am looking for
confirmation that the above is accurate.
Regards,
Peter Tarver
ptar...@ieee.org
-
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
for sale to the public.
If taken very conservatively (as Japan tends to be), this would
apply to all ac/dc power supplies. Does anyone know if this marking
requirement applies to power supplies that are part of a kit or sold
as spares?
Regards,
Peter Tarver
ptar..
to include simple IEEE
802.3 circuits, which were excluded from such testing under 60950-1
(where ITIC had dictated to test houses, "thou shalt not place
transients on mine network circuits").
As a relative newcomer to 62368-1, I am looking for confirmation
that the above is accurate.
Regar
Hi, Doug.
The control systems are internal to the product, but it relies on
power provided by the host equipment.
Peter Tarver
ptar...@ieee.org
From: Doug Nix
Subject:Re: [PSES] Applicability of the Machine Directive
Date sent: Thu, 24 Sep 2020 17:05:32 -0400
Copies
Hello.
For the following, I have (nearly) concluded that the
Machinery Directive applies, but I have some lingering
uncertainty. I'm looking for reasonable arguments to
say that it does or doesn't apply before I dive
headlong into the tasks related to supporting a
declaration against the
tardant and possibly a high percentage of inorganic fill
material (e.g., glass fibers, etc.).
Peter Tarver
From: Ted Eckert <07cf6ebeab9d-dmarc-requ...@ieee.org>
Sent: Monday, September 16, 2019 1:56 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Do We Need Flame Retardants in Elect
I note that my subscription at my home account was not unsubscribed
(POP3).
Peter Tarver
Date sent: Wed, 24 Apr 2019 17:10:55 +
Send reply to: Peter Tarver
From: Peter Tarver
Subject:Re: [PSES] Automated listserv error message
Originally to: Steve Brody
To: EMC
Ditto, but using Outlook on an Outlook 365 server. Mike was very responsive and
restored my subscription.
Peter Tarver
From: Steve Brody
Sent: Wednesday, April 24, 2019 8:38 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Automated listserv error message
Yes - same message and issue. I
All -
I just received an unsolicited e-mail from the address of
jrallen-at-productsafetyinc.com. Beware the probable phishing and malware link,
if you receive the same.
Regards,
Peter L. Tarver
-
This message is from the IEEE
As a subscriber to this list from April, 1995, this is a welcome addition. I
echo John W’s concern for subscribers to not abuse this.
Peter Tarver
From: Jim Bacher
Sent: Monday, December 17, 2018 08:55
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] File Attachments and the emc-pstc email list
it’s a short
leap to including the in the certification.) The product category for Factory
Automation Equipment doesn’t limit the applications to indoor use. Subject 2011
is used in conjunction with NFPA 79.
Regards,
Peter Tarver
From: Chester Summers
Sent: Wednesday, October 17, 2018 10:21
(combo and
ring).
Peter Tarver
From: Scott Aldous
Sent: Wednesday, March 21, 2018 08:33
Hi James,
The UL safety standard for PV inverters, UL 1741, makes normative reference to
IEEE 1547 and IEEE 1547.1 in Section 46. IEEE 1547.1, in clause 5.5 on
interconnection integrity, makes normative
negotiate, make sure you build in some head room for load changes so you don’t
have to repeat testing when someone gets a clever idea for how to repurpose
your design.
Regards,
Peter Tarver
From: Richard Nute [mailto:ri...@ieee.org]
Sent: Friday, December 08, 2017 13:09
To: EMC-PSTC
(or the same) approach accepted by IC?
Regards,
Peter Tarver
> -Original Message-
> From: Dennis Ward [mailto:dennis.w...@pctest.com]
> Sent: Tuesday, October 31, 2017 13:07
> To: Peter Tarver <ptar...@enphaseenergy.com>; EMC-
> p...@listserv.ieee.org
> Subject: RE: shor
automated production line.
Regards,
Peter Tarver
-
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>
All emc-
2015/863/EU will
be incorporated into 2011/65/EU? Anyone have any stories to share?
Peter Tarver
-
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send
d edition (photocopied)
>
> I'll hang onto these for a couple weeks, but they'll be in
> the recycling bin or donated to a library after that.
