Thanks for the two cents, Rick. This project does have the water service stub 
in a less than ideal spot where the underground installer saved some money and 
left some of the “supply” piping for the sprinkler contractor to run. The area 
in question is in an above grade, enclosed and heated garage serving an 
apartment.

There is a back flow preventer with gate valves at this water service stub 
before the long run to the pump flange so there is a way to shut off water 
inside the building.

My initial thoughts are that the alarm on the controller may trigger false 
alarms and would not reliably work in the manner we are hoping. I am hoping my 
pump supplier can walk me through the way that would work when he is back from 
vacation.

Taylor Schumacher ET

On Aug 5, 2022, at 4:46 PM, Rick Matsuda <rick26...@gmail.com> wrote:


I’m hope I’m not too late to jump into this conversation. As an old plan 
reviewer for the insurance industry and for a municipality, I have two issues 
with the suction piping arrangement.

1 - I can’t remember if it’s code or part of the old insurance rules, but I did 
not allow supply piping to run through a building unsupervised. We wanted 
notification in the event of a catastrophic break in the pipe to limit any 
water damage. The instance that I remember involved a riser manifold that was 
moved about 100-feet from where the spigot piece entered the building because 
the engineer and architect screwed up. This was not a pump suction pipe so they 
installed a flow switch and a control
valve at the spigot.
I think it’s written somewhere that it’s “good engineering practice” to make 
the supply pipe from the spigot the the risers as “short as possible”.
For your pump arrangement, I guess a VPA with a pressure switch on the bell 
line would be okay.
You mentioned that the pipe runs about 200-feet through a parking garage so 
maybe water damage wouldn’t be a big issue so the flow switch might not be 
needed unless it’s an underground parking structure. I think a control valve 
still should be installed at the spigot.

2 - Is this an unheated parking garage and is there any possibility of freeze 
damage for the suction pipe?

Just my two cents.
Rick Matsuda

On Aug 5, 2022, at 2:23 PM, Taylor Schumacher <tay...@sfsprinkler.com> wrote:

 Kyle, I’m not sure how that would alert someone to flowing water, other than 
count the water that flowed. What am I missing?

Taylor Schumacher ET

On Aug 5, 2022, at 2:06 PM, Kyle.Montgomery <kmontgom...@aerofire.com> wrote:


Also not free, but what about utilizing a backflow preventer with a detector 
assembly? Not an additional one, just in lieu of the one that’s planned 
already. (I’m guessing there is one planned somewhere, right?)

-Kyle M

From: Taylor Schumacher <tay...@sfsprinkler.com>
Sent: Friday, August 5, 2022 10:51 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] [Sprinklerforum] Re: WFD In Pump Suction Line

Those are often the things that people who make suggestions don’t have to 
consider.


Taylor Schumacher ET



From: Matt Grise <m...@afpsprink.com<mailto:m...@afpsprink.com>>
Sent: Friday, August 05, 2022 11:56 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line

Are you going to be able to get a change order from the owner to cover this 
suggestion from the plan reviewer?

Matt


From: Anthony Carrizosa 
<anth...@archerconstruction.com<mailto:anth...@archerconstruction.com>>
Sent: Friday, August 05, 2022 11:54 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line

Taylor
Every time the jockey pump turns on it will ring the bell? Unless you use a 
very large retard chamber.


From: Taylor Schumacher <tay...@sfsprinkler.com<mailto:tay...@sfsprinkler.com>>
Sent: Friday, August 5, 2022 8:44 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line

Ding Ding Ding (pun intended) I think we have a winner.


