The annex clarifies that any object within the 18” is considered an
obstruction and you are required to use the 3X or bean rule

On Thu, Mar 9, 2023 at 4:51 PM Kevin Hall <kh...@firesprinkler.org> wrote:

> Dane is correct.
>
> We get this question a lot through the Technical Review submissions, and
> the response is pretty cut and dry.
>
> The three times rule does not apply to non structural members in light and
> ordinary hazard occupancies and because the deflector is located above the
> duct, water is able to spray on both sides, so it can be considered a
> noncontinuous obstruction. No additional protection is not required.
>
> -Kevin
>
> On Thu, Mar 9, 2023 at 5:08 PM Greg McGahan <g...@genesisfireservices.com>
> wrote:
>
>> With all due respect Dane - read the annex,  it specifically addresses
>> that issue.
>>
>> On Thu, Mar 9, 2023 at 3:42 PM Dane Long <da...@bamfordfire.com> wrote:
>>
>>> Anthony,
>>>
>>>
>>>
>>> I feel there might be a few sections you need to look at regarding this
>>> question.
>>>
>>>
>>>
>>> For me I would start at *8.6.5.2 Obstructions to Sprinkler Discharge
>>> Pattern Development.*
>>>
>>>
>>>
>>> *8.6.5.2.1.1 *Continuous or noncontinuous obstructions less than or
>>> equal to 18 in. (457 mm)
>>>
>>> below the sprinkler deflector that prevent the pattern from fully
>>> developing shall comply with
>>>
>>> 8.6.5.2.
>>>
>>>
>>>
>>> The section above lays the ground work for the 18in requirement
>>> (8.6.5.2). Then I would look at *8.6.5.2.1.3* Minimum Distance from
>>> Obstructions.*
>>>
>>>
>>>
>>> *8.6.5.2.1.4* *For light and ordinary hazard occupancies, structural
>>>
>>> members only shall be considered when applying the requirements
>>>
>>> of 8.6.5.2.1.3.
>>>
>>>
>>>
>>> IMHO Because it specifically says “structural members only shall be
>>> considered” I believe the intent of this section is to allow for us to not
>>> provide sprinklers on both side to a reasonable degree, meaning we’re able
>>> to get water on both sides of the obstruction as long as its not a
>>> structural member.
>>>
>>>
>>>
>>> Thanks,
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> *Dane Long, AET*
>>> *Engineering Technician *| *Bamford Fire Sprinkler Co., Inc.*
>>> P:    *785.825.7710*
>>> F:    *785.825.0667*
>>> A:   *1383 W. North Street  Salina, KS  67401
>>> <https://www.google.com/maps/search/1383+W.+North+Street%C2%A0+Salina,+KS%C2%A0+67401?entry=gmail&source=g>*
>>>
>>>
>>>
>>>
>>>
>>> *From:* Anthony Johnson <mountainfirepr...@gmail.com>
>>> *Sent:* Thursday, March 9, 2023 2:26 PM
>>> *To:* Discussion list on issues relating to automatic fire sprinklers <
>>> sprinklerforum@lists.firesprinkler.org>
>>> *Subject:* [Sprinklerforum] Re: Duct obstruction criteria in LH attic
>>>
>>>
>>>
>>> The 3x rule is the only one we think would apply but it only applies to
>>> structural components.
>>>
>>>
>>>
>>> Best Regards,
>>>
>>> Anthony Johnson
>>>
>>> Mountain Fire Protection
>>>
>>> 'Saving Lives and Valuing Property'
>>>
>>>
>>>
>>> On Thu, Mar 9, 2023 at 12:58 PM Taylor Schumacher <
>>> tay...@sfsprinkler.com> wrote:
>>>
>>> When you cannot apply one of the obstruction rules, it does not mean
>>> that there isn’t an obstruction.
>>>
>>>
>>>
>>> If you think about this scenario the same way you would with sprinklers
>>> directly attached to a pipe, that’s where to start. Look at the 3x rule or
>>> sprinklers on each side.
>>>
>>>
>>>
>>>
>>>
>>> *Taylor Schumacher*
>>>
>>> Security Fire Sprinkler <http://www.j-berd.com/>
>>>
>>> 1 Industrial Blvd | Sauk Rapids, MN 56379
>>> <https://www.google.com/maps/search/1+Industrial+Blvd+%7C+Sauk+Rapids,+MN+56379+Office:+320?entry=gmail&source=g>
>>>
>>> Office: 320
>>> <https://www.google.com/maps/search/1+Industrial+Blvd+%7C+Sauk+Rapids,+MN+56379+Office:+320?entry=gmail&source=g>.656.0847
>>> | Direct: 320.640.7050
>>>
>>>
>>>
>>> *From:* matthew.will...@ferguson.com <matthew.will...@ferguson.com>
>>> *Sent:* Thursday, March 09, 2023 12:37 PM
