Edward Ned Harvey wrote:
>> 5 amps per node! Woweee! Those would be some beastly servers. I would
>> expect a reasonable server as described by Ski to be closer to 2 amps.
> 
> The best thing to do is to buy something like a Kill-A-Watt, and put your
> server under load, and measure it.  Record the VA, the W, and the A.  I
> normally inflate all of these measurements 10-20% just for the heck of it.
> Keep a spreadsheet of all the servers, make sure you don't exceed 80% of
> your power circuit A's, or 90% of the UPS VA's or W's.
> 
> I do this for every server I have, and the results vary enormously per
> server.  Late model Dell servers are extremely power efficient, and your 2A
> estimate might be reasonable, even generous.  However, I have some old model
> Dells that require 460 VA (4A) and I have a recent Sun fileserver that
> requires about 550VA (5A).
> 

Killawatt is great, but typically does not capture the initial spike when you 
turn the machine on. You should check the manufacturer specs.

-- 
Yves.
http://www.sollers.ca/

_______________________________________________
Tech mailing list
[email protected]
http://lopsa.org/cgi-bin/mailman/listinfo/tech
This list provided by the League of Professional System Administrators
 http://lopsa.org/

Reply via email to