Rick,

This is an interesting train of thought. Logically there should never be a 
reason to use the hose connections on both sides of a horizontal exit at the 
same time. This jives with the allowance to remove the hose valve on one side 
of the separation if the other side can be completely covered from the far 
stairwell.

Nothing in the Flow Rates section of chapter 10 allows this however, and I 
think it may even be specifically prohibited by 10.6.1.1.7 “Where lateral 
piping serves a single hose connection, the minimum flow rate for the system 
shall be determined as if the hose connection is being served from a separate 
standpipe.”

It really does make sense though to consider the hose connections on opposite 
sides of a horizonal exit to be a single standpipe. I would be interested in 
getting other readers thoughts on this.

Sincerely,
Eric Rieve, SET
Rieve Fire Protection

From: Rick Matsuda <rick26...@gmail.com>
Sent: Wednesday, April 3, 2024 11:29 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Standpipe Calculations

Here’s a thought which may be out way of line.

The 2-hour separation wall in the middle of the building was installed in lieu 
of an additional stairway. So technically there would have been three stairways 
and only three standpipes.

Does NFPA 14 allow you to install one standpipe by the separation and supply 
two hose valves on each level, one on each side of the wall, instead of two 
separate standpipes? If this is allowed then you’ll need to calculate only 
1000-gpm.

During a fire condition, the fire department should be hooking up to only the 
hose valve on the safe non-fire side.
Just my crazy opinion.
Rick Matsuda


On Apr 3, 2024, at 10:06 AM, Tstone52 
<tston...@comcast.net<mailto:tston...@comcast.net>> wrote:

The building code calls for buildings more than 3 stories to have Standpipes. 
13R has nothing to do with it.
G Tim Stone




On Apr 3, 2024 at 9:50 AM, <Fpdcdesign<mailto:fpdcdes...@gmail.com>> wrote:
13R buildings are not considered to be fully sprinklered.




On Apr 3, 2024 at 9:45 AM, <Shawn Foor<mailto:shawn.f...@gmail.com>> wrote:
Why would you do 1250 if it’s a fully sprinklered building?

Shawn Foor, SET

FOOR DESIGN, LLC
10208 E 98TH ST
TULSA, OK 74133
P:918-237-1400


On Wed, Apr 3, 2024 at 08:43 
<rimrock.design.servi...@gmail.com<mailto:rimrock.design.servi...@gmail.com>> 
wrote:
Asking this on behalf of Rowe Sprinkler Systems (Temporally Un-Retired)

We have a 4-story modular apartment building sprinklered in accordance with 
NFPA 13R with allowed exceptions, with 4 standpipes. The standpipes are 
connected at the 1st floor level. One each at the ends of the L shaped building 
and two at the approximate mid-point on either side of a 2-hour separation wall 
with self-closing, rated doors in the corridor.
The question is for purposes of calculating the standpipe can these be treated 
as two separate buildings? For example, 250 gpm at the far end of the 4th 
floor, 250 gpm at the far end of the 3rd floor and 250 gpm at the at the 
connecting point of the middle standpipe, for a total of 750 gpm.
Or do we have to calculate the additional standpipes up to 1250 gpm. Available 
water is the issue.


Richard L. Mote CET
Rimrock Design Services, LLC
Middleburg, PA 17842
Mobile 570-541-2685
EMAIL 
rimrock.design.servi...@gmail.com<mailto:rimrock.design.servi...@gmail.com>
WEB: www.rimrockdesignservicesllc.com<http://www.rimrockdesignservicesllc.com>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>