Joe, perhaps it's a small difference however I believe that as there is specific guidance on the size and type of staples to be used for attaching restraint wire to a wood joist or rafter, just as there is for using a screw eye, as long as you met the minimums for them they're acceptable.

I understand that in many jurisdictions the annex isn't enforceable however there is guidance.

My disclaimer still applies.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> ***
On 04/11/2019 12:38 PM, Joe Burtell wrote:
A bit of a joke, but what about the power driven staples for wood joists? I doubt the staples are listed either. The detail for a metal deck with concrete fill, which is what I have, says nothing on the size. I would assume it's the same but some more guidance would be helpful. In Montana, we have no jurisdictions that give guidance, it's all per 13.

Best regards,

*Joe Burtell, SET, CFPS*

Burtell Fire_Small

Phone | Fax | Mobile| Text _406-204-4653 <tel:++1-406-204-4653>_

116 N. 11th Street | Billings, MT 59101

Email: [email protected] <mailto:[email protected]>

Web Site: http://www.burtellfire.com <http://www.burtellfire.com/>

*/“/**/The bitterness of poor quality remains long after the sweetness of low price is forgotten./**/”/*

*NOTICE:*The information contained in this e-mail transmission is intended only for use of the individual or entity named above.  This e-mail transmission, and any documents, files, previous e-mail transmissions or other information attached to it, may contain confidential information that is legally privileged.  If you are not the intended recipient of this e-mail transmission, or the employee or agent responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, dissemination, distribution, copying or other use of this transmission or any of the information contained in or attached to this e-mail is strictly prohibited.  If you have received this e-mail transmission in error, please immediately notify us by return e-mail transmission and destroy the original e-mail transmission as well as its attachments without reading or saving it in any manner.  Thank you.



On Thu, Apr 11, 2019 at 11:47 AM Parsley Consulting <[email protected] <mailto:[email protected]>> wrote:

    Joe,

    when in doubt on something like this I pick up the phone and call
    the manufacturer of the powder-driven stud, and ask them if they
    have any information that their product can be used for that purpose.

    I take note that the annex detail A.9.3.6.1(a) calls for a "5/16"
    drill-in expansion anchor minimum" when attaching to cast in place
    concrete, or winding a pigtail into the concrete pre-casting.
    Further down A.9.3.6.1(c) seems to suggest self-tapping screws,
    requiring them to be set prior to placing the concrete.

    However I really believe the answer is in 9.3.7.7, which notes
    that if the Wp is > 0.50 a powder-driven stud can't be used to
    hang the pipe unless they're specifically listed, and to my
    knowledge none are so listed.

    As I am a member of the hanging and bracing committee please see
    the disclaimer below.

    sincerely,
    *Ken Wagoner, SET
    *Parsley Consulting***
    *350 West 9th Avenue, Suite 206
    *Escondido, California 92025
    *****Phone 760-745-6181*
    Visit the website <http://www.parsleyconsulting.com/>

    IMPORTANT NOTICE: This correspondence is not a Formal
    Interpretation issued pursuant to NFPA Regulations. Any opinion
    expressed is the personal opinion of the author and does not
    necessarily represent the official position of the NFPA or its
    Technical Committees. In addition, this correspondence is neither
    intended, nor should it be relied upon, to provide professional
    consultation or services

    It should be noted that the above is my opinion as a member of the
    NFPA Automatic Sprinkler System Hanging and Bracing Committee in
    accordance with the NFPA Regulations Governing Committee Projects
    and should therefore not be considered, nor relied upon, as the
    official position of the NFPA or its Committees

    ***
    On 04/11/2019 7:01 AM, Joe Burtell wrote:
    I question if they need to be listed at all? Other details show
    staples, #8 self-tapping screws for steel, 1/4" wood eyelets,
    etc... I can't imagine any of these are listed for EQ zones? Pipe
    EQ bracing it is clear, they have to be listed but I don't see
    where fasteners for restraint need to be?

    Best regards,

    *Joe Burtell, SET, CFPS*

    Burtell Fire_Small

    Phone | Fax | Mobile| Text _406-204-4653 <tel:++1-406-204-4653>_

    116 N. 11th Street | Billings, MT 59101

    Email: [email protected] <mailto:[email protected]>

    Web Site: http://www.burtellfire.com <http://www.burtellfire.com/>

    */“/**/The bitterness of poor quality remains long after the
    sweetness of low price is forgotten./**/”/*

    *NOTICE:*The information contained in this e-mail transmission is
    intended only for use of the individual or entity named above.
    This e-mail transmission, and any documents, files, previous
    e-mail transmissions or other information attached to it, may
    contain confidential information that is legally privileged. If
    you are not the intended recipient of this e-mail transmission,
    or the employee or agent responsible for delivering it to the
    intended recipient, you are hereby notified that any disclosure,
    dissemination, distribution, copying or other use of this
    transmission or any of the information contained in or attached
    to this e-mail is strictly prohibited.  If you have received this
    e-mail transmission in error, please immediately notify us by
    return e-mail transmission and destroy the original e-mail
    transmission as well as its attachments without reading or saving
    it in any manner.  Thank you.



    On Thu, Apr 11, 2019 at 7:47 AM Travis Mack <[email protected]
    <mailto:[email protected]>> wrote:

        Are they listed for use in seismic applications? If so, I
        would believe you are good. If they aren’t listed for use in
        Seismic applications then not permitted.

        Travis Mack, CFPS, CWBSP, RME-G, SET
        480-505-9271
        MFP Design, LLC
        www.mfpdesign,com <http://www.mfpdesign,com>
        Send large files to MFP Design via:
        https://www.hightail.com/u/MFPDesign

        Sent from my iPhone

        On Apr 11, 2019, at 6:44 AM, Joe Burtell
        <[email protected] <mailto:[email protected]>> wrote:

        Are there any restrictions on using power-driven studs for
        branchline restraint? In the diagram, they show what looks
        like a wedge bolt anchor but I can't see where there is any
        size or requirements given for fasteners used for branchline
        restraint.

        <image.png>

        Best regards,

        *Joe Burtell, SET, CFPS*

        Burtell Fire_Small

        Phone | Fax | Mobile| Text _406-204-4653 <tel:++1-406-204-4653>_

        116 N. 11th Street | Billings, MT 59101

        Email: [email protected] <mailto:[email protected]>

        Web Site: http://www.burtellfire.com
        <http://www.burtellfire.com/>

        */“/**/The bitterness of poor quality remains long after the
        sweetness of low price is forgotten./**/”/*

        *NOTICE:*The information contained in this e-mail
        transmission is intended only for use of the individual or
        entity named above.  This e-mail transmission, and any
        documents, files, previous e-mail transmissions or other
        information attached to it, may contain confidential
        information that is legally privileged. If you are not the
        intended recipient of this e-mail transmission, or the
        employee or agent responsible for delivering it to the
        intended recipient, you are hereby notified that any
        disclosure, dissemination, distribution, copying or other
        use of this transmission or any of the information contained
        in or attached to this e-mail is strictly prohibited. If you
        have received this e-mail transmission in error, please
        immediately notify us by return e-mail transmission and
        destroy the original e-mail transmission as well as its
        attachments without reading or saving it in any
        manner.  Thank you.

        <image001.jpg>
        _______________________________________________
        Sprinklerforum mailing list
        [email protected]
        <mailto:[email protected]>
        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
        _______________________________________________
        Sprinklerforum mailing list
        [email protected]
        <mailto:[email protected]>
        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


    _______________________________________________
    Sprinklerforum mailing list
    [email protected]  
<mailto:[email protected]>
    http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to