Wow! Impressive knowledge of the NEC, Ted.

 

My two cents: Tapping a hole in the heatsink to connect a ground wire sounds
dead-easy compared to arguing fine-points of the code with the inspector.

 

…Marko

 

________________________________

From: Ted Eckert [mailto:[email protected]] 
Sent: Wednesday, May 13, 2009 9:28 AM
To: [email protected]
Subject: Re: [PSES] NRTL Mark vs. NEC Inspector

 

Hello Christine,

 

I am referencing the 2008 NEC.  Excuse the large sections excerpted, but they
cover the relevant information.  The bold and italic text is from the code.  I
have underlined what I think are some of the critical items.

 

90.7 Examination of Equipment for Safety.  For specific items of equipment and
materials referred to in this Code, examination for safety made under standard
conditions provide a basis for approval where the record is made generally
available through promulgation by organizations properly equipped and
qualified for experimental testing, inspections of the run of goods at
factories, and service-value determination through field inspections.  This
avoids the necessity for repetition of examinations by different examiners,
frequently with inadequate facilities for such work, and the confusion that
would result from conflicting reports on the suitability of devices and
materials examined for a given purpose.

 

It is the intend of this Code that factory-installed internal wiring or the
construction of equipment need not be inspected at the time of installation of
the equipment, except to detect alterations or damage, if the equipment has
been listed by a qualified electrical testing laboratory that is recognized as
having the facilities described in the preceding paragraph and that requires
suitability for installation in accordance with this Code.

 

100 Definitions

 

Listed.  Equipment, materials, or services included in a list published by an
organization that is acceptable to the authority having jurisdiction and
concerned with evaluation of products or services, that maintains periodic
inspection of production of listed equipment or materials or periodic
evaluation of services, and whose listing states that either the equipment,
material, or service meets appropriate designated standards or has been tested
and found suitable for a specified purpose.

 

110.3 Examination, Identification, Installation, and Use of Equipment.

(A) Examination. In judging equipment, considerations such as the following
shall be evaluated:

(1) Suitability for installation and use in conformity with the provisions of
this Code

FPN: Suitability of equipment use may be identified by a description marked on
or provided with a product to identify the suitability of the product for a
specific purpose, environment, or application. Suitability of equipment may be
evidenced by listing or labeling.

 

The final item I have is OSHA’s NRTL program.

http://www.osha.gov/dts/otpca/nrtl/index.html#nrtls

 

Now we can start putting this together.  

 

If your NRTL is shown on OSHA’s list, and UL 60950-1 is shown under that
NRTL’s scope of accreditation, then the Listing of your product should be
valid in most jurisdictions.  Your equipment would be considered Listed as
described by Article 100.

 

Next, Article 110.3, particularly the Fine Print Note (FPN) indicates that the
inspector may determine compliance based on the Listing of the product.

 

Finally, Article 90.7 indicates that the intent of the Listing is so that the
local inspector doesn’t make his/her own evaluation of a products
suitability.  It is assumed to be suitable if determined as such by the NRTL.

 

Your local inspector could make other arguments.  You may have to show that
the NRTL has approved your product for the installation method and use which
the inspector is reviewing.  However, if the NRTL determined that creepage and
clearance requirements were met, then the Listing should be sufficient for the
inspector.

 

The final question is whether you expect more of your products to be installed
in this jurisdiction.  If not, it may be worth fighting this inspector.  If
you are going to face this inspector in the future, you may need to find a
more amicable way of resolving your difference of opinion.  Otherwise, this
inspector may choose to throw everything he/she can find at you on your next
installation.

 

Regards,

Ted Eckert

Compliance Engineer

Microsoft Corporation

[email protected]

 

The opinions expressed are my own and do not necessarily reflect those of my
employer.

 

 

 

From: Christine Rodham [mailto:[email protected]] 
Sent: Wednesday, May 13, 2009 8:55 AM
To: [email protected]
Subject: Re: NRTL Mark vs. NEC Inspector

 

 What is a "NEC (National Electrical Code) inspector" ? -   The local city
inspector that enforces the NEC.

 

I will have to get the formal information ( chapter and verse) from the
installer ( who is out-sourced by us ) I received a voice-mail this morning
regarding this incident.

