Ahhh Nuts,  coordination, project management, collaboration, ........mere words 
on paper.  The design work we get is awful.  I’m working on one right now for 
permits where the sprinkler plans call for a pump, ok so back to the architect 
for a pump room,  where’s the electrical, ok so back to the engineer,   where’s 
the sprinkler supervision and fire alarm,  ok so this is 
pending.........building departments should never ever be caught in this mess.  
 And that’s just me the building and plumbing guys is also going around.   Add 
in the convoluted subjective code stuff.....somethings gotta give.  Your above 
ceiling construction issues most likely trace back to a similar circumstance

John Drucker
Fire and Electrical Code Official
New Jersey.

John Drucker

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Travis Mack via Sprinklerforum <[email protected]>
Sent: Thursday, May 21, 2020 23:46
To: BRUCE VERHEI; [email protected]
Cc: Travis Mack
Subject: Re: [External] Re: I-B construction - ABS plumbing piping

Exactly.

Travis Mack, SET
Engineering Manager
MFP Design
[email protected]
[email protected]
480-505-9271 x700
NEW MOBILE : (480) 272-2471

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>



On May 21, 2020, at 8:45 PM, BRUCE VERHEI via Sprinklerforum 
<[email protected]> wrote:


I can’t comment on the situation above the ceiling. Is this project, ‘bidder 
design’, shorthand for ‘building and systems design is by committee that never 
meets?

Best.

Bruce Verhei
On May 21, 2020 at 3:04 PM Ron Greenman via Sprinklerforum 
<[email protected]> wrote:

I'm going to do a stupid thing and pretend to be logical. Does the plan or spec 
anywhere call for rated cable in these spaces? Would rated cable reduce the 
amount of combustibles enough to obviate the need for the sprinklers? If either 
of these hold true then I would think the fight is with the electrical or alarm 
or data or some sparky contractor. If adding sprinklers is just the band-aid 
for a problem that shouldn't have been allowed to exist in the first place...


Ron Greenman

[email protected]<mailto:[email protected]>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director  (1942-)


On Thu, May 21, 2020 at 11:39 AM Mitchell, Scott via Sprinklerforum < 
[email protected]<mailto:[email protected]>>
 wrote:

It’s one of the unintended consequences of government - at any level.  
Unfortunately, the only way to possibly effect improvement is to present 
grievances to superiors, then to the city council if necessary.  Good luck and 
keep us updated



From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Thursday, May 21, 2020 1:46 PM
To: 
[email protected]<mailto:[email protected]>;
 'John Drucker' <[email protected]<mailto:[email protected]>>
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
<[email protected]<mailto:[email protected]>>; Mitchell, Scott 
<[email protected]<mailto:[email protected]>>
Subject: RE: [External] Re: I-B construction - ABS plumbing piping



Here is the latest on this:



Inspector is going to require a data cabling drawing showing all of the cables 
dispersed through the school.  He then wants an FPE to sign off that the amount 
of cabling is not an issue to trigger the requirement to sprinkler the 
concealed space.



A bit more was learned.  It is not plenum rated cable and the inspector wanted 
plenum rated cable, as I understand it.  So, by forcing sprinklers, it makes 
the issue of plenum rated cable go away.  I may not have that fully understood 
as it was a 4th party conversation relay.  But, it seems, as usual, there is a 
lot more to the story.  The inspector is still really pushing that the 
concealed space needs sprinklers.



However, if this all goes away as not being required, this is where I feel that 
the AHJ should be held for monetary damages they cause.  For all that have been 
involved and the man hours dedicated to it, they have cost several thousands of 
$$ with zero repercussions.   This is one of my major pet peeves.





From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Thursday, May 21, 2020 6:26 AM
To: John Drucker <[email protected]<mailto:[email protected]>>
Cc: Travis Mack <[email protected]<mailto:[email protected]>>; 
[email protected]<mailto:[email protected]>;
 Mitchell, Scott <[email protected]<mailto:[email protected]>>
Subject: Re: [External] Re: I-B construction - ABS plumbing piping



The appeal process is in place as well. The problem is the sprinkler contractor 
is being threatened with liquidated damages if the inspector won’t allow cover 
today in a particular area.



This is where badge heavy inspectors become a real problem. The inspector 
states he will accept only 3 options:



1 - there can only be a single ABS pipe and no other combustibles in the area.



2 - He will allow ABS and data cabling if a FPE will provide the maximum 
quantities of combustibles in the space since NFPA is vague. He wants a way to 
quantify the quantities. The contractor is arguing it is impossible for the 
sprinkler to police the quantities of other trades and to quantify them.



3 - provide full upright protection across the 280k sq ft space above the 
ceiling, including redesign and calculations.  Beams are about 10’ on center 
and 28” deep plus fireproofing. So, the best they can get is 150 sq ft per 
sprinkler. It will likely average out at 100 or so. The GC is trying to state 
the sprinkler contractor would have to absorb the added costs.



