www.interlockkit.com - they stock and custom make interlock bypasses
including multiple breakers.

Square D also makes a 400 A panel which excepts either bolt on or snap on
QO breakers.





*Kirk Herander / **kirkh@vermont.solar <kirkh@vermont.solar>*

*Owner|Principal, VT Solar, LLC*

*Celebrating our 33st Anniversary 1991-2024!!*

dba Vermont Solar Engineering

802.559.1225


On Wed, Mar 27, 2024 at 3:15 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Jason:
>
>
>
> Replies below.
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* Jason Szumlanski [mailto:ja...@floridasolardesigngroup.com]
> *Sent:* Wednesday, March 27, 2024 3:12 AM
> *To:* will...@millersolar.com
> *Cc:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Sol-Ark 15K AC Output
>
>
>
> William,
>
>
>
> Thanks for the information on grid peak shaving. That is what I thought
> could be done. The description is a misnomer of sorts (like a lot of things
> in Sol-Ark lingo). It's a bit hard to follow and not nearly well
> enough documented, particularly with respect to parallel systems.  You
> are welcome.  The Sol-Arc manual is not a great manual in any regards.
>
>
>
> I follow what you are saying about using the 80A input breakers. The
> problem I have is that you must set the generator kW to 36,000 in the
> master inverter, not 9,000W in each inverter. The concept of "underrating"
> the input breakers theorizes that each inverter will share the generator
> pass-through equally. I do not know that to be the case. And what happens
> if the three slave inverters have a fault or are turned off? That would
> allow the single master to pass through the full generator supply.
> Obviously this trips the 80A input breaker and protects the conductors, but
> I feel that is a design deficiency when a single inverter is fully capable
> of passing through all 150A.  You may be designing for an eventuality
> that will never occur:  If the inverters fail then they should be repaired
> or replaced.  While awaiting repair the bypass will keep your loads powered
> at full capacity.
>
>
>
> On top of that, I don't think the 80A output breakers are sufficient
> because each inverter can peak shave 50A with inverter power from the
> batteries. Add that to the theorized balanced 37.5A "grid" input, and you
> are at 87.5A of possible throughput.  I am not sure why you are designing
> to deliver more than the inverters will produce.  The generator support
> function is intended to assist powering loads when the generator is
> undersized.  I define that as the generator ampacity being less than that
> of the inverter system.  The 36kVA generator is greater in ampacity than 4
> Sol-Arc 15s.  You can turn the generator support function down or off in
> the Sol-Arc.  I would recommend it be set to off for this project.  (If
> there are to be occasional loads that are greater than the inverters can
> deliver, like a welder or a car charger, with the plan I suggested you have
> a generator-fed panel that can feed those occasional large loads with the
> generator running.)
>
>
>
> But assuming the 80A input/output concept works, other than a panelboard
> with bolt on breakers, what low-cost load center allows you to fasten four
> 80A backfed breakers? If this is available, I could use a recommendation.
> The load centers I am familiar with only have provisions for one fastened
> backfed breaker.  I use to specify bolt-on panels for this but I came to
> believe this is overkill.  QO breakers are held in place by the panel cover
> that overlaps the breakers.  Other breakers are configured so the contact
> points for the breaker bus are recessed.  You need to convince your AHJ
> that this satisfies the requirement.  Part of the discussion should include
> the point that off-grid systems are specialized and people that do not
> understand them should not be working on them (or judging them-- is what I
> tell inexperienced plan-checkers).
>
>
>
> With respect to the bypass, I would usually use a DPDT switch to
> accomplish this, Even for 400A bypasses, there seems to be a relatively
> cost effective option in the Ronk 7416 (which to date I have not used). I
> get the concept for smaller (<=100A) generators that you could use a
> generator interlock on an off-the-shelf load center. But they typically
> only allow a single backfed 2-pole breaker, whereas something like a Square
> D QO panel with a backfed 150A breaker requires 4 spaces and is
> incompatible with the interlock device.  Since bypass is an emergency
> condition, I sometimes limit my bypass to 100 amps.  If you want full
> bypass ampacity you can build an interlock to accommodate any size
> breaker.  Here
> <https://millersolar.com/MillerSolar/Portfolio/Commercial/RM/Interlock.JPG>
> is a photo of a large frame breaker being interlocked.  Here
> <https://millersolar.com/MillerSolar/Portfolio/Commercial/RM/RM_Interlock.pdf>
> is a design sketch exploring multiple interlock options.
>
>
>
> Always, this is a great discussion and specific recommended equipment is
> appreciated.
>
>
> Jason Szumlanski
>