Taylor Schumacher ET



From: Vincent J. Como <vjc...@waynefire.com<mailto:vjc...@waynefire.com>>
Sent: Friday, August 05, 2022 10:41 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line

If pressure isn’t the issue…I vote water motor gong

Thanks,


<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2f&c=E,1,YAuGiAvh8Bd8tInNL1AcYkwYqe9h7PiJQ9M0R4GO2x8ZDtXiEvQaj0J_kPRSv1Z4K-EclvmiWW-J86oBTIz6tHf9zHiKp4WFVStoy0jfJyzCy_qgvn1Scg,,&typo=1__;JSUlJQ!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R33wZkzJg$>
<image001.png><https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2f&c=E,1,YAuGiAvh8Bd8tInNL1AcYkwYqe9h7PiJQ9M0R4GO2x8ZDtXiEvQaj0J_kPRSv1Z4K-EclvmiWW-J86oBTIz6tHf9zHiKp4WFVStoy0jfJyzCy_qgvn1Scg,,&typo=1__;JSUlJQ!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R33wZkzJg$>

Vinnie Como
Commercial Designer
Wayne Automatic Fire Sprinklers, Inc. ®
3226 Cherry Palm Dr, Tampa, FL 
33619<https://urldefense.com/v3/__https:/www.google.com/maps/place/Wayne*Automatic*Fire*Sprinklers/@27.9731297,-82.3452243,19.11z/data=!4m5!3m4!1s0x88c2cedf6f61e705:0x68ee7d733b51ea7a!8m2!3d27.9730378!4d-82.3449507?hl=en-US__;Kysr!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R3owC7RUA$>
ph: 813-682-1657<tel:813-682-1657> cell: 954-650-2812<tel:954-650-2812>
Ocoee<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2flocations*2focoee-florida-orlando&c=E,1,vExZ6C9e3yCTEbsEFUqlmtTfuz_ppqQDduT__Efj91tWLPGRFJpWv-JGUw2kNJW53jYKuMeg6Q1pvZwQpNfacAbT0zGVwjc4FrN1BKdfAB1IWHSNul3VzlSLiVM,&typo=1__;JSUlJSU!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R3rU4c4vw$>
 | 
Jacksonville<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2flocations*2fjacksonville-florida&c=E,1,ChRfqM4xExpVeUJnNoPL3aR4pxuFWfGc6rDigkPMGiDM3dCOtMTXrd2yzYc2aLK0FLlEPckIpLL3wlYdTL6lADxhLu-kllq9tVnF9Ketspwsd1mGrZtkNb0,&typo=1__;JSUlJSU!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R0UinJo5w$>
 | Deerfield 
Beach<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2flocations*2fdeerfield-florida&c=E,1,3PqPbbwepDlqF7XunOGAV0SRes8yZO0vCXbyWE2r7aD9iNEYOpuNfh6rstStmjPfavEG1LTna5m1vHGHWSqN5rJ26dnw1py_GJ8fqB_LjWJZZrh36fgDrhov&typo=1__;JSUlJSU!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R09DcC7SQ$>
 | 
Tampa<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2flocations*2ftampa-florida&c=E,1,iUQE88MefwFkk2qaxdc_qjjYsunuVI0QicwkQBzsh8_6JHtfcr-ZS71e-H58I279a-1Il23LA1skI9rCw5Lc8ZQgmp1_1XdcMro0AFh07S2hfK0,&typo=1__;JSUlJSU!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R2KEMlhTg$>
 | Ft 
Myers<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2flocations*2fft-meyers-florida&c=E,1,dMe4uwwpSQdGlHqOWbQCEZpK2_178uoHgFGXBPwfjUULOqegaJzG_zCSIvXXNYIIss0z-QQ8zGly3b0Lw2b_jO2YvICXw2x_gk6IZwcjQKw,&typo=1__;JSUlJSU!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R1U62twnA$>
 | Concord, 
NC<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2flocations*2fconcord-north-carolina-charlotte&c=E,1,SuR8xKoJTbG_9aR5gerlAuVvxi0B8dk1hDypA1uYBMllJNcn5Fn7n4hv37y1Mx42xshn-TONHzRK9MwOAWT7qrLadDzvo9IbbT8S9Qye&typo=1__;JSUlJSU!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R3OXR2pfg$>
 | Raleigh, 
NC<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2flocations*2fraleigh-north-carolina*2f&c=E,1,xpStYW12PjbFaEyfOzBxsvqCiDBiMZodfwtYyCkD-w8ghFUHGNXCLkwtDSArE0PWPimmdheGTpxvxPcJAodTFxKe0xTBO7CGjCB9-KdF3ZIChK4Iattk5Anl4Yc,&typo=1__;JSUlJSUl!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R3iDn0Orw$>
<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2f&c=E,1,5-oU3GGUO7qW5kCWm8v-8ZKTOrVGsW0iIOyD72q6hQo7ljv7OmRPROoecHEse3VFj8p_fJ7AM9k8Uds-BQ1izn0N0DWvF3Y28yfuSQNRaq0KLg,,&typo=1__;JSUlJQ!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R2AC5zYkw$>
<image002.png><https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.waynefire.com*2f&c=E,1,5-oU3GGUO7qW5kCWm8v-8ZKTOrVGsW0iIOyD72q6hQo7ljv7OmRPROoecHEse3VFj8p_fJ7AM9k8Uds-BQ1izn0N0DWvF3Y28yfuSQNRaq0KLg,,&typo=1__;JSUlJQ!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R2AC5zYkw$>
 