All of this for some ABS vent piping and typical data cabling you see in a 
school.



I have a feeling this one is going to get pretty ugly.

Travis Mack, SET

Engineering Manager

MFP Design

[email protected]<mailto:[email protected]>

[email protected]<mailto:[email protected]>

480-505-9271 x700

NEW MOBILE : (480) 272-2471



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>







On May 21, 2020, at 6:15 AM, John Drucker 
<[email protected]<mailto:[email protected]>> wrote:



Or as in many jurisdictions, file an appeal.



John Drucker



________________________________

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Travis Mack via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Sent: Thursday, May 21, 2020 09:01
To: 
[email protected]<mailto:[email protected]>
Cc: Travis Mack; Mitchell, Scott
Subject: Re: [External] Re: I-B construction - ABS plumbing piping



That is processing 👍🏼



Travis Mack, SET

Engineering Manager

MFP Design

[email protected]<mailto:[email protected]>

[email protected]<mailto:[email protected]>

480-505-9271 x700

NEW MOBILE : (480) 272-2471



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>







On May 21, 2020, at 6:00 AM, Mitchell, Scott via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 wrote:



You might try an informal interpretation from John August Denhart and company.  
☺



Scott Mitchell



From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of J H via Sprinklerforum
Sent: Wednesday, May 20, 2020 11:43 PM
To: 
[email protected]<mailto:[email protected]>
Cc: J H <[email protected]<mailto:[email protected]>>
Subject: [External] Re: I-B construction - ABS plumbing piping



You're going to have to get your ammo, your formal interpretations and get an 
audience with the little princess's boss - the king



<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>

<image002.jpg>

Virus-free. 
www.avast.com<https://wwwavast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>



On Wed, May 20, 2020 at 5:46 PM Rod DiBona via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 wrote:

Maybe look at the contract for dispute resolution. Hopefully push past the GC 
to the owner for  their decision before it goes to mediation etc. Check the 
contract that the GC has with the owner that the sprinkler sub is likely tied 
to. May be a case where this tie helps. At the end of the day the owner pays 
the bill. Would help to understand the GC’s contract. Is it a firm fixed? GC 
plus fee? How is the contingency money handled? Split with the GC? 100% back to 
owner. I would know these things before going this route. Good luck, this 
clearly isn’t right.





Rod DiBona

Chief Operating Officer

R.F.P.G

Rapid Fire Protection Group

1530 Samco Road

Rapid City, SD 57702

Office-605-348-2342

Cell- 605-391-3553

www.rapidfireinc.com<http://www.rapidfireinccom/>



<image001.jpg>

<image002.jpg>









From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, May 20, 2020 6:36 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
<[email protected]<mailto:[email protected]>>; 'Matt Grise' 
<[email protected]<mailto:[email protected]>>; 'Rocci 3 Cetani' 
<[email protected]<mailto:[email protected]>>
Subject: RE: I-B construction - ABS plumbing piping



Seems like we have an AHJ not backing down. We had the reviewing engineer for 
the sprinkler plans write a letter stating that the criteria is in compliance 
with NFPA and that limited quantities of combustibles are permitted above the 
ceiling and still classify it as non-combustible.  This is data cabling and 
waste vent piping that the inspector is drawing a line in the sand to provide 
protection above the ceilings of a large high school.  I have been working 
getting informal interpretations from various entities to support our position.



GC is telling sprinkler contractor it was design build so no change order.  
But, specs say to put sprinklers above ceiling if structure is combustible or 
if steel beams are not fire proofed.  In this project, the steel beams are fire 
proofed.  The contract “intent” drawings call out to add sprinklers below 
stairs if combustible but no where else in the project.  There is nothing to 
indicate sprinklers would be required above the ceilings.  A similar school 
built the next jurisdiction over does not have sprinklers above the ceiling.  I 
have been told other projects in this jurisdiction have the same construction 
and same situation with no sprinklers above the ceiling.  One of them 
referenced is a hospital.  I’m sure the data cabling in a hospital is far 
greater than a high school.



This one is going to get interesting.  And probably pretty ugly



From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Tuesday, May 19, 2020 2:55 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
<[email protected]<mailto:[email protected]>>; 'Matt Grise' 
<[email protected]<mailto:[email protected]>>; 'Rocci 3 Cetani' 
<[email protected]<mailto:[email protected]>>
Subject: RE: I-B construction - ABS plumbing piping



Yeah.  That is the conundrum we are in.



