Question, in North America are common branch circuit overcurrent protection 
devices (circuit breakers) "listed for operation at 100 percent of its rating"? 
If not, I assume you can purchase circuit breakers that are rated for 100% 
operation.

Like you said, NEC 210-19 specifies the current rating of the conductor, or 
wire. Isn't the wire used in building wiring normally sized to handle 100% the 
continuous current rating of the branch circuit? For instance, won't 14AWG 
handle 15 amps continuously? 12AWG = 20 amps, 10AWG = 30 amps, and so on?

NEC 210.23 Permissible Loads, states "An individual branch circuit shall be 
permitted to supply any load for which it is rated." The rest of that section 
refers to branch circuits supplying more than one outlet, receptacle or load. 
So I assume for "individual branch circuits" or a dedicated circuit seeing a 
load from a single device, the device can draw 100% continuous current of the 
branch circuit rating as long as the conductors and overcurrent device is so 
rated. I think this is what Pete was referring to in his email.

Every time this topic comes up I learn something new.

Thanks to all.

The Other Brian

From: Don Gies [mailto:[email protected]]
Sent: Wednesday, May 16, 2012 12:11 PM
To: Kunde, Brian; [email protected]
Subject: Re: Circuit breakers in Europe (Continuous vs. Non-Continuous Loads)


Other Brian,



In the US and Canada, branch circuits and other circuits (e.g. services) are 
rated for the sum of the continuous loads plus 125 percent of the 
non-continuous loads.



This is stated, for instance, in NEC 210.19 for minimum ampacity of branch 
circuit conductor.  "Continuous Load" is in the definitions (Art. 100) as:



Continuous Load. A load where the maximum current is expected to continue for 3 
hours or more.



Likewise, in the Canadian Electrical Code, Part I, Rule 8-104, maximum circuit 
loading is 80% of the rating of the circuit where a fused switch or circuit 
breaker is marked for continuous operation at 80% of the ampere rating of its 
overcurrent devices (or is unmarked per Appendix B).  A continuous load is 
defined in that same rule as:



(3) The calculated load in a consumer's service, feeder, or branch circuit 
shall be considered a continuous load unless it can be shown that in normal 
operation it will not persist for

(a) a total of more than 1 h in any two-hour period if the load does not exceed 
225 A; or

(b) a total of more than 3 h in any six-hour period if the load exceeds 225 A.



Except for the definitions of continuous loads, the requirements are 
essentially the same in the US and Canada (though they are stated as 
reciprocals in one country versus the other).



An easy example to demonstrate continuous and non-continuous loads would be to 
compare a standard electric heater to a blow dryer.  The standard electrical 
heater plugs into a 120V ac, 15 A receptacle, and is considered a continuous 
load.  It is never rated more than 1500W.  Roughly this equates to 12 A current 
at 120 V ac, or 80% of the 15 A nominal circuit rating (12.5 actually, but you 
are normally allowed to exceed the current rating by no more than 10%).  Blow 
dryers that plug into 120 V ac, 15 A outlets, on the other hand, are often 
rated for up to 1800 W. which equates to a current of 15 A.  Why is this 
possible?  Because a blow dryer's use is short-duty or non-continuous, and will 
not be used for more than 3 hours in the US or for more than 1 hour in a 2 hour 
period in Canada.





Best regards,
DON GIES
ALCATEL-LUCENT
SENIOR PRODUCT COMPLIANCE ENGINEER
BELL LABS - GLOBAL PRODUCT COMPLIANCE LABORATORY
600-700 Mountain Avenue
Room 5B-104
Murray Hill, NJ 07974-0636 USA
Phone: +1 908 582 5978
Fax: +1 908 582 0582
[email protected]<mailto:[email protected]>
MEMBER, ALCATEL-LUCENT TECHNICAL ACADEMY





-----Original Message-----
From: Kunde, Brian [mailto:[email protected]]
Sent: Wednesday, May 16, 2012 10:45 AM
To: [email protected]<mailto:[email protected]>
Subject: Re: Circuit breakers in Europe



Since this topic has been brought up, I'm hoping you experts could clarify the 
80% rule for me for North America (don't forget Canada).



I was given the impression that the 80% rule (as we call it) applies to the 
maximum continuous current of the plug rating regardless of whether there is 
one receptacle or multiple receptacles on that circuit. A product can draw 100% 
the current rating of the plug for periods of time but not more than 80% 
average current or continuous current.



The reason for the rule is to avoid overheating in the plug/receptacle 
connection.



Is this right or wrong?



So say I have a 30 amp plug on my product and it is wired into a dedicated 
receptacle and circuit. My product can be rated and draw up to 30 amps but it 
cannot draw more than 24 amps continuous. Correct?



If the product is wired direct without the plug/receptacle it can draw up to 
100% of the circuit rating continuously. Correct?



Please confirm or clarify.



We gathered this information from CSA who inspects our products in Canada and 
if we rate a product over 80% of the plug rating they require we also provide 
an average current and/or continuous current rating for that product.



Thank you.



The Other Brian



-----Original Message-----

From: [email protected]<mailto:[email protected]> 
[mailto:[email protected]]<mailto:[mailto:[email protected]]> On Behalf Of Pete 
Perkins

Sent: Tuesday, May 15, 2012 6:07 PM

To: [email protected]<mailto:[email protected]>

Subject: RE: [PSES] Circuit breakers in Europe



PSNet,



        One issue that I'm not sure has been reflected in this thread is that 
the NA 80% restriction for utilization circuits is that it is assumed that 
there will be a number of duplex plugs wired into each circuit, as allowed by 
the NA code.  Therefore, any single product may not use the entire rated 
current from the circuit (20A, for instance) but is limited (80% = 16A) so that 
other products may be plugged into the same circuit with out overloading that 
circuit.



        If a product uses the full, rated current from a circuit breaker then 
that product must be wired to a 'dedicated ccircuit' meaning that an 
electrician must be called to wire in a circuit with only one outlet (not a 
duplex outlet) on that breaker. (After getting the required permit, it might 
cost as much to wire a new circuit - if it is even possible - as many 
commercial electronic products cost.)  It's pretty clear that customers do not 
want to hire an electrician to wire a new circuit for a new product thus the 
pressure to meet the 80% limit with the products.



        Industrial customers deal with rewiring to code better than commercial 
or household folks do.



        Been there, done that.



:>)     br,     Pete



Peter E Perkins, PE



Principal Product Safety Engineer



PO Box 23427



Tigard, ORe  97281-3427



503/452-1201     fone/fax



[email protected]<mailto:[email protected]>







-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>



All emc-pstc postings are archived and searchable on the web at:

http://www.ieee-pses.org/emc-pstc.html



Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.



Website:  http://www.ieee-pses.org/

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html



For help, send mail to the list administrators:

Scott Douglas <[email protected]<mailto:[email protected]>>

Mike Cantwell <[email protected]<mailto:[email protected]>>



For policy questions, send mail to:

Jim Bacher:  <[email protected]<mailto:[email protected]>>

David Heald: <[email protected]<mailto:[email protected]>>

________________________________



LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.



-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>



All emc-pstc postings are archived and searchable on the web at:

http://www.ieee-pses.org/emc-pstc.html



Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.



Website:  http://www.ieee-pses.org/

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html



For help, send mail to the list administrators:

Scott Douglas <[email protected]<mailto:[email protected]>>

Mike Cantwell <[email protected]<mailto:[email protected]>>



For policy questions, send mail to:

Jim Bacher:  <[email protected]<mailto:[email protected]>>

David Heald: <[email protected]<mailto:[email protected]>>

________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html