On Wed, Nov 17, 2010 at 7:59 PM, Doug Hughes <[email protected]> wrote:

> I'll reemphasize some earlier points and make some of my own.
>
> On 11/17/2010 11:37 AM, Daniel Clark wrote:
> > Looking for a UPS system that:
> >
> > 1. Runs off of US 115V / 20A
> That isn't much power. Remember, you can only use 16A of a 20A circuit,
> that limits the size of your UPS and your load to about 1.8KW. That's
> not a heckuva a lot. I'd definitely recommend at least going to 220V (or
> 208V, depending upon your building electric power plant)
> > 2. Can handle frequent extended power outages while continuing to
> > provide power to computers and HVAC systems (so amp spikes will be
> > common)
> add batteries for run time. Just remember, the more batteries you have
> and the closer you get it to specifications, the longer it's going to
> take to charge that baby.
> I'd give at least a 20% leeway on the input side.
>
> Acutally more about 1.2KW if you think the best case. He's estimating a 16
hour charge cycle followed by a 8 hour discharge cycle. So during the 16
hour charge cycle, the 115V/20A must charge the battery as well as provide
for the HVAC and the computer. Since there's a 2-1 ratio of charge vs
discharge time, out of your 1.8KW you have to give at least 0.6KW  to
charging the battery (all best case).