Since this is a fun grey area I’m going to sidestep the temperature points the 
member brought up and change this to just a random non heat producing device 
shaped the way you describe.

I would fall back on Annex A.8.12.5.  “….where the sprinkler needs to spray 
under the obstruction or get water both over and under the obstruction….”

In this case I would use Table 8.12.5.1.1 or manufacturers literature to 
determine the water spray pattern.  If the water can go over the obstruction 
uninterrupted, you can probably claim you are within code, although it would 
create quite the shadow.  If I were the building owner’s rep I would ask to 
have the obstruction lowered to be at least 36” below the sprinkler to allow 
full pattern development or shift it over to follow Table 8.12.5.1.1 due to the 
close proximity to sprinkler elevation.  Now, if the water does not have a 
clear trajectory over the top of the obstruction I would say the obstruction is 
too high and falls into the “at or near ceiling” rules and is an obstruction to 
the pattern development.

My opinion.

Thanks,
Sean VG

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack via Sprinklerforum
Sent: Tuesday, August 20, 2019 7:57 AM
To: [email protected]
Cc: Travis Mack <[email protected]>; Kyle.Montgomery 
<[email protected]>; Ed Kramer <[email protected]>
Subject: Re: [EXTERNAL] ESFR's and unit heaters

That was my first thought. No 286F ESFR sprinklers.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=APlWrx5rkikWu_RYi2FJN5KFeDvf1RrjEp-Gr3ahpVY&s=BtBtpxlyL51ns0GAtlAm-qi9Af0cdKAgAE6idFr5LsM&e=>

Sent from my iPhone

On Aug 20, 2019, at 7:47 AM, Kyle.Montgomery via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 wrote:
Also, how are you complying with the temperature rating when you are that close 
to a unit heater? Are they making any high temperature ESFRs yet?

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery via Sprinklerforum
Sent: Tuesday, August 20, 2019 7:40 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Kyle.Montgomery 
<[email protected]<mailto:[email protected]>>; Ed Kramer 
<[email protected]<mailto:[email protected]>>
Subject: RE: [EXTERNAL] ESFR's and unit heaters

I’m looking at the code again, and you may be right. But I always thought that 
an obstruction that close to the sprinkler (could you quantify “just below the 
ESFR deflectors”) would have to meet the rules for “Obstruction at or Near 
Ceiling”, 8.12.5.1.

Are we saying that 8.12.5.1 only applies if the obstruction extends above the 
deflector? I thought that anything in that 0”-31” below the deflector range 
(shown in Table 8.12.5.1.1) was considered “at or near the ceiling”.

Kyle Montgomery
 <image001.png>
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ed Kramer via Sprinklerforum
Sent: Tuesday, August 20, 2019 6:23 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Ed Kramer <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] ESFR's and unit heaters

I’m looking for a bit of a reality check this morning.   Got an ESFR sprinkler 
system and unit heaters.  In plan view, the heaters are 21” by 40”.  Top of the 
heaters will be just below the ESFR deflectors, and they will be located at 
least 1’ horizontally from the ESFR sprinklers.  It appears that NFPA 13 (2013) 
section 8.12.5.2 applies.

Subsection (2) reads: “Additional sprinklers shall not be required where the 
obstruction is 2 ft or less in width and the sprinkler is located horizontally 
1 ft or greater from the nearest edge of the obstruction.”

Since the heater is 2’ or less in its smaller dimension (width), does it matter 
that the other dimension (length) is greater than 2’?  I say the length is not 
relevant (unless its long enough to obstruct more than 1 sprinkler, then 
section 8.12.5.3 applies), and subsection (2) allows me to not install a 
sprinkler below these heaters.

How do the rest of you interpret this?

Thanks
Ed Kramer
Bamford Fire
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=APlWrx5rkikWu_RYi2FJN5KFeDvf1RrjEp-Gr3ahpVY&s=uE1rF6qaAGBJB0o1bLKvPchH81hE8_DBxGR15qIO_WU&e=>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to