Ding Ding Ding (pun intended) I think we have a winner.

Taylor Schumacher ET



From: Vincent J. Como <[email protected]>
Sent: Friday, August 05, 2022 10:41 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line

If pressure isn’t the issue…I vote water motor gong

Thanks,


[Proudly Saving Lives since 1978. Wayne Automatic Fire Sprinklers, Inc. Minutes 
Matter.]<https://www.waynefire.com/>

Vinnie Como
Commercial Designer
Wayne Automatic Fire Sprinklers, Inc. ®
3226 Cherry Palm Dr, Tampa, FL 
33619<https://www.google.com/maps/place/Wayne+Automatic+Fire+Sprinklers/@27.9731297,-82.3452243,19.11z/data=!4m5!3m4!1s0x88c2cedf6f61e705:0x68ee7d733b51ea7a!8m2!3d27.9730378!4d-82.3449507?hl=en-US>
ph: 813-682-1657<tel:813-682-1657> cell: 954-650-2812<tel:954-650-2812>
Ocoee<https://www.waynefire.com/locations/ocoee-florida-orlando> | 
Jacksonville<https://www.waynefire.com/locations/jacksonville-florida> | 
Deerfield Beach<https://www.waynefire.com/locations/deerfield-florida> | 
Tampa<https://www.waynefire.com/locations/tampa-florida> | Ft 
Myers<https://www.waynefire.com/locations/ft-meyers-florida> | Concord, 
NC<https://www.waynefire.com/locations/concord-north-carolina-charlotte> | 
Raleigh, NC<https://www.waynefire.com/locations/raleigh-north-carolina/>
[https://www.alariedesign.com/signatures/wayne/images/icon-www.png]<https://www.waynefire.com/>
 [https://www.alariedesign.com/signatures/wayne/images/icon-fb.png] 
<https://www.facebook.com/Wayne-Automatic-Fire-Sprinklers-Inc-122998935990/>



From: Taylor Schumacher <[email protected]<mailto:[email protected]>>
Sent: Friday, August 5, 2022 11:32 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line

I used a similar phrase during the phone call to point me to the section where 
it is required.

He was/is unable to supply code references for that requirement and pointed it 
out as such-it is merely a recommendation as he is concerned about damage to 
the piping or fittings causing water to flow without any alarms or 
notifications. It was never a concern about adequate suction pressure.


Thanks for all the responses!


Taylor Schumacher ET



From: Ken Wagoner 
<[email protected]<mailto:[email protected]>>
Sent: Friday, August 05, 2022 10:05 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>;
 Taylor Schumacher <[email protected]<mailto:[email protected]>>
Subject: Re: [Sprinklerforum] WFD In Pump Suction Line

Taylor,

After reading your original post, and several of the responses, particularly 
that of Chris Dorn, I'm prompted to share my thoughts.

  *   Is the AHJ looking for supervision of the appropriate suction pressure in 
that feed to the fire pump?  I'm sure you understand this - however the AHJ may 
not - a 'paddle type' switch is only going to provide notification if the line 
is flowing. It won't report any information in a static condition.

  *   If the concern is indeed to supervise the suction pressure at a certain 
level in the supply to the fire pump a pressure switch would be better suited 
for this purpose.  The switch settings could be established at the required 
suction pressure, and any reduction in that pressure would activate the switch, 
and transmit the supervisory notice to the fire pump controller or fire alarm 
panel, whichever is preferred.

  *   If it is only supervision of actual flow in the line as others have 
pointed out there are better choices than a paddle type switch. It's also worth 
noting that the pump controller may already have the supervision the AHJ is 
suggesting.

Finally, as one other poster has noted - if there is a section of the 
applicable code or standard which requires supervision of the suction line to a 
fire pump, then I would request direction to the section.  If it's there, then 
I'll do what it requires, as I want to follow the 'rules' as closely as 
possible.  If it's not there, and it's just the AHJ's preference, then what are 
we talking about?

That concept has guided most of my work, which I've boiled down to 'prove it.'  
My late father's take on this was, "Put up, or shut up."

sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to