Fill completely with water; then connect a high-pressure nitrogen cylinder and 
quickly jack the system to 200 psi. Have seen this method used before to test 
large warehouse systems where it is very time consuming to pressurize the 
system(s).



This information is provided as a courtesy only. Design and installation 
requirements for fire protection systems must be independently evaluated by 
qualified design professionals and approved by all authorities having 
jurisdiction.





Cary Webber CFPS Director, Technical Services

Reliable Automatic Sprinkler Co., Inc.

1470 Smith Grove Road, Liberty, SC  29657

Tel: 864-843-5161







-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Tom Duross via Sprinklerforum
Sent: Thursday, April 15, 2021 6:59 PM
To: [email protected]
Cc: Tom Duross <[email protected]>
Subject: Standpipe Testing



CAUTION: This email originated from outside of the organization. Do not click 
links or open attachments unless you can confirm the sender and know the 
content is safe.





I'm wondering if anyone here on the list can help me with some estimates.







I have 3 elevated roadway standpipes to pressure test and flow test.  All set 
with the flow testing part.



My question is pressure testing.  Never did this part before.  I can use the 
public hydrants to fill to street pressure.  No problem.  Static on grade is 
about 75# as I have a couple of pumps in the area I test annually.

Standpipes are about 50' above.  I need to figure out if I need to rent a pump 
capable of reaching 200+ psi or how long will these 2 little ½ and ¾ hp hydro 
pumps I have will take.  This is all witnessed and the plan is hydro for 2 
hours, walk and check everything, drain completely, hook up the pumper and pull 
the trigger.  Can't make the fire guy stand there for 2 hours while the little 
pump hits 200 plus 50 feet.







If I took each of the standpipes, calculated their volume (close to a mile in 
total), figured in all the expansion joints, pipe to the double wye's, air 
vents, low point drains, dual FDC's, etc., and came up volume.  Use fire

hose to reach static.    I take my little pumps at 4 or 6 gpm, decreases as

pressure grows obviously, I need to figure how long these will take to reach 
200-225#.  Thinking hours.  So maybe I need to look into rentals but I need to 
know what size I need.







Ideas?







TD



_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

https://nam12.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7Ccwebber%40reliablesprinkler.com%7Cb04786256ce84af2331908d9006213d0%7C361f92efbca442cdaf0d8099acee2244%7C0%7C0%7C637541243514932628%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdata=Aocxodu2%2BJTWSNVMGv1oYTfxkRJbfSHxNqQ0Dgm306s%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to