I agree with Kevin’s assessment as well.

But we were not discussing droplet scatter or if suppression would even be 
achieved.

I feel we often overlook the “Beam Rule” having 2 requirements. One of which 
must be met.
Distance per the table, or sprinklers spaced on both sides.

Great discussion. I feel you framed you question to elicit a literal reading 
and response.

Bravo Anthony. Well played sir!

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>
www.FergusonFire.com<http://www.fergusonfire.com/>

From: Anthony Johnson <mountainfirepr...@gmail.com>
Sent: Friday, March 10, 2023 8:29 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Duct obstruction criteria in LH attic

In our situation we are 3" above the duct but can locate the uprights as far as 
2 ft away horizontally. The next line of sprinklers would exceed the halfway 
point to the duct IF the duct posed as an obstruction. I agree with Kevin 
Hall's assessment however I'm also thinking ahead when the inspector questions 
it and want to make sure I'm justified in my position. I might add sprinklers 
just to avoid having a discussion with the inspector on a topic that obviously 
has many different opinions. I think there are good arguments on both sides but 
I think the code makes it obvious in a roundabout way. At the very least I 
would hope for an additional  little "AHJ FAQ" in the handbook as found in the 
commentaries - even though they don't carry weight it would be helpful.

[https://s-install.avcdn.net/ipm/preview/icons/icon-envelope-tick-green-avg-v1.png]<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail>
Virus-free.www.avg.com<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail>

On Fri, Mar 10, 2023 at 8:12 AM 
<matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>> wrote:
The one number I do not recall in this discussion is the distance horizontally.

I guess based on the pretty picture in Figure A.9.5.5.1, I am having trouble 
seeing how a deflector at only 3” above gets water on the other side of a 24” 
duct.

If the sprinkler is 2” from the duct, like happens in an attic, is it still 
your position that water will get on the other side?

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>
www.FergusonFire.com<http://www.fergusonfire.com/>

From: Kevin Hall <kh...@firesprinkler.org<mailto:kh...@firesprinkler.org>>
Sent: Thursday, March 9, 2023 6:38 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Duct obstruction criteria in LH attic

I’m not sure where you are getting that requirement from the annex section:

A.10.2.7.3.1.4  It is the intent of this section to exempt nonstructural 
elements in light and ordinary hazard occupancies from the obstruction criteria 
commonly called the “Three Times Rule.” However, the other obstruction rules, 
including the “Beam Rule” (see 
10.2.7.2<https://link.nfpa.org/publications/13/2022/chapters/10#ID000130001317>)
 and the “Wide Obstruction Rule” (see 
10.2.7.4.2<https://link.nfpa.org/publications/13/2022/chapters/10#ID000130001351>),
 still apply. If an obstruction is so close to a sprinkler that water cannot 
spray on both sides, it is effectively a continuous obstruction as far as the 
sprinkler is concerned and the Beam Rule should be applied.

It is not the intent of this section to permit the use of fixtures and 
architectural features or treatments to conceal, obscure, or otherwise obstruct 
sprinkler discharge. The requirement should be applied in accordance with the 
performance objectives in 
10.2.7.1<https://link.nfpa.org/publications/13/2022/chapters/10#ID000130001315>.



The annex specifically states it IS the intent to EXEMPT nonstructural elements 
in light and ordinary hazard occupancies from the three times rule.



IF the obstruction was at or above the level of the deflector, then the beam 
rule would apply, but this deflector is above the obstruction so water is able 
to spray on both sides of the obstruction, creating a noncontinuous 
obstruction, so the beam rule does NOT apply.



IF the obstruction was wider than 4 ft, then the wide obstruction rule would 
apply, but this obstruction is 2 ft wide, so no additional protection is 
required.



