The criteria that determines if an accessible conductive part requires
grounding is generally whether or not a single fault can make that part come
into contact with a hazardous live part.  The single fault may be failure of
functional or basic insulation, reduction of a functional or basic clearance,
a component fault, etc.

 

>From your statement that the only risk would be if the power supply cord
“near” the heatsink becomes damaged and contacts the heatsink, it sounds
as if you have determined that the internal construction is such that there is
no risk of the heatsink becoming live from contact with internal live parts
under normal or single fault conditions.  If you have not determined that, you
need to, because the inspector might be onto something and the NRTL might have
missed something.  It happens.

 

Assuming that we are indeed left with only the p/s cord to consider, then 2
things have to happen as you stated: damage to the cord, and cord contact with
the heatsink.  If the p/s cord has nothing securing it in position away from
the heatsink, I think you have to assume it can or will contact that heatsink,
without that constituting a fault.  In that case, the question becomes:  can
the Listed power supply cord have an exposed live conductor as the result of a
single fault?  I would say yes, except that if it is a jacketed cord, you
would have to damage both the jacket, and the conductor insulation.  That
could easily happen from a single action, but I do not think it counts as a
single fault, since 2 layers of insulation are involved.  In fact it would
seem logical that if it did count as a single fault, a cord like that would
not be allowed to be exposed to users.

 

Does anyone have an opinion or know of an official NRTL rule on this?  Is an
NRTL approved jacketed cord officially considered single fault tolerant?

 

Finally, if the portion of the p/s cord that is near the heatsink is external
to the projector (ie if it is accessible), then if it is damaged in such a way
that it could energize the heatsink, it is itself a hazard regardless of
whether or not it touches the heatsink.

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: [email protected]
web: www.xantrex.com <http://www.xantrex.com/>   

Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

From: [email protected] [mailto:[email protected]] On Behalf Of Christine
Rodham
Sent: Wednesday, May 13, 2009 7:38 AM
To: [email protected]
Subject: Re:NRTL Mark vs. NEC Inspector

 

 

List Members,

 

We have an interesting problem. We sold an OEM product ( very high end Home
Theater Movie Projector , better than a movie theater quality) which was
listed by a well known NRTL. ( We modify and enhance the SW for high end
performance)

 

The projector was installed in a public place and the installation was
evaluated by a NEC ( National Electrical Code ) inspector. 

 

The projector has a metal ungrounded heat sink attached to the chassis that
was added for cooling but was evaluated and approved by the NRTL. 

 

The NEC inspector will not sign off on the installation stating non-current
carrying exposed metal parts that may be accidentally energized must be
grounded to the chassis. Grounding the heat-sink to the chassis will be
difficult due to the design of this special aluminum heat-sink.

 

Here are my questions:

 

* What is the criteria to determine if a metal part can become accidentally
energized?

  The only way it could happen in this case is if the power cord that is near
the heat-sink is

  damaged and then touches the heat-sink. The power cord is UL approved and
properly 

  rated.

 

* How many fault conditions ( single vs multiple ) are considered to determine
if a metal part can become accidentally energized.

 

* What would be our best option in arguing this ruling. Should we request
another inspector or get the NRTL involved?

 

Note that this unit is ceiling mounted and only trained service people would
have access to it after the initial installation.

 

Thank you!

 

Christine Rodham

 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to