>
>
> Regards,
>
> Peter Tarver
>
-
This message is from the
(photocopied)
fifth edition, 1976 (original)
an erratum to the third edition (photocopied)
I'll hang onto these for a couple weeks, but they'll be in
the recycling bin or donated to a library after that.
Regards,
Peter Tarver
sides of
the border of Germany and Austria, rather than Germany as a whole.
Peter Tarver
From: Kannan Dhamodaran [mailto:kan...@india.tejasnetworks.com]
Sent: Monday, August 14, 2017 21:36
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] -60Vdc Telecom supply voltage
Thank you Joe Randolph and Bostjan
.
If an rms value is also needed, you can capture the inrush on a scope and gate
the measurement over the relevant number of line cycles.
Regards,
Peter Tarver
From: John Woodgate [mailto:jmw1...@btinternet.com]
Sent: Thursday, August 10, 2017 05:32
Well, no-one has challenged Annex B since
for the answer.
Peter Tarver
> -Original Message-
> From: Scott Xe
> Sent: Wednesday, May 31, 2017 08:55
>
> Is the minimum size of 5 mm relaxed to the legible reading
> in LVD and RED? Where and when does it introduce?
The information contained in this message
Is this not in IEC 60601-1 3.1ed?
Peter Tarver
From: Vincent Lee [mailto:08e6c8d35910-dmarc-requ...@ieee.org]
Sent: Thursday, May 18, 2017 07:03
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Surface Creepage & Air Clearance Calculator - IEC 60601-1 3.1ed
Hi all,
Good day,
(1)
coatings, but
not many have certifications for that application.
Peter Tarver
From: Richard Nute
Sent: Wednesday, May 17, 2017 12:43
Solder mask is, necessarily, a reasonable solid insulator. The trace-to-trace
insulation construction is
trace - solder mask - air - solder mask - trace
The solder
on
a board has some height, so it’s possible that, under the right circumstances,
Paschen’s could have an effect on Creepages as well as Clearances.
Peter Tarver
From: Vincent Lee
Sent: Tuesday, May 09, 2017 21:00
Hi all,
Good day,
1) May I know what is the scientific relationship between
Hi, Ralph (say hello to Sarah U also).
UL 1741, Supplement A has this as a requirement in Tables SA8.1 and SA8.2.
Peter Tarver
> -Original Message-
> From: Ralph McDiarmid
> Sent: Wednesday, May 03, 2017 10:59
>
> Has anyone been asked to perform the Unintentional
&g
This afternoon's update: the resolution of the inductive current probes I have
are limited to 10 Ma. All currents look like noise.
Peter Tarver
> -Original Message-
> From: Peter Tarver
> Sent: Wednesday, April 26, 2017 09:29
>
> Thank you, Pete.
>
> I have receive
.
For shock hazard (Let Go and Reaction), the scale is OK.
Peter Tarver
> -Original Message-
> From: Pete Perkins
> Sent: Tuesday, April 25, 2017 23:17
>
> Peter,
>
> Altho I have no experience with the Kikusui meter, I
> believe that
> you are on the right trac
is always "faulted." I can't use
the faceplate outlet for PCC (Protective Conductor Current) measurements, but I
can for touch current measurements.
Peter Tarver
> -Original Message-
> From: Richard
> Sent: Tuesday, April 25, 2017 10:42
>
> Hello Peter:
>
>
are always
there.
I plan to try an isolation transformer, a la 60950-1 to see if there's a
different response.
I have written to Kikusui and asked them a similar question. I'll report back
Peter Tarver
> -Original Message-
> From: John Woodgate
> Sent: Monday, April 24, 2017 23:30
is in good condition and went through a calibration verification
in AUG2016.
The currents are within "Measurement range setting Range 1," but the meter is
set in auto range mode. I plan some additional experiments using defined
ranges, rather than auto in the next day or so.
Pe
series?
I am aware of 61439-0, but haven't yet purchased that document to discover what
guidance it can give.
Peter Tarver
The information contained in this message may be privileged and confidential.
It is intended to be read only by the individual or entity to whom it is
addressed
of the MD, where the text Doug mentions is located, goes
on to say that they’re, “intended for lifting loads and whose only power source
is directly applied human effort.” This encompasses:
• automotive lifts and jacks
• come-alongs
• block and tackle sets (if sold as a unit)
Peter Tarver
From
you get copies of
their certification test reports to verify any claims.
