hi can you share the pump capacity and discharge  head along with the new
building sprinkler requirement additional pressure required,

On Fri, May 7, 2021 at 11:43 PM Kyle.Montgomery via Sprinklerforum <
[email protected]> wrote:

> I'm working on a project where they are adding a new building to an
> existing campus. There is an existing fire water storage tank and fire
> pump  that serves the site underground fire loop. The new building has a
> very demanding sprinkler system that just barely exceeds the fire pump's
> pressure available at the demand flow (using just the pump curve as the
> water supply).
>
> Normally, I would be conservative and use just a few psi as my water
> supply from the tank (as though it were nearly empty). But, is that overly
> conservative? The tank is mounted on the ground, at the same elevation as
> the fire pump, but it is nearly 45 feet tall, with a total capacity of over
> 500,000 gallons. Can I use some of that elevation pressure, or do I need to
> design and calc as though the tank is nearly depleted?
>
> -Kyle M