>>> *To:* sprinklerforum@lists.firesprinkler.org
>>> *Subject:* [Sprinklerforum] Re: Duct obstruction criteria in LH attic
>>>
>>>
>>>
>>> I believe however, the intent of the section must still be applied.
>>> Water on both sides.
>>>
>>> Not sure in the 13 edition the location, but in the 19 it is 10.2.7.1.2.
>>>
>>> We are referred back to it as applicable from the 3 times section.
>>>
>>>
>>>
>>> Sprinklers spaced on opposing sides, not to exceed the max half distance.
>>>
>>>
>>>
>>> R/
>>>
>>> Matt
>>>
>>>
>>>
>>> *Please rate our customer service
>>> <https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>*
>>>
>>>
>>>
>>> *Matthew J. Willis, CWBSP, CET*
>>>
>>> *Engineering Designer IV*
>>>
>>> *FERGUSON FIRE DESIGN, LLC*
>>>
>>> *A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC*
>>>
>>> 401 N 5th Street
>>>
>>> Suite 448
>>>
>>> Wausau, WI 54403
>>>
>>> C: 307-236-8249
>>>
>>> *matthew.will...@ferguson.com <matthew.will...@ferguson.com>*
>>>
>>> *www.FergusonFire.com <http://www.fergusonfire.com/>*
>>>
>>>
>>>
>>> *From:* Anthony Johnson <mountainfirepr...@gmail.com>
>>> *Sent:* Thursday, March 9, 2023 11:24 AM
>>> *To:* sprinklerforum@lists.firesprinkler.org
>>> *Subject:* [Sprinklerforum] Duct obstruction criteria in LH attic
>>>
>>>
>>>
>>> I have an elementary question but know there are varying opinions on the
>>> topic. The situation is a tight unused attic space in a LH occupancy. Our
>>> upright sprinkler deflector will be 3" above the ductwork. Evaluating all
>>> of the obstruction criteria presented in NFPA we've essentially came to the
>>> conclusion that the ductwork would not pose an obstruction but came to this
>>> conclusion mainly by process of elimination. The beam-rule would not apply
>>> since the ductwork is below the deflector. The 3X rule is only for
>>> structural components in light and ordinary hazards and the 'wide
>>> obstruction' rule would not apply since the ductwork is only 24" wide.
>>> That only leaves the 'suspended or floor mounted vertical obstructions'
>>> rule of 8.6.5.2.2 ('2013 ed) but it specifically mentions free standing
>>> partitions, privacy curtains and "similar obstructions". I don't think
>>> duct-work is a similar obstruction. I would like to have my ducks in a row
>>> if this design approach should be questioned but also want to make sure I
>>> have a sound design. Is our reasoning correct that essentially if the
>>> sprinkler deflector is above the duct water will spray on both sides and
>>> the duct would not pose as an obstruction?
>>>
>>>
>>>
>>> Best Regards,
>>>
>>> Anthony Johnson
>>>
>>> Mountain Fire Protection
>>>
>>> 'Saving Lives and Valuing Property'
>>>
>>>
>>> _________________________________________________________
>>> SprinklerForum mailing list:
>>>
>>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>>> To unsubscribe send an email to
>>> sprinklerforum-le...@lists.firesprinkler.org
>>>
>>>
>>> _________________________________________________________
>>> SprinklerForum mailing list:
>>>
>>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>>> To unsubscribe send an email to
>>> sprinklerforum-le...@lists.firesprinkler.org
>>>
>>
>>
>> --
>>
>> Greg McGahan
>>
>> *Genesis Fire Services, LLC*
>>
>> *4912 Glover Lane. Milton, FL
>> <https://www.google.com/maps/search/4912+Glover+Lane.+Milton,+FL%C2%A0+32570?entry=gmail&source=g>**32570
>> <https://www.google.com/maps/search/4912+Glover+Lane.+Milton,+FL%C2%A0+32570?entry=gmail&source=g>*
>>
>> *P- 850-637-8535*
>>
>> *C- 850-712-9555*
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> sprinklerforum-le...@lists.firesprinkler.org
>
> --
> Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
> Sr. Manager, Engineering and Technical Services
> American Fire Sprinkler Association
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org

-- 
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My iPhone
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to