Exactly. 

Travis Mack, SET
Engineering Manager
MFP Design
[email protected]
[email protected]
480-505-9271 x700
NEW MOBILE : (480) 272-2471

Send large files to us via: https://www.hightail.com/u/MFPDesign



> On May 21, 2020, at 8:45 PM, BRUCE VERHEI via Sprinklerforum 
> <[email protected]> wrote:
> 
> 
> I can’t comment on the situation above the ceiling. Is this project, ‘bidder 
> design’, shorthand for ‘building and systems design is by committee that 
> never meets?
> 
> Best.
> 
> Bruce Verhei
>> On May 21, 2020 at 3:04 PM Ron Greenman via Sprinklerforum 
>> <[email protected]> wrote: 
>> 
>> I'm going to do a stupid thing and pretend to be logical. Does the plan or 
>> spec anywhere call for rated cable in these spaces? Would rated cable reduce 
>> the amount of combustibles enough to obviate the need for the sprinklers? If 
>> either of these hold true then I would think the fight is with the 
>> electrical or alarm or data or some sparky contractor. If adding sprinklers 
>> is just the band-aid for a problem that shouldn't have been allowed to exist 
>> in the first place...  
>> 
>> 
>> Ron Greenman
>> 
>> [email protected] 
>> 
>> 253.576.9700 
>> 
>> The Universe is monstrously indifferent to the presence of man. -Werner 
>> Herzog, screenwriter, film director, author, actor and opera director  
>> (1942-) 
>> 
>> 
>> On Thu, May 21, 2020 at 11:39 AM Mitchell, Scott via Sprinklerforum < 
>> [email protected]> wrote: 
>> It’s one of the unintended consequences of government - at any level.  
>> Unfortunately, the only way to possibly effect improvement is to present 
>> grievances to superiors, then to the city council if necessary.  Good luck 
>> and keep us updated.
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
>> Sent: Thursday, May 21, 2020 1:46 PM
>> To: [email protected]; 'John Drucker' 
>> <[email protected]>
>> Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected]>; Mitchell, 
>> Scott <[email protected]>
>> Subject: RE: [External] Re: I-B construction - ABS plumbing piping
>> 
>>  
>> 
>> Here is the latest on this:
>> 
>>  
>> 
>> Inspector is going to require a data cabling drawing showing all of the 
>> cables dispersed through the school.  He then wants an FPE to sign off that 
>> the amount of cabling is not an issue to trigger the requirement to 
>> sprinkler the concealed space.
>> 
>>  
>> 
>> A bit more was learned.  It is not plenum rated cable and the inspector 
>> wanted plenum rated cable, as I understand it.  So, by forcing sprinklers, 
>> it makes the issue of plenum rated cable go away.  I may not have that fully 
>> understood as it was a 4th party conversation relay.  But, it seems, as 
>> usual, there is a lot more to the story.  The inspector is still really 
>> pushing that the concealed space needs sprinklers.
>> 
>>  
>> 
>> However, if this all goes away as not being required, this is where I feel 
>> that the AHJ should be held for monetary damages they cause.  For all that 
>> have been involved and the man hours dedicated to it, they have cost several 
>> thousands of $$ with zero repercussions.   This is one of my major pet 
>> peeves.
>> 
>>  
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Travis Mack via Sprinklerforum
>> Sent: Thursday, May 21, 2020 6:26 AM
>> To: John Drucker <[email protected]>
>> Cc: Travis Mack <[email protected]>; 
>> [email protected]; Mitchell, Scott 
>> <[email protected]>
>> Subject: Re: [External] Re: I-B construction - ABS plumbing piping
>> 
>>  
>> 
>> The appeal process is in place as well. The problem is the sprinkler 
>> contractor is being threatened with liquidated damages if the inspector 
>> won’t allow cover today in a particular area. 
>> 
>>  
>> 
>> This is where badge heavy inspectors become a real problem. The inspector 
>> states he will accept only 3 options:
>> 
>>  
>> 
>> 1 - there can only be a single ABS pipe and no other combustibles in the 
>> area. 
>> 
>>  
>> 
>> 2 - He will allow ABS and data cabling if a FPE will provide the maximum 
>> quantities of combustibles in the space since NFPA is vague. He wants a way 
>> to quantify the quantities. The contractor is arguing it is impossible for 
>> the sprinkler to police the quantities of other trades and to quantify them. 
>> 
>>  
>> 
>> 3 - provide full upright protection across the 280k sq ft space above the 
>> ceiling, including redesign and calculations.  Beams are about 10’ on center 
>> and 28” deep plus fireproofing. So, the best they can get is 150 sq ft per 
>> sprinkler. It will likely average out at 100 or so. The GC is trying to 
>> state the sprinkler contractor would have to absorb the added costs. 
>> 
>>  
>> 
>> All of this for some ABS vent piping and typical data cabling you see in a 
>> school. 
>> 
>>  
>> 
>> I have a feeling this one is going to get pretty ugly. 