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
>
> Florida Certified Electrical Contractor EC13013208
>
>
>
>
>
> On Wed, Mar 27, 2024 at 12:33 AM William Miller <will...@millersolar.com>
> wrote:
>
> Jason:
>
>
>
> Sol-Arc does provide generator support.  They call it “grid peak load
> shaving” and it is described on page 22 of the manual.  Below is an excerpt.
>
>
>
> *Error! Filename not specified.*
>
>
>
> For those that may not be familiar with the concept of generator support,
> here is how I describe it:  The inverter(s) are programmed for the
> generator capacity.  If the generator is powering loads and the demand
> exceeds that programmed generator capacity, the inverter can start
> inverting and synchronize output to the generator to add power.  This is
> only possible if battery charge levels are adequate.  In the Sol-Arc this
> function can be adjusted or turned off.
>
>
>
> Regarding my recommendations on wire sizing:  I may have done a poor job
> describing how I see your project best approached.  Below is a diagram that
> may do a better job.  Power flow is from left to right:
>
>
>
> *Error! Filename not specified.*
>
>
>
> If you follow what I am laying down, you can see there is no single
> inverter or inverter wire that can pass or create more than 80 amps.  Ergo
> #4 copper.  The money and time you save can easily purchase 8 80 amp
> breakers.  If you look at Diagram 10 in the April 5, 2022 Sol-Arc manual
> you will see this concept shown, albeit without bypass capabilities and
> with a separate “LOAD AC Combiner panel.”  The separate panel is
> redundant,-- all of the breakers in the AC combiner panel could be located
> in the “Main Breaker Panel.”
>
>
>
> Contemplate this:  Just because an inverter can pass-through 200 amps,
> does not mean it can pass through amps above what the input breaker
> provides.
>
>
>
> I hope I have been more clear.  I also hope you don’t spend a lot of money
> on and wrassle wire larger than is needed.
>
>
>
> Call me if I can help in any way.
>
>
>
> William
>
>
>
> PS:  Below is a diagram on how to provide bypass.  I tried to depict the
> bypass interlock graphically.  The point is you cannot turn *on* the
> bypass breaker without turning *off* the inverter output breakers.  See
> photos of the actual hardware on the web page linked below.  I find bypass
> very handy because if there is an inverter or battery failure the client
> can restore power immediately and I can respond at a more convenient time.
>
>
>
>
>
> *Error! Filename not specified.*
>
>
>
>
>
> Wm
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
> <https://mailtrack.io/l/3deb3f7f51095bae3cfd8b42df221b4dca044e0a?url=http%3A%2F%2Fwww.millersolar.com%2F&u=1613865&signature=79e9e2e0e8d662d0>
>
> CA Lic. 773985
>
>
>
>
>
> *From:* Jason Szumlanski [mailto:ja...@floridasolardesigngroup.com]
> *Sent:* Tuesday, March 26, 2024 6:41 PM
> *To:* William Miller; RE-wrenches
> *Subject:* Re: [RE-wrenches] Sol-Ark 15K AC Output
>
>
>
> #4 wire as the output of each inverter is definitely not adequate, as each
> inverter can pass through 150A of generator power. In theory it would be
> spit across all four, but that doesn't matter. It's an open spigot, so at a
> minimum the output conductors would need to be 150A rated in my opinion.
> The complication arises when you don't know whether the inverter can
> supplement this AC output all the way to the 200A load OCPD integral to the
> inverter. For that reason, I believe you need to size the output conductors
> to 200A, not 150A in this case. I am trying to find out definitively if
> generator support mode is supplied by Sol-Ark s.
>
>
>
> As for paralleling the outputs, landing the outputs on breakers becomes
> problematic and very expensive. Since the outputs need to be 150A minimum
> or 200A maximum (as discussed previously), how would you do a 400A
> panelboard with four of these large breakers in it, keeping in mind that
> all four need to be fastened as backfed main breakers? I don't see a
> practical way to make that happen.
>
>
>
> The same thing applies to combining the generator inputs. You would need 4
> x 150A backfed breakers, all fastened to the bus. Is there a cost effective
> way to accomplish this?
>
>
>
> Serviceability and bypass are obvious desires, but at what cost? If an
> inverter needs to be taken out of service, it's fairly easy to remove the
> supply and load conductors. And this highlights my issue... What if three
> of four inverters need to be removed from service? Then absolute 150A
> generator power can flow through the remaining single inverter, meaning the
> output conductors need to be sized accordingly.
>
>
>
> Jason
>
>
>
>
>
> On Tue, Mar 26, 2024, 9:15 PM William Miller via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Jason:
>
>
>
> I am wondering on the advisability of hardwiring the outputs of all four
> inverters together.  If one inverter fails the other three can backfeed
> into it without any means to disconnect the failed inverter and without
> over-current protection.  Have you considered landing the output of each
