In this day and age of digital everything it’s surprising that someone doesn’t 
sell a hydro pump set up with any auto shut off, with a standard 205 psig and 
select, with relief at 210 psig. 

Best.

Bruce V.
> On 04/16/2021 4:12 PM Tom Duross via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
>  
> Thanks Matt.
> I also got a tip to buy/rent a large pressure washer today.  I'm thinking
> this little 3/4 hp Reed is not going to do it at all.
> I did 800' of 8" ductile today, flush, pressure test, forward flow test.  It
> was 32° and snowing just north of Boston at this University.  Took me 1 hr.
> 10 mins. to pump from 66 to 210.  It held fine but I got to thinking (during
> the 2 hr. rest) that just one of these roadway #502 standpipes are 2300'
> long, all 6" except the risers to the gated wye's and air releases every
> 275' and a drop at each end to a 5" Storz and Vic717R.  I doubt I will have
> much free use of the local FD's pumper, I'm told they're not too happy about
> having to do it.  Kind of like the power company putting panels on your roof
> with no rental but have to provide access.  I'll know more next week.  I'm
> writing up test procedures over the weekend to coincide with  #25 and #502,
> and then some.  Haven't done a roadway system in a few years but it looks
> like 5 AM Saturdays for 5 weeks and the bridges are in use, never closed.  I
> gotta see what's out there for rentals.  Going to use Scott's math to see
> what the street fill will take and then the pressure pump-up.  Thanks Scott,
> we'll do pizza again next time your in town.  Hey Scott, I got 10 minutes to
> show a full stream after pulling the trigger on 150#, starting empty,  think
> I'll make it?
> 
> 
> It might not be a real fast approach, but is there some reason that you
> could not have the standpipes pressurized to 200 psi before the inspector
> arrives? We frequently hook up the test pump and then go about
> moving-off/cleaning up until the little pump reaches the pressure. If you
> don't have enough time to get it pumped before the inspector comes (ask for
> an afternoon appointment?) - we have pumped the systems up partially the day
> before so that they are close to the test pressure but not excessively high.
> Then you don't need as long to top them off. Just be sure you have a
> helper/day laborer keep an eye on the gauge!
> 
> I suppose it would just depend on how much big pump rental or nitrogen tanks
> would cost VS a couple hours of small pump babysitting.
> 
> Matt 
> 
> 
> Fill completely with water; then connect a high-pressure nitrogen cylinder
> and quickly jack the system to 200 psi. Have seen this method used before to
> test large warehouse systems where it is very time consuming to pressurize
> the system(s).
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to