That was my first thought. No 286F ESFR sprinklers. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Aug 20, 2019, at 7:47 AM, Kyle.Montgomery via Sprinklerforum 
> <[email protected]> wrote:
> 
> Also, how are you complying with the temperature rating when you are that 
> close to a unit heater? Are they making any high temperature ESFRs yet?
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Kyle.Montgomery via Sprinklerforum
> Sent: Tuesday, August 20, 2019 7:40 AM
> To: [email protected]
> Cc: Kyle.Montgomery <[email protected]>; Ed Kramer 
> <[email protected]>
> Subject: RE: [EXTERNAL] ESFR's and unit heaters
>  
> I’m looking at the code again, and you may be right. But I always thought 
> that an obstruction that close to the sprinkler (could you quantify “just 
> below the ESFR deflectors”) would have to meet the rules for “Obstruction at 
> or Near Ceiling”, 8.12.5.1.
>  
> Are we saying that 8.12.5.1 only applies if the obstruction extends above the 
> deflector? I thought that anything in that 0”-31” below the deflector range 
> (shown in Table 8.12.5.1.1) was considered “at or near the ceiling”.
>  
> Kyle Montgomery
>  <image001.png>
> Aero Automatic Sprinkler Co.
> 21605 N. Central Ave.
> Phoenix, AZ 85024
> Direct: 623.580.7820
> Cell: 602.763.4736
> [email protected]
>  
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Ed Kramer via Sprinklerforum
> Sent: Tuesday, August 20, 2019 6:23 AM
> To: [email protected]
> Cc: Ed Kramer <[email protected]>
> Subject: [EXTERNAL] ESFR's and unit heaters
>  
> I’m looking for a bit of a reality check this morning.   Got an ESFR 
> sprinkler system and unit heaters.  In plan view, the heaters are 21” by 40”. 
>  Top of the heaters will be just below the ESFR deflectors, and they will be 
> located at least 1’ horizontally from the ESFR sprinklers.  It appears that 
> NFPA 13 (2013) section 8.12.5.2 applies.
>  
> Subsection (2) reads: “Additional sprinklers shall not be required where the 
> obstruction is 2 ft or less in width and the sprinkler is located 
> horizontally 1 ft or greater from the nearest edge of the obstruction.”
>  
> Since the heater is 2’ or less in its smaller dimension (width), does it 
> matter that the other dimension (length) is greater than 2’?  I say the 
> length is not relevant (unless its long enough to obstruct more than 1 
> sprinkler, then section 8.12.5.3 applies), and subsection (2) allows me to 
> not install a sprinkler below these heaters.
>  
> How do the rest of you interpret this?
>  
> Thanks
> Ed Kramer
> Bamford Fire
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to