Last time I had to apply this was under an overhang with storage.
Area/density but I was only flowing 4 heads so I picked up the rest of the
flow at the riser. Not really room design because the adjoining space was
the great outdoors. I would think the area/density requirements would bot
extend to room design.

Nick Maneen
704-791-7789

On Mon, Apr 22, 2019, 6:19 PM Steve Leyton <[email protected]>
wrote:

> We have a building with fire rated and secure compartments that are less
> than the NFPA 13 minimum design areas so we have calculated those areas
> using the room design method where the compartments comply.   Two are fire
> protected with preaction sprinklers and 23.4.4.2.5 seems to imply that
> where a design area is flowing less than what the density would be across
> the minimum required design area, then a “kicker” needs to be added to
> raise the flow rate to that figure.   Since we’re in Light Hazard and the
> design area is only about 1,000 sq. ft., we’re flowing about 150 GPM.
> But they’re coming after us for 1,500 x 1.3 = 1,950 saying the required
> flow rate is 195.   If it’s LH, we can downward adjust and the demand drops
> to 117 which we satisfy.   In all my years I’ve never had this section
> thrown at us so could use any help or opinion regarding exactly how this
> section should be applied.
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to