From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Rocci 3 Cetani via Sprinklerforum
Sent: Tuesday, May 19, 2020 2:55 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Rocci 3 Cetani <[email protected]<mailto:[email protected]>>; Matt 
Grise <[email protected]<mailto:[email protected]>>
Subject: RE: I-B construction - ABS plumbing piping



Only problem is its vague and I think the committee did that on purpose. “minor 
quantities”  is up for too much interpretation



Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III



Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.1010

F-(408) 776-1590





[email protected]<mailto:[email protected]>

www.norcalfire.com<http://www.norcalfire.com/>



CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information

belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.



From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Matt Grise via Sprinklerforum
Sent: Tuesday, May 19, 2020 2:52 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Matt Grise <[email protected]<mailto:[email protected]>>
Subject: RE: I-B construction - ABS plumbing piping



The NFPA13 annex and handbook address this directly.



NFPA 13 A8.15.1.2.1 “minor quantities of combustible materials such as but not 
limited to cabling, nonmetallic plumbing piping… …should not typically be 
viewed as requiring sprinklers.”



Matt





From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Tuesday, May 19, 2020 4:39 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
<[email protected]<mailto:[email protected]>>
Subject: I-B construction - ABS plumbing piping



We have a fairly good sized school project. Plumber ran ABS drain piping.  
Electrician has some cabling not in conduit.  Inspector is stating the space is 
now combustible and requires sprinklers above all ceiling areas.  Has anyone 
run into this and how was it resolved?



Drawings and specs do not indicate sprinklers required above ceiling spaces.  
But the GC is trying to force it down the contractor’s throat if it is required 
and of course it is now holding up the job.



<image003.jpg><https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mfpdesign.com%2f&c=E,1,SttrIB9CfFxeMf-7pVmoE0k6_pscjwXmxhUTVEZGWqOrfVv_RPWQIfQUKROuTyjZCm-rOVW8fmWBaZ3y_z2Vqz49Ef7R7Xs_g_pgCVhDupBL3AWdHQD4Ndlu0rU,&typo=1>



Travis Mack, CFPS, CWBSP, RME-G, SET

Engineering Manager

MFP Design

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

NEW MOBILE: 480-272-2471

[email protected]<mailto:[email protected]>

[email protected]<mailto:[email protected]>

www.mfpdesign.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.mfpdesign.com&c=E,1,rsfoiKZVjp0r4kS3D_wBk7ruQf4VYZLmhmkorPry67P4-UrK2tOI7g7FSH3jptAu9GNB7afW3q5NVVj-jOX4ldaCw1oexbBuMbLfKwuiDVE,&typo=1>



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>



“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”



Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?

*If you do not already have an account with 
ferguson.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fferguson.com&c=E,1,Z5O9yqH8GnVZs3Rt6WIhxPi09JkGbzPpGDsEUcbDCEYkaSdYqIaBw6uRW-noA4F75taCj-Bhmy_BRHpIanXTELXqOxO646k_2OTofWPXjI7s&typo=1>,
 click 
here<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.ferguson.com%2faccount-registration&c=E,1,Rxm92oOpOtVVVobMNj5wCXGlQvjZ-WMSdx-8dwxbs_Uk8QT97Rso2LVTfX45L9pE3DUz1sb6FlRB0ANrQZSfDpygsb4Cpc5AsKjCHEQOYA,,&typo=1>
 to register.*

**Have a Ferguson account? Download the Ferguson app for on-the-go access to 
your favorite 
ferguson.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fferguson.com&c=E,1,B2AGScmI6dRZBzd3-wi8IHsusGSAHtakXOYh89-AdF2cYJZynjBcCkI28KGeRNLmmL8cILjb4GxRDYxRLAl_IhZR06UoS3EV2wvNSa6wgqoFS0EftugN3ApI&typo=1>
 features. Apple iOS 
devices<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2ffergusoncommunications.us.newsweaver.com%2fhq7bgesq7f%2f1qtklpp37l9byeftyuoy12%2fexternal%3femail%3dtrue%26a%3d6%26p%3d2591775%26t%3d517003&c=E,1,V3b84AQorYwbjEMlIk66KmAuo0o5Kg0J57bHHcrd2-W2xL9Z8JLSUo22OimfdyM-6PI01x9MYUUAYYACYm40uF-C8qudBoelCSbw2dHB2WfKJOWcyOZq&typo=1>
 or Android 
devices<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2ffergusoncommunications.us.newsweaver.com%2fhq7bgesq7f%2fn1gewi5ud95byeftyuoy12%2fexternal%3femail%3dtrue%26a%3d6%26p%3d2591775%26t%3d517003&c=E,1,OnnYpoQ9tkU5vobt4BkTVHjpdoFgPxv_s2dPAhk_GBvZJuBOVcvb94auQGiGFkZO_cEq3VXwibspOFsm-d_UhxIINpxM1awviWx2r7k7WL43lpem&typo=1>**



_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>

<image002.jpg>

Virus-free. 
www.avast.com<https://wwwavast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>



_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to