214 degree ESFR’s are made

Thar’s what I use

ASCOA back in the day made 286 degree

Mike

Sent from my iPhone

On Aug 20, 2019, at 10:47 AM, Kyle.Montgomery via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 wrote:

Also, how are you complying with the temperature rating when you are that close 
to a unit heater? Are they making any high temperature ESFRs yet?

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery via Sprinklerforum
Sent: Tuesday, August 20, 2019 7:40 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Kyle.Montgomery 
<[email protected]<mailto:[email protected]>>; Ed Kramer 
<[email protected]<mailto:[email protected]>>
Subject: RE: [EXTERNAL] ESFR's and unit heaters

I’m looking at the code again, and you may be right. But I always thought that 
an obstruction that close to the sprinkler (could you quantify “just below the 
ESFR deflectors”) would have to meet the rules for “Obstruction at or Near 
Ceiling”, 8.12.5.1.

Are we saying that 8.12.5.1 only applies if the obstruction extends above the 
deflector? I thought that anything in that 0”-31” below the deflector range 
(shown in Table 8.12.5.1.1) was considered “at or near the ceiling”.

Kyle Montgomery
 <image001.png>
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ed Kramer via Sprinklerforum
Sent: Tuesday, August 20, 2019 6:23 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Ed Kramer <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] ESFR's and unit heaters

I’m looking for a bit of a reality check this morning.   Got an ESFR sprinkler 
system and unit heaters.  In plan view, the heaters are 21” by 40”.  Top of the 
heaters will be just below the ESFR deflectors, and they will be located at 
least 1’ horizontally from the ESFR sprinklers.  It appears that NFPA 13 (2013) 
section 8.12.5.2 applies.

Subsection (2) reads: “Additional sprinklers shall not be required where the 
obstruction is 2 ft or less in width and the sprinkler is located horizontally 
1 ft or greater from the nearest edge of the obstruction.”

Since the heater is 2’ or less in its smaller dimension (width), does it matter 
that the other dimension (length) is greater than 2’?  I say the length is not 
relevant (unless its long enough to obstruct more than 1 sprinkler, then 
section 8.12.5.3 applies), and subsection (2) allows me to not install a 
sprinkler below these heaters.

How do the rest of you interpret this?

Thanks
Ed Kramer
Bamford Fire
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to