>> 
>> Travis Mack, SET
>> 
>> Engineering Manager
>> 
>> MFP Design
>> 
>> [email protected]
>> 
>> [email protected]
>> 
>> 480-505-9271 x700
>> 
>> NEW MOBILE : (480) 272-2471
>> 
>>  
>> 
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>> 
>>  
>> 
>>  
>> 
>>  
>> 
>> On May 21, 2020, at 6:15 AM, John Drucker <[email protected]> wrote:
>> 
>>  
>> 
>> Or as in many jurisdictions, file an appeal.  
>> 
>>  
>> 
>> John Drucker
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> on 
>> behalf of Travis Mack via Sprinklerforum 
>> <[email protected]>
>> Sent: Thursday, May 21, 2020 09:01
>> To: [email protected]
>> Cc: Travis Mack; Mitchell, Scott
>> Subject: Re: [External] Re: I-B construction - ABS plumbing piping
>> 
>>  
>> 
>> That is processing 👍🏼
>> 
>>  
>> 
>> Travis Mack, SET
>> 
>> Engineering Manager
>> 
>> MFP Design
>> 
>> [email protected]
>> 
>> [email protected]
>> 
>> 480-505-9271 x700
>> 
>> NEW MOBILE : (480) 272-2471
>> 
>>  
>> 
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>> 
>>  
>> 
>>  
>> 
>>  
>> 
>> On May 21, 2020, at 6:00 AM, Mitchell, Scott via Sprinklerforum 
>> <[email protected]> wrote:
>> 
>>  
>> 
>> You might try an informal interpretation from John August Denhart and 
>> company.  J
>> 
>>  
>> 
>> Scott Mitchell
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of J H via Sprinklerforum
>> Sent: Wednesday, May 20, 2020 11:43 PM
>> To: [email protected]
>> Cc: J H <[email protected]>
>> Subject: [External] Re: I-B construction - ABS plumbing piping
>> 
>>  
>> 
>> You're going to have to get your ammo, your formal interpretations and get 
>> an audience with the little princess's boss - the king
>> 
>>  
>> 
>> <image002.jpg>
>> 
>> Virus-free. www.avast.com
>> 
>>  
>> 
>> On Wed, May 20, 2020 at 5:46 PM Rod DiBona via Sprinklerforum 
>> <[email protected]> wrote:
>> 
>> Maybe look at the contract for dispute resolution. Hopefully push past the 
>> GC to the owner for  their decision before it goes to mediation etc. Check 
>> the contract that the GC has with the owner that the sprinkler sub is likely 
>> tied to. May be a case where this tie helps. At the end of the day the owner 
>> pays the bill. Would help to understand the GC’s contract. Is it a firm 
>> fixed? GC plus fee? How is the contingency money handled? Split with the GC? 
>> 100% back to owner. I would know these things before going this route. Good 
>> luck, this clearly isn’t right.  
>> 
>>  
>> 
>>  
>> 
>> Rod DiBona
>> 
>> Chief Operating Officer
>> 
>> R.F.P.G
>> 
>> Rapid Fire Protection Group
>> 
>> 1530 Samco Road
>> 
>> Rapid City, SD 57702
>> 
>> Office-605-348-2342
>> 
>> Cell- 605-391-3553
>> 
>> www.rapidfireinc.com
>> 
>>  
>> 
>> <image001.jpg>
>> 
>> <image002.jpg>
>> 
>>  
>> 
>>  
>> 
>>  
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
>> Sent: Wednesday, May 20, 2020 6:36 PM
>> To: [email protected]
>> Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected]>; 'Matt Grise' 
>> <[email protected]>; 'Rocci 3 Cetani' <[email protected]>
>> Subject: RE: I-B construction - ABS plumbing piping
>> 
>>  
>> 
>> Seems like we have an AHJ not backing down. We had the reviewing engineer 
>> for the sprinkler plans write a letter stating that the criteria is in 
>> compliance with NFPA and that limited quantities of combustibles are 
>> permitted above the ceiling and still classify it as non-combustible.  This 
>> is data cabling and waste vent piping that the inspector is drawing a line 
>> in the sand to provide protection above the ceilings of a large high school. 
>>  I have been working getting informal interpretations from various entities 
>> to support our position.
>> 
>>  
>> 
>> GC is telling sprinkler contractor it was design build so no change order.  
>> But, specs say to put sprinklers above ceiling if structure is combustible 
>> or if steel beams are not fire proofed.  In this project, the steel beams 
>> are fire proofed.  The contract “intent” drawings call out to add sprinklers 
>> below stairs if combustible but no where else in the project.  There is 
>> nothing to indicate sprinklers would be required above the ceilings.  A 
>> similar school built the next jurisdiction over does not have sprinklers 
>> above the ceiling.  I have been told other projects in this jurisdiction 
>> have the same construction and same situation with no sprinklers above the 
>> ceiling.  One of them referenced is a hospital.  I’m sure the data cabling 
>> in a hospital is far greater than a high school.
