You'd use the flow data you got from a nearby hydrant flow test.  Typically 
I've not seen a ground tank that supplies a municipal system via gravity.  In 
the municipal installations I've dealt with, a ground tank where there was no 
elevation difference had pumped supplies.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
[email protected] | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Mark.Phelps via Sprinklerforum
Sent: Friday, May 7, 2021 5:07 PM
To: [email protected]
Cc: Mark.Phelps <[email protected]>
Subject: RE: [EXTERNAL] Re: Available Pressure from Fire Water Storage Tank

So,  if this same tank and pump were at the same elevation and  5 blocks away 
in a Water Utility Yard owned by the city water department, what pressure and 
flow rate would one use to design a sprinkler system?

Mark at Aero
602 820-7894

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Bob Caputo via Sprinklerforum
Sent: Friday, May 7, 2021 11:21 AM
To: [email protected]
Cc: Bob Caputo <[email protected]>
Subject: [EXTERNAL] Re: Available Pressure from Fire Water Storage Tank

No, you are not permitted to use elevation pressure from a gravity tank.
You do not know the elevation of the water in the tank which is depleted during 
the operation of the systems in fighting the fire.  You are permitted to use 
the pumps productive curve at 150% of rated flow and 65% of rated pressure

On Fri, May 7, 2021 at 11:13 AM Kyle.Montgomery via Sprinklerforum < 
[email protected]> wrote:

> I'm working on a project where they are adding a new building to an
> existing campus. There is an existing fire water storage tank and fire
> pump  that serves the site underground fire loop. The new building has
> a very demanding sprinkler system that just barely exceeds the fire
> pump's pressure available at the demand flow (using just the pump
> curve as the water supply).
>
> Normally, I would be conservative and use just a few psi as my water
> supply from the tank (as though it were nearly empty). But, is that
> overly conservative? The tank is mounted on the ground, at the same
> elevation as the fire pump, but it is nearly 45 feet tall, with a
> total capacity of over
> 500,000 gallons. Can I use some of that elevation pressure, or do I
> need to design and calc as though the tank is nearly depleted?
>
> -Kyle M
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle
> r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZ
> QLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=sbcv
> VKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14&s=xW_3DXTpaglGRp_Lod9_4SygFCmo
> JqtVkLeqtK_Eczg&e=
>
--
Bob Caputo, CFPS
*President*

*American Fire Sprinkler Association*
p: 214-349-5965 ext124
w: firesprinkler.org
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.facebook.com_firesprinkler.org_&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=sbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14&s=9_q6urq9zEQtQy7i4Nd_rk4BBZBOiJsNCVSFRpcdMjg&e=
 > 
<https://urldefense.proofpoint.com/v2/url?u=https-3A__twitter.com_afsa_status_1039528345367732224&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=sbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14&s=PSOMCv00HpTP3bMjgG5Wczk2iOEH35yxgU-i0lh4kvM&e=
 > 
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.linkedin.com_company_american-2Dfire-2Dsprinkler-2Dassociation-2Dafsa-2D_&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=sbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14&s=4hyISelb176OLCvYsOKsSvSbu842IyJoPrQ706vZmVA&e=
 >
   
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.instagram.com_firesprinklerorg_&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=sbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14&s=WnV3x7dwAvD344IBMMjlrMdRQMfoQ8YIBkyVCR4kNW4&e=
 >

*Train a safer, more efficient workforce.*

By enrolling your employees in the AFSA Apprenticeship Training Series for 
Sprinkler Fitters 
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.firesprinkler.org_WWW_Education_Apprentice-5FTraining_WWW_Education_Apprenticeship-5FTraining.aspx-3Fhkey-3De88ef09e-2Dd74c-2D407f-2Dabcd-2D995aff866149&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=sbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14&s=_6Tmf4i1Euk-al8jqF5PF4JDRqcO13XAFZjt64gY110&e=
 >, you will reap the benefits of a qualified, professional installation crew.
Well-trained employees will work smarter, increasing your company's 
productivity and, in turn, its profits. Learn more 
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.firesprinkler.org_WWW_Education_Apprentice-5FTraining_WWW_Education_Apprenticeship-5FTraining.aspx-3Fhkey-3De88ef09e-2Dd74c-2D407f-2Dabcd-2D995aff866149&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=sbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14&s=_6Tmf4i1Euk-al8jqF5PF4JDRqcO13XAFZjt64gY110&e=
 > .
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=sbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14&s=xW_3DXTpaglGRp_Lod9_4SygFCmoJqtVkLeqtK_Eczg&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!Ul5vSasIKyPqlfhAgWF_3SuAdWL3R4Yn1ecegiMM7DkGFvV-YyjiLDO_5Kx2jkNYLA$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to