You use the residual pressure with the full demand. However, through the nipple 
and tee to the valve you only flow 250 gpm.


Travis Mack, SET

M.E.P.CAD |

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad

________________________________
From: Greg McGahan <[email protected]>
Sent: Tuesday, October 31, 2023 4:20:27 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Pressure Regulating Valves Residual Pressures

Micah,
When you test the valves you will test each one individually flowing 250 gpm so 
therefore you have to size them individually.

On Tue, Oct 31, 2023 at 5:53 AM Micah Davis 
<[email protected]<mailto:[email protected]>> wrote:
Good morning, Forum!  I hope everyone is having a great week!!

I think I got this right, but someone is questioning me.  I have an automatic 
standpipe with factory pressure-regulating valves (i.e., Zurn 4000).  When 
calculating residual pressures at the inlet of the PRV to be used in the sizing 
charts, the question is, how much water should I be flowing in the system?  One 
suggestion is only flowing 250 gpm at the hose valve you are sizing.  The other 
suggestion is flowing the system demand flow per NFPA 14.  In this case, that 
would be 750 gpm (250 gpm at each of the two most remote hose valves plus 250 
gpm at the top of the only other standpipe).  We are in agreement that the 
calculation should be a source calc to determine the actual pressure provided 
by the system.

Thank you,
Micah Davis
Ferguson Fire Design

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>


--

Greg McGahan

Genesis Fire Services, LLC

4912 Glover Lane. Milton, FL 32570

P- 850-637-8535

C- 850-712-9555
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to