Yeah, in simple terms, hydraulic design basis is the discharge criteria.   So 
if you are using QR sprinklers in a portion of a building that has mixed uses – 
say you’re considering the office area (LH) of an industrial building that also 
has higher hazard fire areas, you can take the area reduction in the offices 
where that basis of design is applied.

Steve L.



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Thursday, February 28, 2019 7:40 AM
To: [email protected]
Subject: RE: QR Reduction - Question about wording of code

For example, not mixing density/area and residential sprinkler calculations.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum <[email protected]> On Behalf 
Of Kyle.Montgomery
Sent: Thursday, February 28, 2019 8:36 AM
To: [email protected]
Subject: QR Reduction - Question about wording of code

All,

What is the intention of the highlighted wording in the code section below:


[cid:[email protected]]

What is it prohibiting us from doing, if anything?

Kyle Montgomery
 [cid:[email protected]]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to