This section has been in since 2013 and it has caused some issues.

 

If you are doing room design and meet the requirements for room design then
you are done.

 

If you are doing density / area and you only have 1000 sq ft, where the
required design area would be 1950 sq ft, then as I understand it, you have
to get the flow to a minimum of 195 gpm.  This comes into play on exterior
overhangs and small preaction areas and such like that.  It can be a real
pain.

 

I've also had this come up on paint booths.  The booth is EH2, so 04/2000 or
800 gpm.  If we only have 6 sprinklers, we may only flow 250 gpm, but we
have to add 550 to the cross main to get to 800 gpm.  It really hurts.

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:[email protected]> [email protected]

www.mfpdesign.com

 

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

 

From: Sprinklerforum <[email protected]> On
Behalf Of Steve Leyton
Sent: Monday, April 22, 2019 3:19 PM
To: [email protected]
Subject: Intent of 23.4.4.2.5

 

We have a building with fire rated and secure compartments that are less
than the NFPA 13 minimum design areas so we have calculated those areas
using the room design method where the compartments comply.   Two are fire
protected with preaction sprinklers and 23.4.4.2.5 seems to imply that where
a design area is flowing less than what the density would be across the
minimum required design area, then a "kicker" needs to be added to raise the
flow rate to that figure.   Since we're in Light Hazard and the design area
is only about 1,000 sq. ft., we're flowing about 150 GPM.    But they're
coming after us for 1,500 x 1.3 = 1,950 saying the required flow rate is
195.   If it's LH, we can downward adjust and the demand drops to 117 which
we satisfy.   In all my years I've never had this section thrown at us so
could use any help or opinion regarding exactly how this section should be
applied.

 



 

 