IEC 62040-2 should have had a parallel vote in CENELEC as it was intended
to replace EN 50091-2.  That was not done which lead to a  lot of
confusion. The "under consideration" phrase was carried forward from EN
50091-2 to IEC 62040-2 in Annex D.  The normative reference part of the IEC
standard was corrected but the Annex wasnt.  The next edition of IEC
62040-2 will have the proper corrections for all the"under consideration"
type errors as well as a parallel vote in CENELEC so that there will be a
EN 62040-2.

IEC 62040-2 should have been turned into an EN and a lot of confusion would
have been eliminated.  The schedule for turning the IEC to an EN as listed
below is quite ambicious to say the least.  A CDV by December.  It could
happen but seeing as how we haven't scheduled a meeting to discuss the
standard yet that does seem a little agressive.  But hey stranger things
have happened.

Please let me know if you have further questions regarding this standard as
I am involved with the committee that is doing the writing.


                                                                                
                                             
                    John Woodgate                                               
                                             
                    <[email protected]>         To:     
[email protected]                                       
                    Sent by:                       cc:                          
                                             
                    owner-emc-pstc@majordom        Subject:     Re: 
EN50091-2:1995                                           
                    o.ieee.org                                                  
                                             
                                                                                
                                             
                                                                                
                                             
                    01/11/2002 04:18 PM                                         
                                             
                    Please respond to John                                      
                                             
                    Woodgate                                                    
                                             
                                                                                
                                             
                                                                                
                                             




I read in !emc-pstc that Sam Wismer <[email protected]> wrote (in
<000901c19ab1$7feb4ae0$0201a8c0@sam>) about 'EN50091-2:1995', on Fri, 11
Jan 2002:
>    I am reviewing EN50091-2:1995 to determine the immunity requirements
for UPS
>    systems.  According to the harmonized list, this is the correct
version of
>    the standard under the EMCD.  It calls for radiated emissions, IEC
801-2, -3
>    and -4.  It then says 801-5 is under consideration.  Our customer is
>    requesting 801-5, but based on how I read the standard, it is not
required
>    at this time.  Could that be true?
>
The standard is seriously out-of-date. 801-5 was never published (but an
unfinished version was issued as ENV50142), and the requirements in
801-2 to -4 have been considerably changed in the current IEC/EN 61000-4
series.

Here is the (re-formatted) information from the CENELEC web site on the
replacement:

Project number 14872
Standard reference prEN62040-2
Reference document IEC 62040-2:200X
Technical body CLC/TC 22X
IEC/TC IEC/SC 22H

Stage code Stage code date Stage code deadline Real next stage code
31 (2020)      2001-10-31      2002-06-30          32 (3020)

Target enquiry Target approval Target ratification Target available
  2003-06-30      2003-11-30       2004-03-31

Note 2001-10 decision: Work on future IEC 62040-2 to replace EN
50091-2:1995 * CDV expected December 2002

Title (EN) Uninterruptible power systems (UPS) -- Part 2:
Electromagnetic compatibility (EMC) requirements


Now, what should you do? IMO, you probably cannot just ignore the surge
test, so I suggest you apply IEC61000-4-5, and explain in your technical
file why you did that.


--
Regards, John Woodgate, OOO - Own Opinions Only.
http://www.jmwa.demon.co.uk
After swimming across the Hellespont, I felt like a Hero.

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old
messages are imported into the new server.





-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to