You're going to have to get your ammo, your formal interpretations and get
an audience with the little princess's boss - the king.

<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
Virus-free.
www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
<#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>

On Wed, May 20, 2020 at 5:46 PM Rod DiBona via Sprinklerforum <
[email protected]> wrote:

> Maybe look at the contract for dispute resolution. Hopefully push past the
> GC to the owner for  their decision before it goes to mediation etc. Check
> the contract that the GC has with the owner that the sprinkler sub is
> likely tied to. May be a case where this tie helps. At the end of the day
> the owner pays the bill. Would help to understand the GC’s contract. Is it
> a firm fixed? GC plus fee? How is the contingency money handled? Split with
> the GC? 100% back to owner. I would know these things before going this
> route. Good luck, this clearly isn’t right.
>
>
>
>
>
> *Rod DiBona*
>
> *Chief Operating Officer*
>
> *R.F.P.G*
>
> *Rapid Fire Protection Group*
>
> *1530 Samco Road*
>
> *Rapid City, SD 57702*
>
> *Office-605-348-2342*
>
> *Cell- 605-391-3553*
>
> *www.rapidfireinc.com <http://www.rapidfireinc.com/> *
>
>
>
>
>
>
>
>
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
> *Sent:* Wednesday, May 20, 2020 6:36 PM
> *To:* [email protected]
> *Cc:* Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected]>; 'Matt
> Grise' <[email protected]>; 'Rocci 3 Cetani' <[email protected]>
> *Subject:* RE: I-B construction - ABS plumbing piping
>
>
>
> *Seems like we have an AHJ not backing down. We had the reviewing engineer
> for the sprinkler plans write a letter stating that the criteria is in
> compliance with NFPA and that limited quantities of combustibles are
> permitted above the ceiling and still classify it as non-combustible.  This
> is data cabling and waste vent piping that the inspector is drawing a line
> in the sand to provide protection above the ceilings of a large high
> school.  I have been working getting informal interpretations from various
> entities to support our position.*
>
>
>
> *GC is telling sprinkler contractor it was design build so no change
> order.  But, specs say to put sprinklers above ceiling if structure is
> combustible or if steel beams are not fire proofed.  In this project, the
> steel beams are fire proofed.  The contract “intent” drawings call out to
> add sprinklers below stairs if combustible but no where else in the
> project.  There is nothing to indicate sprinklers would be required above
> the ceilings.  A similar school built the next jurisdiction over does not
> have sprinklers above the ceiling.  I have been told other projects in this
> jurisdiction have the same construction and same situation with no
> sprinklers above the ceiling.  One of them referenced is a hospital.  I’m
> sure the data cabling in a hospital is far greater than a high school.*
>
>
>
> *This one is going to get interesting.  And probably pretty ugly.*
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
> *Sent:* Tuesday, May 19, 2020 2:55 PM
> *To:* [email protected]
> *Cc:* Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected]>; 'Matt
> Grise' <[email protected]>; 'Rocci 3 Cetani' <[email protected]>
> *Subject:* RE: I-B construction - ABS plumbing piping
>
>
>
> *Yeah.  That is the conundrum we are in.  *
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Rocci 3 Cetani via Sprinklerforum
> *Sent:* Tuesday, May 19, 2020 2:55 PM
> *To:* [email protected]
> *Cc:* Rocci 3 Cetani <[email protected]>; Matt Grise <[email protected]
> >
> *Subject:* RE: I-B construction - ABS plumbing piping
>
>
>
> Only problem is its vague and I think the committee did that on purpose.
> “minor quantities”  is up for too much interpretation
>
>
>
> *Rocci Cetani III, **CET*
>
> *Senior Designer*
>
> *Water-Based Fire Protections Systems Layout, Nicet Level III*
>
>
>
> *Northern California Fire Protection Services Inc.*
>
> 16840 Joleen Way Bldg. A
>
> Morgan Hill, CA 93037
>
> P-(408) 776-1580 EXT.1010
>
> F-(408) 776-1590
>
>
>
>
>
> [email protected]
>
> www.norcalfire.com
>
>
>
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may
> contain confidential information
>
> belonging to the sender. The information is intended only for the use of
> individual or entity named above. If you are not the intended recipient, or
> the employee or agent responsible to deliver this message to the intended
> recipient, you are hereby notified that any disclosure, copying or taking
> of any action in reliance on the contents of this information is strictly
> prohibited. If you have received this transmission in error, please
> immediately notify us by telephone to arrange for return of the documents.
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Matt Grise via Sprinklerforum
> *Sent:* Tuesday, May 19, 2020 2:52 PM
