In projects where we have a city supply that can meet the site fire flow, but 
not the sprinkler system, then we have been directed to size the fire pump to 
meet the sprinkler system + NFPA hose allowances.  The bypass has been 
considered to take into account the site fire flow requirements in those cases.

Travis Mack, CFPS, CWBSP, RME-G, COC, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271 ext. 700 C: 480-272-2471
[email protected]<mailto:[email protected]>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

From: Sprinklerforum <[email protected]> On Behalf 
Of Gregg Fontes via Sprinklerforum
Sent: Wednesday, April 21, 2021 7:47 AM
To: Prahl, Craig/GVL <[email protected]>; 
[email protected]
Cc: Gregg Fontes <[email protected]>
Subject: RE: Fire Pump Sprk & Fire Flow Demand

Yes. But our is CFC Section 507. What I am trying to understand is NFPA 13 2016 
Edition 11.1.5.3<http://11.1.5.3> & A.11.1.5.3 "Where pumps serve some 
combination of sprinklers, inside hose stations or outside hose stations, the 
pump needs to be capable of providing the flow of the equipment that is fed 
from the pump." The fire pump would be size for the fire sprinkler and any NFPA 
13 inside and/or outside hose demands, but does it also have to be size for the 
2000 gpm fire flow demand since 11.1.5.3<http://11.1.5.3> & A.11.1.5.3 states 
pump needs to be capable of providing flow that is fed from the pump?

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

-----Original Message-----
From: Prahl, Craig/GVL <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 21, 2021 7:09 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Gregg Fontes <[email protected]<mailto:[email protected]>>
Subject: RE: Fire Pump Sprk & Fire Flow Demand

Are site Fire Flow requirements (IFC Section 507) what you're referring to as 
"hydrant demand"?

At minimum, the pump should be capable of flowing the sprinkler and related 
hose stream allowance flow rate combined.

BUT, when there have been no municipal hydrants to be used for the actual 
firefighting effort, we've had to be capable of providing the Fire Flow rate to 
area hydrants plus sprinkler demand via the site fire pump.

I've also had AHJs say to only provide the sprinkler flow plus the hose stream 
allowance via the site pump. So it really depends on the AHJ as the Fire Flow 
requirement is stated in the code as being "by an approved method" i.e., per 
the AHJ.

Have you discussed this with the local fire code official yet?

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com>
1041 East Butler Road Greenville, South Carolina 29606
CONTACT BY: email or MS TEAMS

-----Original Message-----
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Gregg Fontes via Sprinklerforum
Sent: Wednesday, April 21, 2021 9:57 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Gregg Fontes <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] Fire Pump Sprk & Fire Flow Demand

If a fire pump supplies both the fire sprinkler system and the site fire 
hydrants, does the fire pump gpm need to be capable of suppling both? (Fire 
sprinkler demand 900 gpm and site fire hydrant demand 2000 gpm for a total of 
2,900. Can the fire pump be size at 750 for the fire sprinkler/hose demand or 
does it have to be a 2000 gpm so it can supply both the sprinkler and site fire 
hydrant flows of 2900 gpm?) The supply is city water and there is a bypass on 
the fire pump. The city supply comes into the fire pump house and goes out to 
single loop that supplies both the fire sprinkler systems and the site fire 
hydrants. (The city flow and psi is adequate to meet the site fire flow at 
20-psi.)

Thanks,
Gregg Fontes

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!XLuydu_C5h5U5xoYfFkjhto75Yz1NndsYBhU_-ghPrj9wf496LJOQnnfdGty1B3DAw$<https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!XLuydu_C5h5U5xoYfFkjhto75Yz1NndsYBhU_-ghPrj9wf496LJOQnnfdGty1B3DAw$>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to