The last paragraph of the annex defers to the requirements in 10.2.7.1 which 
state, “Sprinklers shall be located so as to minimize obstructions to discharge 
as defined in 
10.2.7<https://link.nfpa.org/publications/13/2022/chapters/10#ID000130001314>, 
or additional sprinklers shall be provided to ensure adequate coverage of the 
hazard.” The obstruction is minimized based on the position of the sprinkler 
deflector above the obstruction, and adequate coverage is provided for the 
hazard present. It is a light hazard occupancy — low quantity and low 
combustibility — it is NOT the intent of the installation and obstruction rules 
to get every inch of the floor wet. There will be shadow areas, but the 
thermodynamic properties of the water spray converting to steam will provide 
plenty of cooling to achieve adequate fire control.


[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
Sr. Manager, Engineering and Technical Services
American Fire Sprinkler Association
p:
214-349-5971
w:
firesprinkler.org<http://firesprinkler.org>
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/facebook_sig.png]<https://www.facebook.com/firesprinkler.org/>
  
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/twitter_sig.png] 
<https://twitter.com/afsa/status/1039528345367732224>   
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/linkedin_sig.png]
 <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>  
 
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/instagram_sig.png]
 <https://www.instagram.com/firesprinklerorg/>

AFSA is on the move!
Our new address is 1410 East Renner Rd., Suite 150, Richardson, TX 75082

Advanced Sprinkler Hydraulic Calculations

Take a deep dive into advanced hydraulic principles for standpipe systems, fire 
pump assemblies, and water storage tanks. Learn more and register for the May 
3-5 class 
here<https://www.firesprinkler.org/programs/advanced-sprinkler-hydraulic-calculations-workshop/>.

On Thu, Mar 9, 2023 at 8:13 PM Brett Peters 
<br...@proudline.ca<mailto:br...@proudline.ca>> wrote:
The annex clarifies that any object within the 18” is considered an obstruction 
and you are required to use the 3X or bean rule

On Thu, Mar 9, 2023 at 4:51 PM Kevin Hall 
<kh...@firesprinkler.org<mailto:kh...@firesprinkler.org>> wrote:
Dane is correct.

We get this question a lot through the Technical Review submissions, and the 
response is pretty cut and dry.

The three times rule does not apply to non structural members in light and 
ordinary hazard occupancies and because the deflector is located above the 
duct, water is able to spray on both sides, so it can be considered a 
noncontinuous obstruction. No additional protection is not required.

-Kevin

On Thu, Mar 9, 2023 at 5:08 PM Greg McGahan 
<g...@genesisfireservices.com<mailto:g...@genesisfireservices.com>> wrote:
With all due respect Dane - read the annex,  it specifically addresses that 
issue.

On Thu, Mar 9, 2023 at 3:42 PM Dane Long 
<da...@bamfordfire.com<mailto:da...@bamfordfire.com>> wrote:
Anthony,

I feel there might be a few sections you need to look at regarding this 
question.

For me I would start at 8.6.5.2<http://8.6.5.2> Obstructions to Sprinkler 
Discharge Pattern Development.

8.6.5.2.1.1 Continuous or noncontinuous obstructions less than or equal to 18 
in. (457 mm)
below the sprinkler deflector that prevent the pattern from fully developing 
shall comply with
8.6.5.2<http://8.6.5.2>.

The section above lays the ground work for the 18in requirement 
(8.6.5.2<http://8.6.5.2>). Then I would look at 8.6.5.2.1.3* Minimum Distance 
from Obstructions.

8.6.5.2.1.4* For light and ordinary hazard occupancies, structural
members only shall be considered when applying the requirements
of 8.6.5.2.1.3.

IMHO Because it specifically says “structural members only shall be considered” 
I believe the intent of this section is to allow for us to not provide 
sprinklers on both side to a reasonable degree, meaning we’re able to get water 
on both sides of the obstruction as long as its not a structural member.

