Taylor, 
Old plan reviewers never die…they just go crazy and lose their minds. I had a 
dream last night trying to find a solution to resolve this issue. Here’s 
another penny of my thoughts so total of three cents. 

3 - I think you should ask the plan reviewer what his intent is for the flow 
switch. If he wants it just to protect the owner from potential water damage 
from a break in the supply pipe AND the parking garage is not subject to 
significant water damage OR a security patrol is provided, then maybe he might 
consider a signed letter from the owner, architect, or engineer accepting 
responsibility and liability for any water damage in lieu of the flow switch. 

Since this “deficiency” is not a life safety issue, I might accept a letter, 
but I never had anyone write me one of that nature. I generally got what I 
asked for when I convinced them that it was in their best interest to follow my 
“suggestions”. Since the backflow preventer should already have valve 
supervision, the additional cost of a VPA with pressure switch is not too 
extreme and the waterflow signal could be treated as a supervisory signal 
instead of alarm. 

Now just my three cents. 
Rick Matsuda 

> On Aug 5, 2022, at 6:28 PM, Taylor Schumacher <tay...@sfsprinkler.com> wrote:
> 
>  Thanks for the two cents, Rick. This project does have the water service 
> stub in a less than ideal spot where the underground installer saved some 
> money and left some of the “supply” piping for the sprinkler contractor to 
> run. The area in question is in an above grade, enclosed and heated garage 
> serving an apartment. 
> 
> There is a back flow preventer with gate valves at this water service stub 
> before the long run to the pump flange so there is a way to shut off water 
> inside the building.
> 
> My initial thoughts are that the alarm on the controller may trigger false 
> alarms and would not reliably work in the manner we are hoping. I am hoping 
> my pump supplier can walk me through the way that would work when he is back 
> from vacation.
> 
>> Taylor Schumacher ET
> 
> 
>>> On Aug 5, 2022, at 4:46 PM, Rick Matsuda <rick26...@gmail.com> wrote:
>>> 
>> 
>> I’m hope I’m not too late to jump into this conversation. As an old plan 
>> reviewer for the insurance industry and for a municipality, I have two 
>> issues with the suction piping arrangement. 
>> 
>> 1 - I can’t remember if it’s code or part of the old insurance rules, but I 
>> did not allow supply piping to run through a building unsupervised. We 
>> wanted notification in the event of a catastrophic break in the pipe to 
>> limit any water damage. The instance that I remember involved a riser 
>> manifold that was moved about 100-feet from where the spigot piece entered 
>> the building because the engineer and architect screwed up. This was not a 
>> pump suction pipe so they installed a flow switch and a control
>> valve at the spigot.
>> I think it’s written somewhere that it’s “good engineering practice” to make 
>> the supply pipe from the spigot the the risers as “short as possible”. 
>> For your pump arrangement, I guess a VPA with a pressure switch on the bell 
>> line would be okay.
>> You mentioned that the pipe runs about 200-feet through a parking garage so 
>> maybe water damage wouldn’t be a big issue so the flow switch might not be 
>> needed unless it’s an underground parking structure. I think a control valve 
>> still should be installed at the spigot. 
>> 
>> 2 - Is this an unheated parking garage and is there any possibility of 
>> freeze damage for the suction pipe?
>> 
>> Just my two cents. 
>> Rick Matsuda
>> 
>>> On Aug 5, 2022, at 2:23 PM, Taylor Schumacher <tay...@sfsprinkler.com> 
>>> wrote:
>>> 
>>>  Kyle, I’m not sure how that would alert someone to flowing water, other 
>>> than count the water that flowed. What am I missing?
>>> 
>>>> Taylor Schumacher ET
>>> 
>>> 
>>>> On Aug 5, 2022, at 2:06 PM, Kyle.Montgomery <kmontgom...@aerofire.com> 
>>>> wrote:
>>>> 
>>>> 
>>>> Also not free, but what about utilizing a backflow preventer with a 
>>>> detector assembly? Not an additional one, just in lieu of the one that’s 
>>>> planned already. (I’m guessing there is one planned somewhere, right?)
>>>>  
>>>> -Kyle M
>>>>  
>>>> From: Taylor Schumacher <tay...@sfsprinkler.com> 
>>>> Sent: Friday, August 5, 2022 10:51 AM
>>>> To: Discussion list on issues relating to automatic fire sprinklers 
>>>> <sprinklerforum@lists.firesprinkler.org>
>>>> Subject: [EXTERNAL] [Sprinklerforum] Re: WFD In Pump Suction Line
>>>>  
>>>> Those are often the things that people who make suggestions don’t have to 
>>>> consider.
>>>>  
>>>>  
>>>> Taylor Schumacher ET
>>>>  
>>>>  
>>>>  
>>>> From: Matt Grise <m...@afpsprink.com> 
>>>> Sent: Friday, August 05, 2022 11:56 AM
>>>> To: Discussion list on issues relating to automatic fire sprinklers 
>>>> <sprinklerforum@lists.firesprinkler.org>
>>>> Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
>>>>  
>>>> Are you going to be able to get a change order from the owner to cover 
>>>> this suggestion from the plan reviewer?
>>>>  
>>>> Matt
>>>>  
>>>>  
>>>> From: Anthony Carrizosa <anth...@archerconstruction.com> 
>>>> Sent: Friday, August 05, 2022 11:54 AM
