That's a surprisingly small volume. The machine has one of its smaller
dimensions 3 meters. So, even 1.5m/s per second at one end would cool the
device.

2016-05-21 15:51 GMT-03:00 Alan Fletcher <[email protected]>:

> Back-of-the-envelope calculation
>
> I'm going to look at a column of air of volume V -- with area A ... and a
> height H sufficient to hold
> 1-second's worth of 1MW of heat. This has to be vented in 1 second.
>
> 1MW is 1000 kJ /second.
> Q = 1000 kJ in one second
>
> Specific heat of air at 100C is 1 kJ / (kg K)
> Density of air at 100C is r = 1kg/m^3
>
> http://www.engineeringtoolbox.com/air-properties-d_156.html
>
> Ambient air is 20C, heated air is 100C dK = 80
>
> Q = S * dK * M
>
>
> Mass = 1kg * r * V = r * V
>
> Q = S * dK * r * V
>
> Solve for V :
>
> V = Q / ( S * dK * r ) = 1000 / ( 1. * 80 * 1.)
> = 12.5 m^3 per SECOND
> = 750 m^3 per MINUTE
>
> = 26,486 CFM (Cubic Feet per Minute)
>
> That's a teeny tiny little fan!
>
> http://www.industrialfansdirect.com/wall-ventilation.html?&gclid=CIb8x7zb68wCFQEJaQodk4AMnQ
>
> ------------------------------
> *From: *"Alan Fletcher" <[email protected]>
> *To: *"vortex-l" <[email protected]>
> *Sent: *Saturday, May 21, 2016 10:37:55 AM
> *Subject: *Re: [Vo]:1 MW of heat in a 6,500 sq. ft. facility without
> industrial ventilation would be fatal
>
> This chimney sizing link doesn't really apply --- it's for natural draft
> up a chimney of a given height and diameter --  WITHOUT a fan.
>
> (The longer the chimney the higher velocity of the draft, so a given
> diameter can exhaust more heat.  They recommend "The velocity of air and
> flue gas in a smaller furnace should not exceed *2 m/s*. " -- so I
> presume that the charts are based on this, and not the maximum 10m/s.).
>
> I haven't put a ruler on the aerial photos of the vents on the roof ...
> but it looks like they could easily be 22 inches.
>
> Since  a 22-inch vent WITHOUT a fan at a velocity of 2 m/s can handle 1MW,
> it seems likely that a vent WITH a fan could also do so.
>
> There's probably a vent/fan sizing chart somewhere, but this isn't it.
>
> ------------------------------
> *From: *"Jed Rothwell" <[email protected]>
> *To: *"vortex-l" <[email protected]>
> *Sent: *Saturday, May 21, 2016 9:16:31 AM
> As I said, 1 MW in this space would be like running 16 space heating
> furnaces continuously without thermostats. To remove that much heat, you
> need a 22" vent and a large fan. An expert from I.H. would have to confirm
> this ventilation equipment is installed and working to confirm the claim. 1
> MW of heat release calls for at least at 22" vent:
>
> http://www.engineeringtoolbox.com/chimney-sizing-d_175.html
>
>


-- 
Daniel Rocha - RJ
[email protected]

Reply via email to