>> 
>>  
>> 
>> This one is going to get interesting.  And probably pretty ugly.
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
>> Sent: Tuesday, May 19, 2020 2:55 PM
>> To: [email protected]
>> Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected]>; 'Matt Grise' 
>> <[email protected]>; 'Rocci 3 Cetani' <[email protected]>
>> Subject: RE: I-B construction - ABS plumbing piping
>> 
>>  
>> 
>> Yeah.  That is the conundrum we are in. 
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Rocci 3 Cetani via Sprinklerforum
>> Sent: Tuesday, May 19, 2020 2:55 PM
>> To: [email protected]
>> Cc: Rocci 3 Cetani <[email protected]>; Matt Grise <[email protected]>
>> Subject: RE: I-B construction - ABS plumbing piping
>> 
>>  
>> 
>> Only problem is its vague and I think the committee did that on purpose. 
>> “minor quantities”  is up for too much interpretation
>> 
>>  
>> 
>> Rocci Cetani III, CET
>> 
>> Senior Designer
>> 
>> Water-Based Fire Protections Systems Layout, Nicet Level III
>> 
>>  
>> 
>> Northern California Fire Protection Services Inc.
>> 
>> 16840 Joleen Way Bldg. A
>> 
>> Morgan Hill, CA 93037
>> 
>> P-(408) 776-1580 EXT.1010
>> 
>> F-(408) 776-1590
>> 
>>  
>> 
>>  
>> 
>> [email protected]
>> 
>> www.norcalfire.com
>> 
>>  
>> 
>> CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
>> contain confidential information
>> 
>> belonging to the sender. The information is intended only for the use of 
>> individual or entity named above. If you are not the intended recipient, or 
>> the employee or agent responsible to deliver this message to the intended 
>> recipient, you are hereby notified that any disclosure, copying or taking of 
>> any action in reliance on the contents of this information is strictly 
>> prohibited. If you have received this transmission in error, please 
>> immediately notify us by telephone to arrange for return of the documents.
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Matt Grise via Sprinklerforum
>> Sent: Tuesday, May 19, 2020 2:52 PM
>> To: [email protected]
>> Cc: Matt Grise <[email protected]>
>> Subject: RE: I-B construction - ABS plumbing piping
>> 
>>  
>> 
>> The NFPA13 annex and handbook address this directly.
>> 
>>  
>> 
>> NFPA 13 A8.15.1.2.1 “minor quantities of combustible materials such as but 
>> not limited to cabling, nonmetallic plumbing piping… …should not typically 
>> be viewed as requiring sprinklers.”
>> 
>>  
>> 
>> Matt
>> 
>>  
>> 
>>  
>> 
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
>> Sent: Tuesday, May 19, 2020 4:39 PM
>> To: [email protected]
>> Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected]>
>> Subject: I-B construction - ABS plumbing piping
>> 
>>  
>> 
>> We have a fairly good sized school project. Plumber ran ABS drain piping.  
>> Electrician has some cabling not in conduit.  Inspector is stating the space 
>> is now combustible and requires sprinklers above all ceiling areas.  Has 
>> anyone run into this and how was it resolved?
>> 
>>  
>> 
>> Drawings and specs do not indicate sprinklers required above ceiling spaces. 
>>  But the GC is trying to force it down the contractor’s throat if it is 
>> required and of course it is now holding up the job.
>> 
>>  
>> 
>> <image003.jpg>
>> 
>>  
>> 
>> Travis Mack, CFPS, CWBSP, RME-G, SET
>> 
>> Engineering Manager
>> 
>> MFP Design
>> 
>> 3356 E Vallejo Ct
>> 
>> Gilbert, AZ 85298
>> 
>> NEW EXTENSION: 480-505-9271 ext. 700
>> 
>> NEW MOBILE: 480-272-2471
>> 
>> [email protected]
>> 
>> [email protected]
>> 
>> www.mfpdesign.com
>> 
>>  
>> 
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>> 
>> LinkedIn: https://www.linkedin.com/in/travismack
>> 
>>  
>> 
>> “The bitterness of poor quality remains long after the sweetness of low 
>> price is forgotten.”
>> 
>>  
>> 
>> Need/Want a faster way to check material pricing?  Build a material quote?  
>> Check availability ?   Searching for an invoice?
>> 
>> *If you do not already have an account with ferguson.com, click here to 
>> register.*
>> 
>> **Have a Ferguson account? Download the Ferguson app for on-the-go access to 
>> your favorite ferguson.com features. Apple iOS devices or Android devices**
>> 
>>  
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>>  
>> 
>> <image002.jpg>
>> 
>> Virus-free. www.avast.com
>> 
>>  
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________ 
>> Sprinklerforum mailing list 
>> [email protected] 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
>> _______________________________________________ 
>> Sprinklerforum mailing list 
>> [email protected] 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> 
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org