>>>> To: Discussion list on issues relating to automatic fire sprinklers 
>>>> <sprinklerforum@lists.firesprinkler.org>
>>>> Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
>>>>  
>>>> Taylor
>>>> Every time the jockey pump turns on it will ring the bell? Unless you use 
>>>> a very large retard chamber.
>>>>  
>>>>  
>>>> From: Taylor Schumacher <tay...@sfsprinkler.com> 
>>>> Sent: Friday, August 5, 2022 8:44 AM
>>>> To: Discussion list on issues relating to automatic fire sprinklers 
>>>> <sprinklerforum@lists.firesprinkler.org>
>>>> Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
>>>>  
>>>> Ding Ding Ding (pun intended) I think we have a winner.
>>>>  
>>>>  
>>>> Taylor Schumacher ET
>>>>  
>>>>  
>>>>  
>>>> From: Vincent J. Como <vjc...@waynefire.com> 
>>>> Sent: Friday, August 05, 2022 10:41 AM
>>>> To: Discussion list on issues relating to automatic fire sprinklers 
>>>> <sprinklerforum@lists.firesprinkler.org>
>>>> Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
>>>>  
>>>> If pressure isn’t the issue…I vote water motor gong
>>>>  
>>>> Thanks,
>>>>  
>>>>  
>>>> <image001.png>
>>>> Vinnie Como
>>>> Commercial Designer
>>>> Wayne Automatic Fire Sprinklers, Inc. ®
>>>> 3226 Cherry Palm Dr, Tampa, FL 33619
>>>> ph: 813-682-1657 cell: 954-650-2812
>>>> Ocoee | Jacksonville | Deerfield Beach | Tampa | Ft Myers | Concord, NC | 
>>>> Raleigh, NC
>>>> <image002.png>
>>>>  
>>>> <image003.png>
>>>>  
>>>>  
>>>> From: Taylor Schumacher <tay...@sfsprinkler.com> 
>>>> Sent: Friday, August 5, 2022 11:32 AM
>>>> To: Discussion list on issues relating to automatic fire sprinklers 
>>>> <sprinklerforum@lists.firesprinkler.org>
>>>> Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
>>>>  
>>>> I used a similar phrase during the phone call to point me to the section 
>>>> where it is required.
>>>>  
>>>> He was/is unable to supply code references for that requirement and 
>>>> pointed it out as such-it is merely a recommendation as he is concerned 
>>>> about damage to the piping or fittings causing water to flow without any 
>>>> alarms or notifications. It was never a concern about adequate suction 
>>>> pressure.
>>>>  
>>>>  
>>>> Thanks for all the responses!
>>>>  
>>>>  
>>>> Taylor Schumacher ET
>>>>  
>>>>  
>>>>  
>>>> From: Ken Wagoner <k...@parsleyconsulting.com> 
>>>> Sent: Friday, August 05, 2022 10:05 AM
>>>> To: Discussion list on issues relating to automatic fire sprinklers 
>>>> <sprinklerforum@lists.firesprinkler.org>; Taylor Schumacher 
>>>> <tay...@sfsprinkler.com>
>>>> Subject: Re: [Sprinklerforum] WFD In Pump Suction Line
>>>>  
>>>> Taylor,
>>>> 
>>>> After reading your original post, and several of the responses, 
>>>> particularly that of Chris Dorn, I'm prompted to share my thoughts.
>>>> Is the AHJ looking for supervision of the appropriate suction pressure in 
>>>> that feed to the fire pump?  I'm sure you understand this - however the 
>>>> AHJ may not - a 'paddle type' switch is only going to provide notification 
>>>> if the line is flowing. It won't report any information in a static 
>>>> condition.  
>>>>  
>>>> If the concern is indeed to supervise the suction pressure at a certain 
>>>> level in the supply to the fire pump a pressure switch would be better 
>>>> suited for this purpose.  The switch settings could be established at the 
>>>> required suction pressure, and any reduction in that pressure would 
>>>> activate the switch, and transmit the supervisory notice to the fire pump 
>>>> controller or fire alarm panel, whichever is preferred.
>>>>  
>>>> If it is only supervision of actual flow in the line as others have 
>>>> pointed out there are better choices than a paddle type switch. It's also 
>>>> worth noting that the pump controller may already have the supervision the 
>>>> AHJ is suggesting.
>>>> Finally, as one other poster has noted - if there is a section of the 
>>>> applicable code or standard which requires supervision of the suction line 
>>>> to a fire pump, then I would request direction to the section.  If it's 
>>>> there, then I'll do what it requires, as I want to follow the 'rules' as 
>>>> closely as possible.  If it's not there, and it's just the AHJ's 
>>>> preference, then what are we talking about? 
>>>> 
>>>> That concept has guided most of my work, which I've boiled down to 'prove 
>>>> it.'  My late father's take on this was, "Put up, or shut up."
>>>> 
>>>> sincerely,
>>>> 
>>>> Ken Wagoner, SET
>>>> Parsley Consulting
>>>> 500 West Mechanic Street
>>>> Harrisonville, Missouri 64701-2235
>>>> Phone: (760) 745-6181 
>>>> Visit the website
>>>>  
>>>> 
>>>> _________________________________________________________
>>>> SprinklerForum mailing list:
>>>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>>>> To unsubscribe send an email to 
>>>> sprinklerforum-le...@lists.firesprinkler.org
>>> 
>>> _________________________________________________________
>>> SprinklerForum mailing list:
>>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>>> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
>> 
>> _________________________________________________________
>> SprinklerForum mailing list:
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to