Thanks,

[cid:image001.jpg@01D9532B.C20050C0]

[cid:image002.png@01D9532B.C20050C0]


Dane Long, AET
Engineering Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  
67401<https://www.google.com/maps/search/1383+W.+North+Street%C2%A0+Salina,+KS%C2%A0+67401?entry=gmail&source=g>


From: Anthony Johnson 
<mountainfirepr...@gmail.com<mailto:mountainfirepr...@gmail.com>>
Sent: Thursday, March 9, 2023 2:26 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Duct obstruction criteria in LH attic

The 3x rule is the only one we think would apply but it only applies to 
structural components.

Best Regards,
Anthony Johnson
Mountain Fire Protection
'Saving Lives and Valuing Property'

On Thu, Mar 9, 2023 at 12:58 PM Taylor Schumacher 
<tay...@sfsprinkler.com<mailto:tay...@sfsprinkler.com>> wrote:
When you cannot apply one of the obstruction rules, it does not mean that there 
isn’t an obstruction.

If you think about this scenario the same way you would with sprinklers 
directly attached to a pipe, that’s where to start. Look at the 3x rule or 
sprinklers on each side.


Taylor Schumacher
Security Fire Sprinkler<http://www.j-berd.com/>
1 Industrial Blvd | Sauk Rapids, MN 
56379<https://www.google.com/maps/search/1+Industrial+Blvd+%7C+Sauk+Rapids,+MN+56379+Office:+320?entry=gmail&source=g>
Office: 
320<https://www.google.com/maps/search/1+Industrial+Blvd+%7C+Sauk+Rapids,+MN+56379+Office:+320?entry=gmail&source=g>.656.0847
 | Direct: 320.640.7050

From: matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com> 
<matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>>
Sent: Thursday, March 09, 2023 12:37 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Duct obstruction criteria in LH attic

I believe however, the intent of the section must still be applied. Water on 
both sides.
Not sure in the 13 edition the location, but in the 19 it is 10.2.7.1.2.
We are referred back to it as applicable from the 3 times section.

Sprinklers spaced on opposing sides, not to exceed the max half distance.

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>
www.FergusonFire.com<http://www.fergusonfire.com/>

From: Anthony Johnson 
<mountainfirepr...@gmail.com<mailto:mountainfirepr...@gmail.com>>
Sent: Thursday, March 9, 2023 11:24 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Duct obstruction criteria in LH attic

I have an elementary question but know there are varying opinions on the topic. 
The situation is a tight unused attic space in a LH occupancy. Our upright 
sprinkler deflector will be 3" above the ductwork. Evaluating all of the 
obstruction criteria presented in NFPA we've essentially came to the conclusion 
that the ductwork would not pose an obstruction but came to this conclusion 
mainly by process of elimination. The beam-rule would not apply since the 
ductwork is below the deflector. The 3X rule is only for structural components 
in light and ordinary hazards and the 'wide obstruction' rule would not apply 
since the ductwork is only 24" wide.  That only leaves the 'suspended or floor 
mounted vertical obstructions' rule of 8.6.5.2.2 ('2013 ed) but it specifically 
mentions free standing partitions, privacy curtains and "similar obstructions". 
I don't think duct-work is a similar obstruction. I would like to have my ducks 
in a row if this design approach should be questioned but also want to make 
sure I have a sound design. Is our reasoning correct that essentially if the 
sprinkler deflector is above the duct water will spray on both sides and the 
duct would not pose as an obstruction?

Best Regards,
Anthony Johnson
Mountain Fire Protection
'Saving Lives and Valuing Property'

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>


--
Greg McGahan
Genesis Fire Services, LLC
4912 Glover Lane. Milton, FL 
<https://www.google.com/maps/search/4912+Glover+Lane.+Milton,+FL%C2%A0+32570?entry=gmail&source=g>
 
32570<https://www.google.com/maps/search/4912+Glover+Lane.+Milton,+FL%C2%A0+32570?entry=gmail&source=g>
P- 850-637-8535
C- 850-712-9555

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
--
Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
Sr. Manager, Engineering and Technical Services
American Fire Sprinkler Association

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
--
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My iPhone

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to