This is a great discussion but with all matters concerning standpipes, hose 
valves, and FDC’s, you really need to discuss this with the AHJ and fire 
department to see what they want. They are the end user. 
Rick Matsuda 

> On Apr 3, 2024, at 11:01 AM, Anthony Carrizosa 
> <anth...@archerconstruction.com> wrote:
> 
> 
> I think Don kern hit it on the head, Unless it’s a high rise then a manual 
> standpipe system is all that’s needed.
>  
> Anthony Carrizosa
> Project Manager | Fire Protection
> 7855 S 206th St Kent, WA 98032
> Cell: 206-679-5283 | Office Dir: 253-341-4593
> 
> https://archerconstruction.com
>  
> From: Steve Leyton <st...@protectiondesign.com> 
> Sent: Wednesday, April 3, 2024 8:57 AM
> To: Discussion list on issues relating to automatic fire sprinklers 
> <sprinklerforum@lists.firesprinkler.org>
> Subject: [Sprinklerforum] Re: Standpipe Calculations
>  
> Yes, a building separation does divide the hydraulic demands to what is 
> required on each side of the separation.   See Fig. A.10.6.1.2.3.1 (2024 ed).
>  
>  
> The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
> Technical Committee, nor intended to serve as an interpretation of the 
> standard.
>  
> Protection Design and Consulting
> Steve Leyton, President
> T  |  619.255.8964 x 102  |  www.protectiondesign.com 
> 2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
> Fire Protection System Design | Consulting | Planning | Training
>  
>  
>  
>  
>  
>  
>  
> From: Rick Matsuda <rick26...@gmail.com> 
> Sent: Wednesday, April 03, 2024 8:29 AM
> To: Discussion list on issues relating to automatic fire sprinklers 
> <sprinklerforum@lists.firesprinkler.org>
> Subject: [Sprinklerforum] Re: Standpipe Calculations
>  
> Here’s a thought which may be out way of line. 
>  
> The 2-hour separation wall in the middle of the building was installed in 
> lieu of an additional stairway. So technically there would have been three 
> stairways and only three standpipes. 
>  
> Does NFPA 14 allow you to install one standpipe by the separation and supply 
> two hose valves on each level, one on each side of the wall, instead of two 
> separate standpipes? If this is allowed then you’ll need to calculate only 
> 1000-gpm. 
>  
> During a fire condition, the fire department should be hooking up to only the 
> hose valve on the safe non-fire side. 
> Just my crazy opinion. 
> Rick Matsuda 
>  
> 
> On Apr 3, 2024, at 10:06 AM, Tstone52 <tston...@comcast.net> wrote:
> 
> 
> The building code calls for buildings more than 3 stories to have Standpipes. 
> 13R has nothing to do with it. 
> G Tim Stone
>  
> 
> 
> 
> On Apr 3, 2024 at 9:50 AM, <Fpdcdesign> wrote:
> 
> 13R buildings are not considered to be fully sprinklered. 
>  
> 
> 
> 
> On Apr 3, 2024 at 9:45 AM, <Shawn Foor> wrote:
> 
> Why would you do 1250 if it’s a fully sprinklered building?  
> 
> Shawn Foor, SET
>  
> FOOR DESIGN, LLC
> 10208 E 98TH ST
> TULSA, OK 74133
> P:918-237-1400
>  
>  
> On Wed, Apr 3, 2024 at 08:43 <rimrock.design.servi...@gmail.com> wrote:
> Asking this on behalf of Rowe Sprinkler Systems (Temporally Un-Retired)
>  
> We have a 4-story modular apartment building sprinklered in accordance with 
> NFPA 13R with allowed exceptions, with 4 standpipes. The standpipes are 
> connected at the 1st floor level. One each at the ends of the L shaped 
> building and two at the approximate mid-point on either side of a 2-hour 
> separation wall with self-closing, rated doors in the corridor.
> The question is for purposes of calculating the standpipe can these be 
> treated as two separate buildings? For example, 250 gpm at the far end of the 
> 4th floor, 250 gpm at the far end of the 3rd floor and 250 gpm at the at the 
> connecting point of the middle standpipe, for a total of 750 gpm.
> Or do we have to calculate the additional standpipes up to 1250 gpm. 
> Available water is the issue.
>  
>  
> Richard L. Mote CET
> Rimrock Design Services, LLC
> Middleburg, PA 17842
> Mobile 570-541-2685
> EMAIL rimrock.design.servi...@gmail.com
> WEB: www.rimrockdesignservicesllc.com
>  
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
> _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
> _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to