I read in !emc-pstc that Sam Wismer <swis...@bellsouth.net> wrote (in
<000901c19ab1$7feb4ae0$0201a8c0@sam>) about 'EN50091-2:1995', on Fri, 11
Jan 2002:
>    I am reviewing EN50091-2:1995 to determine the immunity requirements for 
> UPS 
>    systems.  According to the harmonized list, this is the correct version of 
>    the standard under the EMCD.  It calls for radiated emissions, IEC 801-2, 
> -3 
>    and -4.  It then says 801-5 is under consideration.  Our customer is 
>    requesting 801-5, but based on how I read the standard, it is not required 
>    at this time.  Could that be true?   
>
The standard is seriously out-of-date. 801-5 was never published (but an
unfinished version was issued as ENV50142), and the requirements in
801-2 to -4 have been considerably changed in the current IEC/EN 61000-4
series.

Here is the (re-formatted) information from the CENELEC web site on the
replacement:

Project number 14872
Standard reference prEN62040-2
Reference document IEC 62040-2:200X
Technical body CLC/TC 22X
IEC/TC IEC/SC 22H  
   
Stage code Stage code date Stage code deadline Real next stage code 
31 (2020)      2001-10-31      2002-06-30          32 (3020)  

Target enquiry Target approval Target ratification Target available 
  2003-06-30      2003-11-30       2004-03-31
  
Note 2001-10 decision: Work on future IEC 62040-2 to replace EN
50091-2:1995 * CDV expected December 2002 

Title (EN) Uninterruptible power systems (UPS) -- Part 2:
Electromagnetic compatibility (EMC) requirements 

  
Now, what should you do? IMO, you probably cannot just ignore the surge
test, so I suggest you apply IEC61000-4-5, and explain in your technical
file why you did that.
  

-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        pstc_ad...@garretson.org
     Dave Heald                davehe...@mediaone.net

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to