Bruce,

My guess is that your customer is declaring compliance to the EMC Directive
under EN 61326 Class A.

EN 61326 defines Class A equipment in Section 3.4 as "Equipment suitable
for use in establishments other than domestic, and those directly connected
to a low voltage power supply network which supplies buildings used for
domestic purposes."

Section 3.7 of EN 61326 defines industrial locations as "locations
characterized by a separate power network, in most cases supplied from a
high or medium voltage transformer, dedicated for the supply of
installations feeding manufacturing or similar plants..."

Section 7.2 specifies that "Table 3 gives the limit values for Class A
equipment."  Table 3 does not include harmonics and Flicker.

Section 4 states that "... Emission limits for industrial locations are
given in Table 3."

Thus, Class A equipment is equipment used in industrial locations supplied
by high or medium voltage transformers.

EN 61000-3-2 Harmonics Section 1 Scope states "this section of IEC 1000-3
is applicable to electrical and electronic equipment...intended to be
connected to public low voltage distribution systems."  In my opinion, this
would not include industrial locations.

Regards

Joe Martin
EMC Consultant





[email protected]@ieee.org on 12/03/2000 03:03:37 PM

Please respond to [email protected]

Sent by:  [email protected]


To:   [email protected]
cc:

Subject:  EN 61000-3-3 Flicker Tests



Hello group!

I've got a customer in our EMC lab that makes a laboratory instrument
incorporating heaters with a typical 3-4 amp input current at 230vac.  He
is failing the flicker test due to the design of the heater control.  They
are undertaking a redesign but would like to keep selling product in the
interim.

They have come up with an interesting interpretation of the scope of EN
61000-3-3:  the standard specifies that the tests are applicable to
products connected to the "public low voltage distribution systems"  but if
you take a typical industrial location or even a typical commercial
location, isn't it true that these locations are fed by a dedicated
transformer at the building that isolates them from the public network?  I
guess the question becomes - what is considered the public network?  What
if the marketing of the product was restricted to "industrial" locations?

My initial reaction to the question was that anyplace you can plug or wire
into at typical 230vac is considered the "public network", especially
considering the mixed residential / commercial buildings common in Europe.

Anyone care to comment?

Bruce Fagley
Sr. Specialist, EMC
Industrial Products
TUV Rheinland
12 Commerce Rd.
Newtown CT. 06470
203-426-0888 ext 119
203-426-4009 fax


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]






-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to