These are evidence and com rooms in a sheriff's station.   Spaces are rated, 
doors are too as well as secure and self-closing.   There's no question the 
compartments are appropriate for room design.

SL





From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Monday, April 22, 2019 3:23 PM
To: [email protected]
Subject: RE: Intent of 23.4.4.2.5

This section has been in since 2013 and it has caused some issues.

If you are doing room design and meet the requirements for room design then you 
are done.

If you are doing density / area and you only have 1000 sq ft, where the 
required design area would be 1950 sq ft, then as I understand it, you have to 
get the flow to a minimum of 195 gpm.  This comes into play on exterior 
overhangs and small preaction areas and such like that.  It can be a real pain.

I've also had this come up on paint booths.  The booth is EH2, so 04/2000 or 
800 gpm.  If we only have 6 sprinklers, we may only flow 250 gpm, but we have 
to add 550 to the cross main to get to 800 gpm.  It really hurts.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."


From: Sprinklerforum <[email protected]> On Behalf 
Of Steve Leyton
Sent: Monday, April 22, 2019 3:19 PM
To: [email protected]
Subject: Intent of 23.4.4.2.5

We have a building with fire rated and secure compartments that are less than 
the NFPA 13 minimum design areas so we have calculated those areas using the 
room design method where the compartments comply.   Two are fire protected with 
preaction sprinklers and 23.4.4.2.5 seems to imply that where a design area is 
flowing less than what the density would be across the minimum required design 
area, then a "kicker" needs to be added to raise the flow rate to that figure.  
 Since we're in Light Hazard and the design area is only about 1,000 sq. ft., 
we're flowing about 150 GPM.    But they're coming after us for 1,500 x 1.3 = 
1,950 saying the required flow rate is 195.   If it's LH, we can downward 
adjust and the demand drops to 117 which we satisfy.   In all my years I've 
never had this section thrown at us so could use any help or opinion regarding 
exactly how this section should be applied.