Regards,
Peter Tarver
The information contained in this message may be privileged and confidential.
It is intended to be read only by the individual or entity to whom it is
addressed or by their designee. If the reader
It should be kept in mind that all of these so-called services are sales tools.
My experience with all of the agencies discussed have been less than stellar on
the delivery side, once a PO is placed.
Peter Tarver
The information contained in this message may be privileged and confidential
of competencies relative to several countries'
requirements for grid compliance of distributed generators, we received an
exorbitant quote for UL to research their own capabilities.
I have been less than impressed so far with such claims of aid, so I'm
reluctant to entertain a subscription service.
Peter
measures from 13 June 2016.
Article 50
Repeal
Directive 1999/5/EC is repealed with effect from 13 June 2016.
RED is effective now. Unless I missed something deferring it’s adoption.
Peter Tarver
From: Charlie Blackham [mailto:char...@sulisconsultants.com]
Sent: Wednesday, November 02, 2016 09:00
9703," is not a consideration. These outlines are for different
product types.
Peter Tarver
From: Brian Gregory [mailto:brian_greg...@netzero.net]
Sent: Wednesday, September 28, 2016 14:33
I'm trying to find out if UL 6703 (connectors for PV systems) is being upgraded
to UL 9703 or the other
Reminds me of a movie, Them!
From: Ed Price [mailto:edpr...@cox.net]
Sent: Wednesday, September 14, 2016 23:09
Plutonium is probably not a good answer;
The information contained in this message may be privileged and confidential.
It is intended to be read only by the individual or entity to
Brian -
UL will generally accept a Class 1 air filter. These are evaluated against UL
900.
Otherwise, it depends on the standard for the end product what requirement
apply. I recall 60950-1 accepting HF-1.
Peter Tarver
From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Monday
them guess if the next sound they heard
sound was recorded or live. Folklore to people like me, but gospel to some
audiophiles.
Peter Tarver
> -Original Message-
> From: Ken Javor
> [mailto:ken.ja...@emccompliance.com]
> Sent: Thursday, August 25, 2016 17:32
>
.
Pretty clever, but outlandishly expensive.
Peter Tarver
> -Original Message-
> From: Ken Javor
> [mailto:ken.ja...@emccompliance.com]
> Sent: Monday, August 22, 2016 19:55
>
> Next, the terms are not entirely gibberish. They may be
> unfamiliar to those not in the hi-fi
the testing was simplified to a single temperature with the
pass/fail criterion simply being the 2.0 mm diameter dimple, rather than
finding the temperature at which the 2.0 mm dimple forms.
Maybe Pete Perkins or Rich Knute recall further back than I do.
Peter Tarver
From: Carpentier
s as well and quickens thermal equilibrium. Open
face of the cube toward the benchtop. Especially nice
in drafty or heavily air conditioned areas.
Peter Tarver
-
This message is from the IEEE Product Safety Engineering Society emc-pstc
d
measurement. They will
rarely give the temperature at the location the EUT is placed.
If the EUT is large the environmental chamber needs to be much larger than
the EUT, as indicated by others.
Peter Tarver
-
This message is from the IEEE
Fine and valuable responses. Thank you.
Can anyone respond to my question?
> Has anyone else encountered this sort of requirement? The CBTL
either
> could not or would not provide a written requirement, so this
smells off.
Peter Tarver
Date sent: Fri, 26 Feb 2016 14
Howdy, howdy, howdy.
Product incorporates Type 5 component VDRs and is installed in an OVC III
environment via field wiring connections. Evaluation for a CB Scheme
Certificate and Test Report.
In recent dealings with a CBTL, I was told that the VDRs in a product
needed to be Type 2. In
We are marking a product with the RCM and have done relevant emissions
testing for the complete product. The intent from the start has been to
leverage the testing and certifications the supplier obtained to reduce
the amount of testing needed for the end product (a "modular approach" in
a global
One hopes, then, that artists will not lick their brushes or hold them in
their mouths, the same way one hopes science academy janitors will not do
the same with their mops and brooms.
