> 5 amps per node! Woweee! Those would be some beastly servers. I would
> expect a reasonable server as described by Ski to be closer to 2 amps.

The best thing to do is to buy something like a Kill-A-Watt, and put your
server under load, and measure it.  Record the VA, the W, and the A.  I
normally inflate all of these measurements 10-20% just for the heck of it.
Keep a spreadsheet of all the servers, make sure you don't exceed 80% of
your power circuit A's, or 90% of the UPS VA's or W's.

I do this for every server I have, and the results vary enormously per
server.  Late model Dell servers are extremely power efficient, and your 2A
estimate might be reasonable, even generous.  However, I have some old model
Dells that require 460 VA (4A) and I have a recent Sun fileserver that
requires about 550VA (5A).