Slightly off topic - the determination of "reliable" normal power can
change with time.  Look at the Texas area after last winter.  Look at New
Orleans after the last 24 hours.  Just because an area was served by
reliable power in the psat, things do change.  Have the engineer of record
determine if standby power is required.  As Craig stated, many factors can
influence the decision.

On a personal note, I have specified, designed, installed, tested, and
maintained thousands of diesel driven fire pumps systems.  Thet do make a
good option where normal and or standby power is an issue.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do.*

*Get in the (Fitter) Zone!*


AFSA's "Fitter Zone" features live webinars designed specifically for fire
sprinkler fitters. These live presentations are held on Saturdays whenever
possible, so you don't have to take your fitters out of the field during
the workweek. If you cannot attend live sessions, these webinars will be
recorded and can be purchased for on-demand access.  Learn more *here*
<https://www.firesprinkler.org/fitterzone>.




On Mon, Aug 30, 2021 at 8:58 AM Prahl, Craig/GVL via Sprinklerforum <
[email protected]> wrote:

> No. Just because a generator is present doesn't automatically require it
> to be connected to the fire pump.
>
> The requirement of secondary or backup power for an electric fire pump is
> directly related to the reliability of the primary power source and other
> factors, some which may be code driven, some based on the function of the
> building and other reasons may be related to the contents of the building
> (hazardous materials).  There are specific guidelines that typically are
> addressed or queried as part of the electrical power supply analysis by the
> project electrical engineer/contractor.  (well, hopefully).
>
> NFPA 20, 2019 9.3.2 speaks about non-reliable power sources and additional
> criteria is defined within the appendix.  Now, while this particular
> section is addressing High-Rises, the same application can apply to any
> building with contents or other conditions that absolutely must have an
> operational fire pump.
>
> So in the case of this building which has refrigerated consumables,
> whether or not the fire pump HAS to be operational in a power outage to
> protect the building and product is more of an owner/insurer preference.
> If the ice cream melts, it will be a mess but it will not endanger the
> public.
>
> Craig Prahl | Jacobs | Group Lead/SME - Fire Protection |
> [email protected] | www.jacobs.com
> 1041 East Butler Road   Greenville, South Carolina  29606
> CONTACT BY: email or MS TEAMS
>
>
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of Richard Mote via Sprinklerforum
> Sent: Thursday, August 26, 2021 8:04 PM
> To: [email protected]
> Cc: Richard Mote <[email protected]>
> Subject: [EXTERNAL] Transfer Switches
>
> Got a email from a customer with the following question. I'm on the road
> with no access to my books.If an emergency generator is installed on a
> building, is there anything in the codes that would require it to be
> connected to the fire pump.
> RichardL. Mote CET
>
> Rimrock Design Services,LLC
>
> PO Box 36
> Middleburg, PA 17842
>
> Mobile 570-541-2685
>
> EMAIL [email protected]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!T4uYAkl7uaiDaLLk06_07WCUsdxHvgb0jPnXmoR860XehiP7vacKg939FxRbmK-YAw$
>
> ________________________________
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to