Yeah, in simple terms, hydraulic design basis is the discharge criteria. So if you are using QR sprinklers in a portion of a building that has mixed uses – say you’re considering the office area (LH) of an industrial building that also has higher hazard fire areas, you can take the area reduction in the offices where that basis of design is applied.
Steve L. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Thursday, February 28, 2019 7:40 AM To: [email protected] Subject: RE: QR Reduction - Question about wording of code For example, not mixing density/area and residential sprinkler calculations. [MFP_logo_F]<http://www.mfpdesign.com/> Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 [email protected]<mailto:[email protected]> Send large files to us via: https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0> LinkedIn: https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0> “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” From: Sprinklerforum <[email protected]> On Behalf Of Kyle.Montgomery Sent: Thursday, February 28, 2019 8:36 AM To: [email protected] Subject: QR Reduction - Question about wording of code All, What is the intention of the highlighted wording in the code section below: [cid:[email protected]] What is it prohibiting us from doing, if anything? Kyle Montgomery [cid:[email protected]] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 602.763.4736 [email protected]<mailto:[email protected]>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org