> *To:* [email protected]
> *Cc:* Matt Grise <[email protected]>
> *Subject:* RE: I-B construction - ABS plumbing piping
>
>
>
> The NFPA13 annex and handbook address this directly.
>
>
>
> NFPA 13 A8.15.1.2.1 “minor quantities of combustible materials such as but
> not limited to cabling, nonmetallic plumbing piping… …should not typically
> be viewed as requiring sprinklers.”
>
>
>
> Matt
>
>
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
> *Sent:* Tuesday, May 19, 2020 4:39 PM
> *To:* [email protected]
> *Cc:* Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected]>
> *Subject:* I-B construction - ABS plumbing piping
>
>
>
> We have a fairly good sized school project. Plumber ran ABS drain piping.
> Electrician has some cabling not in conduit.  Inspector is stating the
> space is now combustible and requires sprinklers above all ceiling areas.
> Has anyone run into this and how was it resolved?
>
>
>
> Drawings and specs do not indicate sprinklers required above ceiling
> spaces.  But the GC is trying to force it down the contractor’s throat if
> it is required and of course it is now holding up the job.
>
>
>
> [image: MFP_logo_F]
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mfpdesign.com%2f&c=E,1,SttrIB9CfFxeMf-7pVmoE0k6_pscjwXmxhUTVEZGWqOrfVv_RPWQIfQUKROuTyjZCm-rOVW8fmWBaZ3y_z2Vqz49Ef7R7Xs_g_pgCVhDupBL3AWdHQD4Ndlu0rU,&typo=1>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> Engineering Manager
>
> MFP Design
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> NEW EXTENSION: 480-505-9271 ext. 700
>
> NEW MOBILE: 480-272-2471
>
> [email protected]
>
> [email protected]
>
> www.mfpdesign.com
> <https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.mfpdesign.com&c=E,1,rsfoiKZVjp0r4kS3D_wBk7ruQf4VYZLmhmkorPry67P4-UrK2tOI7g7FSH3jptAu9GNB7afW3q5NVVj-jOX4ldaCw1oexbBuMbLfKwuiDVE,&typo=1>
>
>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.”*
>
>
>
> *Need/Want a faster way to check material pricing?  Build a material
> quote?  Check availability ?   Searching for an invoice?*
>
> *If you do not already have an account with ferguson.com
> <https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fferguson.com&c=E,1,Z5O9yqH8GnVZs3Rt6WIhxPi09JkGbzPpGDsEUcbDCEYkaSdYqIaBw6uRW-noA4F75taCj-Bhmy_BRHpIanXTELXqOxO646k_2OTofWPXjI7s&typo=1>,
> click *here*
> <https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.ferguson.com%2faccount-registration&c=E,1,Rxm92oOpOtVVVobMNj5wCXGlQvjZ-WMSdx-8dwxbs_Uk8QT97Rso2LVTfX45L9pE3DUz1sb6FlRB0ANrQZSfDpygsb4Cpc5AsKjCHEQOYA,,&typo=1>
>  to register.*
>
> **Have a Ferguson account? Download the Ferguson app for on-the-go access
> to your favorite ferguson.com
> <https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fferguson.com&c=E,1,B2AGScmI6dRZBzd3-wi8IHsusGSAHtakXOYh89-AdF2cYJZynjBcCkI28KGeRNLmmL8cILjb4GxRDYxRLAl_IhZR06UoS3EV2wvNSa6wgqoFS0EftugN3ApI&typo=1>
> features. *Apple iOS devices*
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2ffergusoncommunications.us.newsweaver.com%2fhq7bgesq7f%2f1qtklpp37l9byeftyuoy12%2fexternal%3femail%3dtrue%26a%3d6%26p%3d2591775%26t%3d517003&c=E,1,V3b84AQorYwbjEMlIk66KmAuo0o5Kg0J57bHHcrd2-W2xL9Z8JLSUo22OimfdyM-6PI01x9MYUUAYYACYm40uF-C8qudBoelCSbw2dHB2WfKJOWcyOZq&typo=1>
>  or *Android devices*
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2ffergusoncommunications.us.newsweaver.com%2fhq7bgesq7f%2fn1gewi5ud95byeftyuoy12%2fexternal%3femail%3dtrue%26a%3d6%26p%3d2591775%26t%3d517003&c=E,1,OnnYpoQ9tkU5vobt4BkTVHjpdoFgPxv_s2dPAhk_GBvZJuBOVcvb94auQGiGFkZO_cEq3VXwibspOFsm-d_UhxIINpxM1awviWx2r7k7WL43lpem&typo=1>
> **
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>

<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
Virus-free.
www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
<#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • I-B construction -... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
    • RE: I-B const... Matt Grise via Sprinklerforum
      • RE: I-B c... Rocci 3 Cetani via Sprinklerforum
        • RE: I... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
          • R... Mark.Phelps via Sprinklerforum
            • ... John Drucker via Sprinklerforum
          • R... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
            • ... Rod DiBona via Sprinklerforum
              • ... J H via Sprinklerforum
                • ... Mitchell, Scott via Sprinklerforum
                • ... Travis Mack via Sprinklerforum
                • ... John Drucker via Sprinklerforum
                • ... Travis Mack via Sprinklerforum
                • ... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
                • ... Steve Leyton via Sprinklerforum
                • ... Mitchell, Scott via Sprinklerforum
                • ... Ron Greenman via Sprinklerforum
                • ... BRUCE VERHEI via Sprinklerforum
                • ... Travis Mack via Sprinklerforum

Reply via email to