The entire 801 Series is obsolete and replaced by the EN61000-4-X series;
61000-4-2, 61000-4-3, 61000-4-4 and 61000-4-5.
 
It sounds like the product standard you have is out of date and needs to be
revised, if it hasn't been already, to call out the new standards.
 
Today, virtually all product standards call for testing to 61000-4-2 (ESD),
61000-4-3 (RF Radiated), 61000-4-4 (EFT), 61000-4-5 (Surge), 61000-4-6 (RF
Conducted) and 61000-4-11 (Dip and Interrupts). Additionally, virtually all
product standards require emissions testing as well. It is possible a
revision of EN50091-2:1995 would not call for surge testing, but more than
likely, it will. I would think if surge immunity were to be required for any
set of products, UPS's would be at the top of the list..... I'd recommend it
whether you're required to do surge testing or not. (Be careful, I sell
surge testers, so you better get other opinions!) Good Luck.
 
 
Mike Hopkins
Thermo KeyTek
 
 
 
 
-----Original Message-----
From: Sam Wismer [mailto:[email protected]]
Sent: Friday, January 11, 2002 10:06 AM
To: EMC Forum
Subject: EN50091-2:1995


Hi all,
I am reviewing EN50091-2:1995 to determine the immunity requirements for UPS
systems.  According to the harmonized list, this is the correct version of
the standard under the EMCD.  It calls for radiated emissions, IEC 801-2, -3
and -4.  It then says 801-5 is under consideration.  Our customer is
requesting 801-5, but based on how I read the standard, it is not required
at this time.  Could that be true?   
 
 
Kind Regards,
 
 
Sam Wismer
Engineering Manager
ACS, Inc.
 
Phone:  (770) 831-8048
Fax:  (770) 831-8598
 
Web:  www.acstestlab.com
 