by the way the fan you've linked is 60mm, for that particular vent you will
want 80mm.  I've never seen an outdoor enclosure done with 60mm fans. 80 or
120mm move a lot more air and are much quieter.

On Wed, Apr 20, 2016 at 8:28 PM, Scott Vander Dussen <[email protected]>
wrote:

> Fiberglass enclosure
> Bud Industries IPV-1116<
> http://www.alliedelec.com/bud-industries-ipv-1116/70368864/> vents
> Orion WMG60M<
> http://www.alliedelec.com/orion-knight-electronics-inc-wmg60m/70103693/>
> wire filters
> 60mm DC fan<
> http://www.rpelectronics.com/cfa246025ms-24vdc-sleeve-bearing-60mm-fan.html>
> with Locked Rotor Alarm Signal Output
> 60mm guard<
> http://www.rpelectronics.com/cfg-60m-60mm-metal-finger-guard.html>
>
> The enclosure includes a Site Monitor, I'm hoping to use its secondary DC
> input to monitor the fan's yellow alarm wire lead and trigger an error
> state in our SNMP monitoring if a fan becomes locked.
>
> I'm concerned about the fans running 24x7 potentially bringing in moisture
> from fog/nightly humidity.  With the site monitor could to turn the fans
> on/off based upon ambient temperature or time of day?  If yes, how would I
> do that, a relay?  What kind of relay?  I don't have much experience with
> relays/Site Monitors, thanks.  Or is there some other obvious solution I'm
> missing?
>
> Another idea is to use a Hyderon RG-11 Rain Sensor / Gauge<
> http://rainsensors.com/how-it-works/> to trigger the fans off for both
> dark (less than 2000 lux) and/or rain.  This seems pretty rad!
>
> Thanks,
> `S
>