Peter Tarver
> -Original Message-
> From: Brian O'Connell
>
> The chemical princi
Ralph –
I’m less familiar with the CEC, but the NEC does not preclude 208/120 V WYE
to a single-family home (residence). It all depends on how much one is
willing to pay the utility for the service and proper provisioning and
system design at the use location.
Peter Tarver
*From
. A
specific area cited was "around Boston."
Has anyone heard of or directly experienced this voltage system?
Is it split-phase or was I misinformed and it's from a WYE
connected transformer?
Peter Tarver
ptar..
All the best, Doug
doug...@gmail.com
http://www.linkedin.com/in/dougp01
On Wed, Oct 21, 2015 at 8:21 AM, Peter Tarver <ptar...@ieee.org> wrote:
Good morning.
There are oftensmall, legacy grids that you come across or hear
about.
I was recently told that some areas of the Northea
Brian of the nonburrito ilk -
This is usually called 208 V single-phase.
I'm still trying to clarify the specifics of the request.
Peter Tarver
> -Original Message-
> From: Kunde, Brian
> Sent: Wednesday, October 21, 2015 12:34
>
> snip <
>
> I have heard t
David -
Thank you.
In one case, the output was after the CDN. In the other, the CDN was not in
the circuit. I will ask for calibration screen captures with and without
the CDN on both cases. This could prove informative.
Regards,
Peter Tarver
-Original Message-
From: Schaefer
Good morning.
I'm wondering if others have experienced cases where different
manufacturers' surge test equipment (ANSI/IEEE C62.41 ring and
combination waves) with nearly identical open-circuit voltage and
short-circuit current calibrations have led to very different results. In
these cases,
potpourri to fit the application.
Regards,
Peter Tarver
*From:* Adam Dixon [mailto:lanterna.viri...@gmail.com]
*Sent:* Thursday, August 20, 2015 13:36
*To:* EMC-PSTC@LISTSERV.IEEE.ORG
*Subject:* Re: [PSES] 208V/30A/3PH NEMA 3R power distribution question
Thanks for the suggestion, Brian. I
ISO 17025 (General requirements for the competence of testing and
calibration laboratories) has some requirements related to knowing what
you’re doing.
Regards,
Peter Tarver
*From:* Brian Gregory [mailto:brian_greg...@netzero.net]
*Sent:* Wednesday, May 13, 2015 11:30
*To:* EMC-PSTC
UL recently changed a number of URLs and other items, probably as a matter
normal churn. Several bookmarks no longer worked.
This is probably a related thing that they'll work through in time.
Regards,
Peter Tarver
-Original Message-
From: Brian Oconnell
Sent: Friday, May 15, 2015
Good morning.
I am reviewing the suitability of serrated head screws in grounding and
bonding applications. I am aware that these screws are good at resisting
vibration, but I've not seen them used for grounding and bonding purposes.
I question this application since, while the serrations
Anyone know how to contact him? All contact information I have for Steven
is outdated. E-mails bounce and the last telephone number I have for him
is kaput.
Regards,
Peter L. Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or
-
From: Peter Tarver [mailto:ptar...@enphaseenergy.com]
Sent: Tuesday, September 23, 2014 3:11 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Looking for Steven Holmes, formerly of UL
Anyone know how to contact him? All contact information I
have for Steven is outdated. E-mails bounce
accepts our
business.
Regards,
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an intended
recipient, you may not review, use, copy, disclose or distribute this message.
If you received
IEC 62109-1 considers “PV circuits in general” to be OVCII.
Regards,
Peter Tarver
*From:* McDiarmid, Ralph [mailto:ralph.mcdiar...@schneider-electric.com]
*Sent:* Friday, August 08, 2014 13:57
*To:* EMC-PSTC@LISTSERV.IEEE.ORG
*Subject:* Re: [PSES] question with regard of inverter
My
Brian -
I'm looking to control smoke and fumes during component and other abnormal
conditions, as well as UL 94 testing.
Lots of food for thought. Thanks.
Regards,
Peter Tarver
-Original Message-
From: Brian Oconnell [mailto:oconne...@tamuracorp.com]
Sent: Friday, June 20, 2014
Doug –
I’m familiar with those fans. They were used in a PBX system I was
associated with in an alternate universe. Good variable speed control on
them.
I’m not sure I’ll need a spark arrestor, but I appreciate the reference.
