I hesitate to give an interpretation on the legal
meaning of  'public low voltage supply' although
I suspect the interpretation your customer would
put on it would be described  'domestic low voltage
supply'. I don't see from the view point of common
speech why 'public' excludes commercial and don't
see in any other European standards  or guidance notes
any formal interpretation this way.

However, I can certainly confirm that it is common
for light industrial premises not to have individual
transformers. Close to our factory is a set of 10
small industrial units with a common supply
at 240V.
240V (Phase to neutral), three phase at 150A per
phase gives 108kW,  plenty for many commercial
premises and much greater than it is possible to draw
from the domestic supply in many cases in America.

Also near here is a small commercial pathology
lab run upstairs from a shop. Next door in the
block, the upstairs rooms provide living
accommodation for the family of the owner of the
shop below. The whole block of shops, together
with some purely domestic premises, is supplied
like most urban domestic premises in the UK  by
a three phase and neutral cable buried in the road
with each shop being connected between one phase
and neutral, each third shop being connected to the
same phase (U.K. 3 phase supply is always balanced
about neutral) Such arrangements are common here in
the UK and from what I have seen of places like
Italy even more common over there.

As for marketing only to industrial locations, even if
you could get by on the supply not being 'public' this
would surely depend on how much control your customer
had over its location. If each unit were installed and
maintained by them only in premises with their own
supply transformer they might claim it was buffered
by the transformer. However if they are selling them
through distributors or trade paper adverts the authorities
are likely to form a judgement as to the likelihood of
it being connected to unbuffered supplies, either new
or second hand.

Hope this helps
Nick Rouse
----- Original Message -----
From: <[email protected]>
To: <[email protected]>
Sent: Sunday, December 03, 2000 11:03 PM
Subject: EN 61000-3-3 Flicker Tests


>
>
> Hello group!
>
> I've got a customer in our EMC lab that makes a laboratory instrument
> incorporating heaters with a typical 3-4 amp input current at 230vac.  He
> is failing the flicker test due to the design of the heater control.  They
> are undertaking a redesign but would like to keep selling product in the
> interim.
>
> They have come up with an interesting interpretation of the scope of EN
> 61000-3-3:  the standard specifies that the tests are applicable to
> products connected to the "public low voltage distribution systems"  but
if
> you take a typical industrial location or even a typical commercial
> location, isn't it true that these locations are fed by a dedicated
> transformer at the building that isolates them from the public network?  I
> guess the question becomes - what is considered the public network?  What
> if the marketing of the product was restricted to "industrial" locations?
>
> My initial reaction to the question was that anyplace you can plug or wire
> into at typical 230vac is considered the "public network", especially
> considering the mixed residential / commercial buildings common in Europe.
>
> Anyone care to comment?
>
> Bruce Fagley
> Sr. Specialist, EMC
> Industrial Products
> TUV Rheinland
> 12 Commerce Rd.
> Newtown CT. 06470
> 203-426-0888 ext 119
> 203-426-4009 fax
>
>
> -------------------------------------------
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
>
> To cancel your subscription, send mail to:
>      [email protected]
> with the single line:
>      unsubscribe emc-pstc
>
> For help, send mail to the list administrators:
>      Jim Bacher:              [email protected]
>      Michael Garretson:        [email protected]
>
> For policy questions, send mail to:
>      Richard Nute:           [email protected]
>
>


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to