I would agree with you. Both redundant and diverse should ensure that a failure 
to anyone component shouldn’t have affected both supplies.

Sent from my iPhone

> On 17 Oct 2018, at 11:34, Paul Civati <[email protected]> wrote:
> 
>> On 17 Oct 2018, at 11:10 am, Robert Williams <[email protected]> wrote:
>> 
>> Thus, the overall claim that our dual feed racks have “Redundant Diverse 
>> Power” is, IMHO, false.
> 
> Unfortunately as I found out to my own cost, DC providers are vague on these 
> things and get 
> away with it.  If you walk into a facility that looks the part, and they talk 
> the talk, you can be fooled
> into believing things are redundant or even up to spec when they aren't.
> 
> The simple fact is that you have to get it all nailed down in writing or all 
> the talk of redundancy
> is finger in the air stuff.
> 
> Even then, asking for N+1 power feeds, and N+1 UPS, you almost need a 
> schematic of how
> it’s all connected to be fully aware of the failure modes.
> 
> Too much of all this stuff is marketing BS in my experience.
> 
> Finally, a lot of SLAs are so weak that they find ways of getting around 
> them, or even if you
> make an SLA claim, the payout in no way compensates for the level pain you 
> will incur during 
> down time.
> 
> -Paul-
> 
> 