Regards,
Peter Tarver
*From:* Douglas Nix [mailto:d
surface. A simple
stainless steel pan could transmit heat and create undesirable secondary
effects.☺ An air gap might fix that, but then I need to come up with a good
support system.
Details, details ...
Regards,
Peter Tarver
-Original Message-
From: Richard Nute [mailto:ri...@ieee.org
Hi.
I'm doing some research and am looking for recommendations for fume hoods
for abnormal condition testing for my lab. I have an opportunity to have
an exhaust to outside air system and am looking for your thoughts on what
has worked well for you in terms of cfm capacity and which
Following the link on the page to a HAR member list shows Greece is
absent.
Does anyone know the back story?
Regards,
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an intended
switch for inverter
output connections to the grid. Whether or not this switch can operate
a contactor will depend on the jurisdiction involved.
Regards,
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information
of the applicable
standard) would be deemed critical.
Regards,
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an intended
recipient, you may not review, use, copy, disclose or distribute
is a narrower concept?
In undergrad courses I attended, 'network' and 'circuit' were used
interchangeably.
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an intended
recipient, you may
be derived based on passive -v- active
components, number of nodes, or based on function. Someone will always
have a different opinion.
In the standards world, they are used interchangeably.
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential
impulse start fans is that that generate
negligible heat when stalled, but this method would remove all doubt.
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an intended
recipient, you
is an ongoing
issue for everyone involved in product safety certifications. You can try
to have a handful of alternates ready when the certification evaluation is
performed and still have this concern because there's always a less
expensive alternative available.
Peter Tarver
This email message
for branch
circuit protection and are only suitable for supplementary protection
applications, unless it's used as a part of a Listed assembly identified
for use as branch circuit protection.
QVNU2 breakers are not suitable for branch circuit protection.
Regards,
Peter Tarver
This email message
From: Brian Oconnell
Sent: Tuesday, December 03, 2013 12:31
To: EMC-PSTC@LISTSERV.IEEE.ORG
But there are, in fact, listed CBs intended for supp
interrupt protect.
I'm aware of UL Listed supplementary overcurrent protection fuses, but not
CBs. What's the product category?
Peter Tarver
are immune to being illogical or ridiculous, either by
design or through ignorance or negligence. ☺
Regards,
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an intended
recipient, you may
their web sites for these devices and get the
flavor of their certifications. Fair warning, many specs. are not
available in English.
Regards,
Peter Tarver
*From:* Brian Ceresney [mailto:bceres...@delta-q.com]
*Sent:* Thursday, November 21, 2013 15:52
*To:* EMC-PSTC@LISTSERV.IEEE.ORG
For those who don't subscribe to InCompliance magazine or track recalls
through other methods, the below link is related to a US product recall of
a relocateable power tap with surge protection.
http://www.cpsc.gov/en/Recalls/2014/Schneider-Electric-Recalls-APC-Surge-P
rotectors/
Regards,
not be
the contracted company's responsibility to take action beyond this minimal
level, unless there's a desire to play extra nice until it's time to not
play nice.
If the contracted company's legal dweebs are on the ball, they're most
likely already on these issues.
Regards,
Peter Tarver
There is occasionally much haranguing regarding how standards should be
free.
The NFPA has joined ASHRAE and
ASTMhttp://www.nfpa.org/newsandpublications/nfpa-journal/2013/september-october-2013/pov/first-word?order_src=C247to
claim otherwise.
Regards,
Peter L. Tarver
This email
to that site out of curiosity and it told me that to use the site to
look at its content, I had to allow setting cookies in my browser (I have my
browser to not allow third-party site cookies, but otherwise they're
allowed).
Must be Canadian humor.☺
Peter Tarver
This email message
.
Regards,
Peter Tarver
-Original Message-
From: Zhangguoqing (A) [mailto:zhangguoq...@huawei.com]
Sent: Monday, September 16, 2013 19:05
To: Peter Tarver; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: 答复: [PSES] question on clause 6.3 and 1.4.11
of IEC60950-1
Dear Peter,
Thanks for your reply
in this thread.
Regards,
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an intended
recipient, you may not review, use, copy, disclose or distribute this message.
If you received this message
.
Regards,
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an intended
recipient, you may not review, use, copy, disclose or distribute this message.
