No. Just because a generator is present doesn't automatically require it to be 
connected to the fire pump.

The requirement of secondary or backup power for an electric fire pump is 
directly related to the reliability of the primary power source and other 
factors, some which may be code driven, some based on the function of the 
building and other reasons may be related to the contents of the building 
(hazardous materials).  There are specific guidelines that typically are 
addressed or queried as part of the electrical power supply analysis by the 
project electrical engineer/contractor.  (well, hopefully).

NFPA 20, 2019 9.3.2 speaks about non-reliable power sources and additional 
criteria is defined within the appendix.  Now, while this particular section is 
addressing High-Rises, the same application can apply to any building with 
contents or other conditions that absolutely must have an operational fire pump.

So in the case of this building which has refrigerated consumables, whether or 
not the fire pump HAS to be operational in a power outage to protect the 
building and product is more of an owner/insurer preference.  If the ice cream 
melts, it will be a mess but it will not endanger the public.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
[email protected] | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Richard Mote via Sprinklerforum
Sent: Thursday, August 26, 2021 8:04 PM
To: [email protected]
Cc: Richard Mote <[email protected]>
Subject: [EXTERNAL] Transfer Switches

Got a email from a customer with the following question. I'm on the road with 
no access to my books.If an emergency generator is installed on a building, is 
there anything in the codes that would require it to be connected to the fire 
pump.
RichardL. Mote CET

Rimrock Design Services,LLC

PO Box 36
Middleburg, PA 17842

Mobile 570-541-2685

EMAIL [email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!T4uYAkl7uaiDaLLk06_07WCUsdxHvgb0jPnXmoR860XehiP7vacKg939FxRbmK-YAw$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to