, at 08:09, John Irwin <[email protected]> wrote:
> 
> Now if they could just get this bit of clarification in to the actual code …
>  
>  
>  
> John Irwin
> Quick Response Fire Protection
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Kaiser, Dan (DPS)
> Sent: Wednesday, November 21, 2018 11:06 AM
> To: [email protected]
> Subject: RE: Calculation Plates
>  
> NFPA 25, 2017 edition Handbook:
>  
> <image001.png>
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Steve Leyton
> Sent: Wednesday, November 21, 2018 10:01 AM
> To: [email protected]
> Subject: RE: Calculation Plates
>  
> Correct.  But if the plate is missing and the basis of the system design 
> isn’t known and no as-built drawings are available, which branch on the 
> decision tree do you follow?   If it’s a retail center, it MUST be Ordinary 
> 2, right?   If it’s an office building it has to be Light, unless the shell 
> was designed for Ordinary.  Would that be Ordinary 1 or 2?   If it’s a 
> warehouse … ???   Seems to me that many of these situations involve a lot 
> more than just hanging a new sign, unless you have documented knowledge of 
> the system design or a UL/FM crystal ball.
>  
> SML
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Matthew J Willis
> Sent: Wednesday, November 21, 2018 7:45 AM
> To: [email protected]
> Subject: RE: Calculation Plates
>  
> The answer to your original question is no. NFPA 25 does not require a 
> calculation. It requires the plate.
>  
> The information on the plate drives the fact that you must now do a 
> calculation.
> To be correct, you would have to use the Original flow test, as that was the 
> basis of design. So a new flow test more than likely will not match.
> Getting a new flow test and calc is NFPA 13. Further NFPA 13 involvement 
> could come into play if the calcs no longer work.
> At this point, you will have moved well beyond 25, and should be operating 
> under a different scope.
>  
> If you really wanted to have some fun.., 25 just requires the placard to be 
> in place.
>  
> What if you see a blank one during the inspection? Per 25, you are compliant.
>  
> <image002.jpg>
>  
> R/
> Matt
>  
> Matthew J. Willis, CWBSP
> Design Manager /3-D Specialist
> Rapid Fire Protection Inc.
> 1530 Samco Road
> Rapid City, SD 57702
> Office-605.348.2342
> Direct Line-605.593.5063
> Cell-605.391.2733
> Fax:-605.348.0108
>  
> <image003.png>
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Wayne Cordiner
> Sent: Wednesday, November 21, 2018 7:56 AM
> To: [email protected]
> Subject: Re: Calculation Plates
>  
> John,
>  
> The key to remember here is in NFPA 25 the intent is to inspect, test and 
> maintain a previously approved system. With that in mind the plate you’d be 
> inspecting exists based on the original installation. The data added even to 
> a new plate should reflect that. 
> 
> Regards,
>  
> Wayne T. Cordiner, Jr.
> 917-426-5844
> [email protected]
> 
> On Nov 21, 2018, at 05:24, John Irwin <[email protected]> wrote:
> 
> I have been in this industry for 25 years. I believe every company I have 
> ever worked at has done a hydraulic calculation when replacing Hydraulic 
> Placards due to an inspection deficiency. But yesterday we were having a 
> discussion here in the office as to whether or not the calculation was 
> actually required per NFPA 25. There is no information on the plate that 
> indicates whether or not the system even works … just what is required. Does 
> your company do a flow test and calculation when replacing missing plates? 
> And if so, what happens when you discover that the system no longer works as 
> originally designed?
>  
>  
>  
> John Irwin
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to