 

Thanks

 

Christine


--- On Wed, 5/13/09, Brian O'Connell <[email protected]> wrote:

        
        From: Brian O'Connell <[email protected]>
        Subject: RE: NRTL Mark vs. NEC Inspector
        To: [email protected]
        Date: Wednesday, May 13, 2009, 8:11 AM

        What is a "NEC (National Electrical Code) inspector" ?
        
        In any case, the electrical/fire inspector should have noted specific 
NFPA70
clauses. You cannot conform to code until you know the requirement.
        
        Fault conditions, as described for Type Tests in a product safety 
standard,
are not defined in the NEC. The NEC 'tends' to describe required construction
for various combinations of specific ratings and environments.
        
        The biggie is for > 150V to P.E., where all exposed metal must be 
'grounded'
for Class I construction. I do not like this, but there is an NEC clause that
allows an exemption for insulated heat sinks.
        
        
        -----Original Message-----
        From: [email protected] <http://us.mc5
7.mail.yahoo.com/mc/[email protected]>  [mailto:[email protected]
<http://us.mc557.mail.yahoo.com/mc/[email protected]> ]On Behalf Of
Christine Rodham
        Sent: Wednesday, May 13, 2009 7:38 AM
        To: [email protected] <http://us.mc557
mail.yahoo.com/mc/[email protected]> 
        Subject: Re:NRTL Mark vs. NEC Inspector
        
        List Members,
        
        We have an interesting problem. We sold an OEM product ( very high end 
Home
Theater Movie Projector , better than a movie theater quality) which was
listed by a well known NRTL. ( We modify and enhance the SW for high end
performance)
        
        The projector was installed in a public place and the installation was
evaluated by a NEC ( National Electrical Code ) inspector. 
        
        The projector has a metal ungrounded heat sink attached to the chassis 
that
was added for cooling but was evaluated and approved by the NRTL. 
        
        The NEC inspector will not sign off on the installation stating 
non-current
carrying exposed metal parts that may be accidentally energized must be
grounded to the chassis. Grounding the heat-sink to the chassis will be
difficult due to the design of this special aluminum heat-sink.
        
        Here are my questions:
        
        * What is the criteria to determine if a metal part can become 
accidentally
energized?
          The only way it could happen in this case is if the power cord that 
is near
the heat-sink is
          damaged and then touches the heat-sink. The power cord is UL approved 
and
properly 
          rated.
        
        * How many fault conditions ( single vs multiple ) are considered to
determine if a metal part can become accidentally energized.
        
        * What would be our best option in arguing this ruling. Should we 
request
another inspector or get the NRTL involved?
        
        Note that this unit is ceiling mounted and only trained service people 
would
have access to it after the initial installation.
        
        Thank you!
        
        Christine Rodham
        
        -
        ----------------------------------------------------------------
        This message is from the IEEE Product Safety Engineering Society 
emc-pstc discussion list. To post a message to the list, send your
e-mail to <[email protected] <http://us
mc557.mail.yahoo.com/mc/[email protected]> >
        
        All emc-pstc postings are archived and searchable on the web at:
        http://www.ieeecommunities.org/emc-pstc
        Graphics (in well-used formats), large files, etc. can be posted to 
that URL.
        
        Website:  http://www.ieee-pses.org/
        Instructions:  http://listserv.ieee.org/request/user-guide.html
        List rules: http://www.ieee-pses.org/listrules.html
        
        For help, send mail to the list administrators:
        Scott Douglas <[email protected] <h
tp://us.mc557.mail.yahoo.com/mc/[email protected]> >
        Mike Cantwell <[email protected] <htt
://us.mc557.mail.yahoo.com/mc/[email protected]> >
        
        For policy questions, send mail to:
        Jim Bacher:  <[email protected] <http:
/us.mc557.mail.yahoo.com/mc/[email protected]> >
        David Heald: <[email protected] <http:/
us.mc557.mail.yahoo.com/mc/[email protected]> >


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Important : This message is intended only for the recipient(s) identified
above by the originator or forwarder of this message and may contain
information that is confidential, proprietary and/or legally privileged. If
you have any reason to believe or suspect that this message may have come to
you in error, please notify the originator of this message of your receipt of
it, refrain from sharing this message with anyone else, delete it from each
computer or server on which it is stored (without copying it or printing it
out) and take no other action based on its content. Thank you.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to