OK, I don’t think everyone followed that you were talking about DC power for up 
to 6 450m sectors.  Especially with the talk about hybrid cable.

 

From: AF <af-boun...@af.afmug.com> On Behalf Of dave via AF
Sent: Friday, April 3, 2020 2:22 PM
To: af@af.afmug.com
Cc: dave <dmilho...@wletc.com>
Subject: Re: [AFMUG] Fiber Up Tower

 


We dont do batteries for our larger sites that have 4 or more of these we have 
mostly 3Ghz medusas. 
Its Genny or nothing. Until I can get a perfected lightning detector for an all 
battery backup site I just dont do it anymore. 
Its too risky for continuous run during a lightning storm. Too many dc factors 
to cause overload or damage. 
You may get away with doing 10awg for 2. I just know for 6 I had have a minimal 
of 8awg which included 4 450m 3Ghz and 2 450m 5Ghz
We ran all the cables into a tower top enclosure which included a hardened 
switch and packetflux rack injector for timing using dinrails and buss bar 
to keep everything in order and some din rail mounted lugs to distribute power 
and fuse buss we also installed a transtector 48v dc arrestor top and bottom 
for 
the main line protection. We also included all Lpus for each medusa for both Dc 
line and ethernet. 

The site has been in play for a while now with out issue. 

Hope this will help others trying to deploy these big guys. 
Using the large riser wire 8awg is not over kill for the medusa at all just do 
some simple surge protection top and bottom and everything should be fine.
I mean I think about how we just spent $$$$$ on a single medusa why not give it 
what it needs to perform and sustain. 

Plus if you ever expand the site with other gear it needs power too. 






On 4/2/20 9:24 PM, Ken Hohhof wrote:

Agreed.  And I think actual power consumption is closer to 65 or 70W.  Maybe 
the 80W number is at startup or extremes of temperature or something.

 

I have 2 of them on one tower and 1 on another powered via POE over cables 
right at the 100 meter limit, so >300 feet.  So they are powered over 4 x 24AWG 
wires in parallel.  2 in parallel is equivalent to 3 wire gauges, 4 in parallel 
is equivalent to 6 wire gauges.  So 4 x 24 AWG is equivalent to 1 x 18 AWG.  So 
nothing even close to 12 AWG much less 8 AWG is needed.

 

Oh, and spec sheet says input voltage range is 40-60 volts.

 

3 GHz version is a beast and the power consumption scares me.  That’s a lot of 
batteries.

 

 

From: AF  <mailto:af-boun...@af.afmug.com> <af-boun...@af.afmug.com> On Behalf 
Of Josh Baird
Sent: Thursday, April 2, 2020 7:55 PM
To: AnimalFarm Microwave Users Group  <mailto:af@af.afmug.com> <af@af.afmug.com>
Subject: Re: [AFMUG] Fiber Up Tower

 

I'm not following these requirements for the 450M.

 

The 450M @ 5ghz uses ~80W peak (if you aren't using the AUX port).  This is 
about 1.6A @ 48V.

 

12AWG cable with 56V at 250ft has a voltage drop of ~2.8% resulting in 54.5V at 
the top of the tower.  The 450M should run just fine at 54.5V according to the 
spec sheet.

 

Obviously, the 3ghz 450M requires much more power, but still should be fine 
using 12AWG @ 250ft.  

 

What am I missing? 

 

On Mon, Mar 30, 2020 at 6:24 PM dave via AF <af@af.afmug.com 
<mailto:af@af.afmug.com> > wrote:

That may work for most radios limited by 4 possibly 6 450i or something 
equivalent.
 If running medusa 3.65 and 5.7 radios youll need #8 min by 2 pair pvc jacket 
or better for outdoor operation. 
We have a few like this and learned the hard way even with #10 hybrid cable 
that would not fly due to the loss in the wire at 250' 
We use Tactical SM fiber LC-LC pre-terminated  
We also use Duracomms  
https://duracomm.com/product-category/rack-mount-power-supplies/centri-series-he1u-mu/
Note we use the 50Amp version of this. 
Youll need most of it to get to the top to sustain that 48vDC those beast need 
lol.
We now have our 3rd site up with Fiber going to everything and #8 stranded 
pairs up the tower for power. 
Also, be sure and add in the surge stuff. 




On 3/30/20 4:46 PM, TJ Trout wrote:

I've been thinking of offering hybrid fiber / 12 awg copper pre-terminated 
cables... if anyone has a desire for such a thing, let me know the fiber count, 
connector type and lengths you would want... 

 

On Mon, Mar 30, 2020 at 2:35 PM Matt <matt.mailingli...@gmail.com 
<mailto:matt.mailingli...@gmail.com> > wrote:

What is everyone using for fiber up tower? What using for connectors?

 

-- 
AF mailing list
AF@af.afmug.com <mailto:AF@af.afmug.com> 
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

 

 

-- 
AF mailing list
AF@af.afmug.com <mailto:AF@af.afmug.com> 
http://af.afmug.com/mailman/listinfo/af_af.afmug.com





 

-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to