> inverter on a separate, appropriately sized 2 pole breaker in the output
> load-center?
>
>
>
> In the same vein, how are you feeding generator input into the inverters?
> Are these hard-wired paralleled as well?  You might consider having the
> generator feed a dedicated load-center with an appropriately sized breaker
> to feed each inverter.  You protect the conductors as required and you can
> isolate any inverter for service
>
>
>
> What size should these breaker be?  If your inverter can supply 62.5 AAC,
> upsizing for continuous duty and to the next higher standard breaker size
> you get 80 amps.  If you use 80 amp breakers into and out of each Sol-Arc
> you require #4 copper at 75°C.  Each inverter and all of the conductors are
> protected for the max current they will see and you get the combined
> amperage at your output.  There should be no need to run 400 amp wire.
>
>
>
> BTW, you can easily contrive a bypass system by creating a sliding
> mechanical interlock.  You run an appropriately sized feeder between the
> generator fed and inverter fed panels.  The bypass breaker in the
> inverter-fed panels is interlocked with the inverter output breakers.  The
> installation might look like this
> <https://mailtrack.io/l/e90ccdb6d87171ee02747bc52f4aa4c7f57064ca?url=https%3A%2F%2Fmillersolar.com%2FMillerSolar%2FPortfolio%2FInverters%2Fbattery_iinverters%2FChimney_Rock%2FChimney_rock.html&u=1613865&signature=38c4488f52bdc385>.
> This is way cheaper and easier than installing an additional 200A,
> double-throw safety switch.  (A home-made interlock may not be listed but
> what is the worse that will happen if all breakers are on?  The inverters
> will detect backfeed and shut down.  No harm will come of it.)
>
>
>
> Hope this helps.
>
>
>
> William
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
> <https://mailtrack.io/l/7e13e4b3b56e5496552a9f21904f404635490f63?url=http%3A%2F%2Fwww.millersolar.com%2F&u=1613865&signature=6c634bcc39faeca3>
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Jason Szumlanski via RE-wrenches
> *Sent:* Tuesday, March 26, 2024 2:26 PM
> *To:* RE-wrenches
> *Cc:* Jason Szumlanski
> *Subject:* [RE-wrenches] Sol-Ark 15K AC Output
>
>
>
> I am going to have a quad-stack of Sol-Ark 15K for an off-grid 120/240V
> system with a 150A generator. I know the max real power is 62.5A each
> inverter including battery and PV. That would be 62.5A x 4 = 250A total. I
> intend to connect the output of the 4 inverters together with a 5-port
> Polaris tap, with the output of the Polaris Tap going to a 400A main lug
> only panelboard.
>
>
>
> My question revolves around the 200A passthrough capability for the
> generator, which is 150A max output and would be connected to the Grid
> input on each inverter. Since each inverter would need to handle the full
> pass-through current, that would require minimum 150A conductors on the
> input side of each inverter. I am under the impression that the inverters
> can supplement the "grid" or generator in this case if the current exceeds
> the available input. That means the inverter would have 150A of input plus
> 62.5A  of inverter power for a total of 212.5A. But there is a 200A load
> OCPD, so I could size the load conductors from each inverter for 200A.
>
>
>
> Obviously the 4 inverters can only pass through 150A from the generator in
> total, which would probably be split among them, but could go through a
> single unit if the rest fail.
>
>
>
> Now, is it possible for each inverter to output 62.5A each PLUS 150A of
> generator power spread across them for a total of 400A? That is important
> because I would need to size the combined output conductors for 400A if
> that is the case.
>
>
>
> I guess I'm not clear on how Sol-Ark 15K handles grid/generator
> assist/supplement. It does not seem to be documented clearly.
>
>
>
> Jason Szumlanski
>
> Florida Solar Design Group
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
> <https://mailtrack.io/l/5f5ecb45fa0ccb0d11cccafb2c0f97618fa79e70?url=http%3A%2F%2Fre-wrenches.org&u=1613865&signature=fdeabe6cf92ab25a>
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/l/020c93287659704ad1c52093f304e341f5d0498c?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&u=1613865&signature=3efe2a50c80c33a7>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://mailtrack.io/l/52cc42ac082af0eeca614dbe4c0d638d5d336ad1?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&u=1613865&signature=209030a25db2ff5a>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/l/f48fe27d75d453c7157b484946d36bcdf4698ad0?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&u=1613865&signature=42f5213a717423ce>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/l/076ca2ee1c125ea468d20fa3e4c460f58b568b0d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&u=1613865&signature=96238382e5fb3b50>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://mailtrack.io/l/d6a9b62f894eaeef0e7d7d91724b427d785ae85e?url=http%3A%2F%2Fwww.members.re-wrenches.org&u=1613865&signature=e4238f11cf07c6fa>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to