-----Original Message-----
From: Glen Bounds [mailto:[EMAIL PROTECTED]]
Sent: Friday, September 14, 2001 9:15 AM
To: Foxboro DCS Mail List
Subject: Re: PLC Question


First, thanks for all the responses.

Second, I have issues with all of the listed methods of communication
from ControlLogix to I/A because of the following reasons:

> 1. AB Integrator 30 to AB 1770-KF2 or 1779-KFL DH+ module in single or
> redundant ControLogix configuration.

I have nine overloaded AB30's connected to one PLC-3 that I plan on updating
to a ControlLogix 5550.  This is absurd.  I would like to have something
LIKE
an AB30 (with no hard drives, moving parts, configure in ICC, ...) but with
a
much larger capacity - like a CP60 communicating over Ethernet to
ControlLogix.

> 2. AW51 or AW70 with Ethernet interface, FoxBlocks and AB Interchange or
> RSLinx software.

I actually purchased AB Interchange for Solaris and was considering
installing it
when I realized how much maintenance and configuration is required.  One of
our plants does us this method and is not happy with the results.

> 3. AW70 with DH+ interface, FoxBlocks and AB RSLinx software.

If it has a "70" anywhere in the model number, it will not reside in my
control
system.  (Sorry, Foxboro!)

> 4. Micro I/A with AB Ethernet interface.

This was actually something I was very interested in until I found out the
true
performance and it isn't much better than the AB30.  I would still end up
with
many stations.

> 5. AW70 with FoxBlocks and DDE I/O Gate through a serial or Ethernet
> interface which addresses data in the native ControLogic naming structure.

See answer for #3.

> 6. AW51 or AW70 through an Ethernet interface with a third party OPC
> software which addresses data in the native ControLogic naming structure.

This is what I will probably have to end up doing.  AW51 with a third party
OPC server.  I just wish I didn't have go this way.  It has a hard drive,
has
to be configured a couple of places instead of one, and I will have to deal
with finger pointing when something goes wrong.

So, in conclusion, I want a "CP60" like performance and form factor, with
the ability to configure C:B.P directly in ICC or FoxCAE communicating
over fast Ethernet.  We have many plants around the world that could use
this technology today.  Is that too much to ask?


Glen Bounds
[EMAIL PROTECTED]
Corn Products International



----- Original Message -----
From: "Jason Wright" <[EMAIL PROTECTED]>
Subject: RE: PLC Question


> Glen,
>
> I don't think there is a real good answer, but I've seen it done. I have
> copied some old information I found below for reference (from Foxboro
tech).
> There are several options depending on the amount of data and type of
> communications. From the Foxboro perspective, the easiest way would be to
> communicate to the ControlLogix as a PLC-5. This would require a little
bit
> of configuration on the Rockwell side. I hope this is helpful.
>
> Regards,
> Jason
> ___
> Jason Wright
> Regional Technical Specialist
> ControlSoft
> (216) 397-3900 x201
>
>
> A-B ControlLogix PLC's
>
> Many Foxboro customers are purchasing the new Allen Bradley ControLogix
PLC
> and asking how would we interface it to I/A Series. The ControLogix
product
> is designed around their new ControlNet data highway and uses an object
> oriented data naming structure. Fortunately, Allen Bradley also supports
> Ethernet and DH+ with PLC5 data table structure so that all of our
> traditional interfaces can be used. When a data object (up to 40
characters
> in length) is created, a pull-down menu is available to assign the data
> object to a PLC5 data table. In addition, Allen Bradley will be
introducing
> a fault-tolerant ControLogix configuration with two processors and shared
> I/O. As a result, we can interface via the following methods:
>
> 1. AB Integrator 30 to AB 1770-KF2 or 1779-KFL DH+ module in single or
> redundant ControLogix configuration.
> 2. AW51 or AW70 with Ethernet interface, FoxBlocks and AB Interchange or
> RSLinx software.
> 3. AW70 with DH+ interface, FoxBlocks and AB RSLinx software.
> 4. Micro I/A with AB Ethernet interface.
> 5. AW70 with FoxBlocks and DDE I/O Gate through a serial or Ethernet
> interface which addresses data in the native ControLogic naming structure.
> 6. AW51 or AW70 through an Ethernet interface with a third party OPC
> software which addresses data in the native ControLogic naming structure.
>
> -----Original Message-----
> Subject: Re: PLC Question
>
>
> I for one would be interested in some more detailed information.
>
> I have asked Foxboro about this for a couple of years now with
> no results.
>
> Glen Bounds
> [EMAIL PROTECTED]
> Corn Products International
>
>
>
> ----- Original Message -----
> > Foxboro does not yet endorse connectivity to ControlLogix.
> >
> > We (FeedForward, a Foxboro Systems Integrator) have, however,
successfully
> > integrated the two for one of our customers.
> > I was not directly involved with this project, but from my
understanding,
> it
> > requires no more than entering the correct (but not intuitively obvious)
> > parameters in the ABSCAN blocks, and also requires the setup of aliases
in
> > the ControlLogix processor.
> >
> > If you are interested, let me know and I can get you more detailed
> > information by prodding a couple of co-workers.
> >
> >
> > Mark Dumond
> > mailto:[EMAIL PROTECTED]
> > Senior Applications Engineer
> > FeedForward, Inc.
> > 1341 Canton Road, Suite H1
> > Marietta, GA  30066
> >
> >
> > -----Original Message-----
> > We have the 51A series of APs and WPs running 6.1.1 I/A software.  We
have
> > installed several AB30 Gateways that use KF2 modules for the AB
interface
> to
> > PLC5s.  Now, we are considering to install a ControLogix PLC.  Does
anyone
> > have experience with this type of set up?



-----------------------------------------------------------------------
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]

-----------------------------------------------------------------------
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]

Reply via email to