Good morning, Forum! I hope everyone is having a great week!! I think I got this right, but someone is questioning me. I have an automatic standpipe with factory pressure-regulating valves (i.e., Zurn 4000). When calculating residual pressures at the inlet of the PRV to be used in the sizing charts, the question is, how much water should I be flowing in the system? One suggestion is only flowing 250 gpm at the hose valve you are sizing. The other suggestion is flowing the system demand flow per NFPA 14. In this case, that would be 750 gpm (250 gpm at each of the two most remote hose valves plus 250 gpm at the top of the only other standpipe). We are in agreement that the calculation should be a source calc to determine the actual pressure provided by the system.
Thank you, Micah Davis Ferguson Fire Design