FM Global is acceptable also.

Mike

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Parsley Consulting via Sprinklerforum 
<[email protected]>
Sent: Thursday, January 23, 2020 1:26 PM
To: Luis Perea via Sprinklerforum <[email protected]>
Cc: Parsley Consulting <[email protected]>
Subject: Re: Fire Pump NFPA 20

Per the 2019 edition of NFPA 20:
4.7.1* Fire pumps shall be dedicated to and listed for fire protection service.
The identical language was contained in the 2013 and 2016 editions.

It would be a good idea to be familiar with the term "listed" as defined in 
NFPA 20 [also 2019 edition]:
3.2.3* Listed. Equipment, materials, or services included in a list published 
by an organization that is acceptable to the authority having jurisdiction and 
concerned with evaluation of products or services, that maintains periodic 
inspection of production of listed equipment or materials or periodic 
evaluation of services, and whose listing states that either the equipment, 
material, or service meets approprite designated standards or has been tested 
and found suitable for a specified purpose.
So, it appears the short answer is "yes."

sincerely,
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website<http://www.parsleyconsulting.com/>
On 01/23/2020 9:55 AM, Luis Perea via Sprinklerforum wrote:

Hi Everyone

Does The Fire Pump needs to be UL to comply with NFPA 20?



Regards.



[[email protected]]

[Base Firma               RSE]





_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to