We have a state agency that has separate departmental plan reviews for FLS and structural. The structural reviews are like a proctological exam (sorry Ro) and we have seen ALL manner of comments on hanger, bracing and restraint details, from bullseyes to bull****. The most frustrating thing that they regularly do is confuse bracing and restraints and we are constantly pointing out the difference between a HANGER used in a restraint assembly and an BRACE because they impose EQB provisions on our restraint details. Having repeated the same defense of our details over and over like a mental patient, I assure you that there is no prescriptive requirement that anchorage used in a restraint assembly must be listed.
Steve L. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Joe Burtell Sent: Thursday, April 11, 2019 7:02 AM To: [email protected] Subject: Re: Branchline Restraint I question if they need to be listed at all? Other details show staples, #8 self-tapping screws for steel, 1/4" wood eyelets, etc... I can't imagine any of these are listed for EQ zones? Pipe EQ bracing it is clear, they have to be listed but I don't see where fasteners for restraint need to be? Best regards, Joe Burtell, SET, CFPS [Burtell Fire_Small] Phone | Fax | Mobile| Text 406-204-4653<tel:++1-406-204-4653> 116 N. 11th Street | Billings, MT 59101 Email: [email protected]<mailto:[email protected]> Web Site: http://www.burtellfire.com<http://www.burtellfire.com/> “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” NOTICE: The information contained in this e-mail transmission is intended only for use of the individual or entity named above. This e-mail transmission, and any documents, files, previous e-mail transmissions or other information attached to it, may contain confidential information that is legally privileged. If you are not the intended recipient of this e-mail transmission, or the employee or agent responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, dissemination, distribution, copying or other use of this transmission or any of the information contained in or attached to this e-mail is strictly prohibited. If you have received this e-mail transmission in error, please immediately notify us by return e-mail transmission and destroy the original e-mail transmission as well as its attachments without reading or saving it in any manner. Thank you. On Thu, Apr 11, 2019 at 7:47 AM Travis Mack <[email protected]<mailto:[email protected]>> wrote: Are they listed for use in seismic applications? If so, I would believe you are good. If they aren’t listed for use in Seismic applications then not permitted. Travis Mack, CFPS, CWBSP, RME-G, SET 480-505-9271 MFP Design, LLC www.mfpdesign,com Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone On Apr 11, 2019, at 6:44 AM, Joe Burtell <[email protected]<mailto:[email protected]>> wrote: Are there any restrictions on using power-driven studs for branchline restraint? In the diagram, they show what looks like a wedge bolt anchor but I can't see where there is any size or requirements given for fasteners used for branchline restraint. <image.png> Best regards, Joe Burtell, SET, CFPS Error! Filename not specified. Phone | Fax | Mobile| Text 406-204-4653<tel:++1-406-204-4653> 116 N. 11th Street | Billings, MT 59101 Email: [email protected]<mailto:[email protected]> Web Site: http://www.burtellfire.com<http://www.burtellfire.com/> “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” NOTICE: The information contained in this e-mail transmission is intended only for use of the individual or entity named above. This e-mail transmission, and any documents, files, previous e-mail transmissions or other information attached to it, may contain confidential information that is legally privileged. If you are not the intended recipient of this e-mail transmission, or the employee or agent responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, dissemination, distribution, copying or other use of this transmission or any of the information contained in or attached to this e-mail is strictly prohibited. If you have received this e-mail transmission in error, please immediately notify us by return e-mail transmission and destroy the original e-mail transmission as well as its attachments without reading or saving it in any manner. Thank you. <image001.jpg> _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org