If you received this message in error
in
telecommunications networks, in particular modular plugs/jacks, line cords
and the like.
Regards,
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an intended
recipient, you may
at an
elevated temperature, etc.
Regards,
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an intended
recipient, you may not review, use, copy, disclose or distribute this message.
If you
You can check CENELEC’s TC 20 web site.
Regards,
Peter Tarver
*From:* Niels Hougaard [mailto:n...@bolls.dk]
*Sent:* Thursday, August 29, 2013 07:23
*To:* EMC-PSTC@LISTSERV.IEEE.ORG
*Subject:* [PSES] Standard for testing of high voltage penetrators
Dear list members,
High voltage
in further research.
Regards,
Peter Tarver
*From:* Ed Price [mailto:edpr...@cox.net]
*Sent:* Thursday, August 29, 2013 05:11
*To:* EMC-PSTC@LISTSERV.IEEE.ORG
*Subject:* [PSES] Norwegian RF Study
*The Norwegian Institute of Public Health released a study of
electromagnetic exposure
glass tube fuses crack,
ferrules become dislodged (even on solder in place fuses), when the
interrupting (breaking) capacity was too low for an application in
end-product equipment.
I'm glad the fuse will be replaced with another, more approriate type.
Peter Tarver
This email message
. If each successive fuse replacement uses the same fuse, more
of the same may result. If the product isn't returned for replacement or
discarded, the fuse might eventually be replaced with a larger rated fuse
with possible further degradation of safety.
Peter Tarver
This email message
, there was about a 3 1/2 year transition window.
Peter Tarver
-Original Message-
From: McInturff, Gary
[mailto:gary.mcintu...@esterline.com]
Sent: Friday, July 19, 2013 08:06
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] 60950 1st edition and amendments
Ha now I'm getting new
Photovoltaic inverters and related equipment.
Poor service and lousy communications are leading me to consider a move.
Any input will be accepted.
Regards,
Peter L. Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged
*From:* McInturff, Gary [mailto:gary.mcintu...@esterline.com]
*Sent:* Thursday, July 18, 2013 16:23
Anybody know the Docopocoss (or whatever on that) on IEC 60950-1:2001,
First Edition
Gary –
*EN** *60950-1:2001 lost favor on 1DEC2010.
You owe John Woodgate a nickel.
Peter Tarver
of
fulfilling their intended functions.
This view is similar in concept to allowing a dc test when capacitances
will allow excess currents to flow during the same tests.
Your answer sells better in committee.
Peter Tarver
-Original Message-
From: Richard Nute
Hi Joe:
Very quickly
too much electricity, and so Google can let
you know when you need to buy more certified organically produced, free
trade soy-milk.
Peter Tarver
This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you
UL warning regarding a wall receptacle (socket outlet)
http://www.nema.org/News/Pages/UL-Warns-of-Potentially-Hazardous-Receptacl
e.aspx
I'm not aware if mixing of voltages is allowed in a duplex receptacle (I
suspect it is not, since wiring errors become more likely and segregation
of wiring
))
Peter Tarver
-Original Message-
From: John Allen [mailto:john_e_al...@blueyonder.co.uk]
Sent: Monday, May 06, 2013 10:11
To: 'Peter Tarver'; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: UL warning regarding a wall receptacle
Peter
Whilst the link to the UL press release works
receptacle with
USB outlets in their listings for outlets.
In such cases, I suspect the USB portion requires no field wiring and that
the USB portion replaces one outlet from a duplex configured device. Is
this accurate?
Regards,
Peter Tarver
This email message is for the sole use
.
Regards,
Peter Tarver
*From:* safetyl...@gmail.com [mailto:safetyl...@gmail.com] *On Behalf
Of *Arthur
Michael
*Sent:* Wednesday, April 24, 2013 20:14
*To:* Peter Tarver
*Cc:* EMC-PSTC@listserv.ieee.org
*Subject:* Re: [PSES] HAR factories for marked cable
Hi Peter et al,
Here
Good afternoon.
A cable supplier has mentioned that cables cannot bear the HAR marking
if they are not manufactured within an EU country. This seems to be
buried in HAR agreement documents that are out of my reach. Can anyone
confirm this?
Regards,
Peter L. Tarver
This email message is for
1 - 100 of 328 matches
Mail list logo