<https://urldefense.com/v3/__https:/www.facebook.com/Wayne-Automatic-Fire-Sprinklers-Inc-122998935990/__;!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R3WYraJHA$>
<image003.png>



From: Taylor Schumacher <tay...@sfsprinkler.com<mailto:tay...@sfsprinkler.com>>
Sent: Friday, August 5, 2022 11:32 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line

I used a similar phrase during the phone call to point me to the section where 
it is required.

He was/is unable to supply code references for that requirement and pointed it 
out as such-it is merely a recommendation as he is concerned about damage to 
the piping or fittings causing water to flow without any alarms or 
notifications. It was never a concern about adequate suction pressure.


Thanks for all the responses!


Taylor Schumacher ET



From: Ken Wagoner 
<k...@parsleyconsulting.com<mailto:k...@parsleyconsulting.com>>
Sent: Friday, August 05, 2022 10:05 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>;
 Taylor Schumacher <tay...@sfsprinkler.com<mailto:tay...@sfsprinkler.com>>
Subject: Re: [Sprinklerforum] WFD In Pump Suction Line

Taylor,

After reading your original post, and several of the responses, particularly 
that of Chris Dorn, I'm prompted to share my thoughts.

  *   Is the AHJ looking for supervision of the appropriate suction pressure in 
that feed to the fire pump?  I'm sure you understand this - however the AHJ may 
not - a 'paddle type' switch is only going to provide notification if the line 
is flowing. It won't report any information in a static condition.

  *   If the concern is indeed to supervise the suction pressure at a certain 
level in the supply to the fire pump a pressure switch would be better suited 
for this purpose.  The switch settings could be established at the required 
suction pressure, and any reduction in that pressure would activate the switch, 
and transmit the supervisory notice to the fire pump controller or fire alarm 
panel, whichever is preferred.

  *   If it is only supervision of actual flow in the line as others have 
pointed out there are better choices than a paddle type switch. It's also worth 
noting that the pump controller may already have the supervision the AHJ is 
suggesting.

Finally, as one other poster has noted - if there is a section of the 
applicable code or standard which requires supervision of the suction line to a 
fire pump, then I would request direction to the section.  If it's there, then 
I'll do what it requires, as I want to follow the 'rules' as closely as 
possible.  If it's not there, and it's just the AHJ's preference, then what are 
we talking about?

That concept has guided most of my work, which I've boiled down to 'prove it.'  
My late father's take on this was, "Put up, or shut up."

sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.parsleyconsulting.com*2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1__;JSUlJQ!!Ba8_KKAT!M9UNxAXu263yE-UFsVmaWJujCDpCEjVEk4XTsEseaGdr1rqiCQz5dYZz4Nd1WBQ2El_HniMVj9Cy8R3xyRwMrw$>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to