Brian,

 

In order to get 100% continuous current through a circuit breaker in North
America, the breaker has to be rated for 100% use.  I have heard and
suspected that these are rare, somewhat of a special-order item, and
naturally, more expensive than the common circuit breaker that cannot handle
100% current continuously.

 

Actually, when selecting the components of branch circuits, you have to
consider more than the ampacity of the conductor and the circuit breaker.
Temperature, particularly at the terminations, is the first item that has to
be checked in sizing conductors in a wiring system.  Per the National
Electrical Code, you size the conductors  based on NEC 110.14(C)(1).  This
means that unless both terminations of a conductor are Listed and marked
otherwise, the ampacity of a conductor under 100 A is based on the 60°C
column of Table 310.15(B)(16) (formerly Table 310.16), and for over 100 A or
over 1 AWG, the ampacity of the conductor is based on the 75°C column of
Table 310.15(B)(16).  Afterwards, you can use higher temperature conductors
for temperature adjustments.   Working in telecommunication infrastructure,
I have caught lots of people over the years choosing wire sizes for
tray-cable systems using the free-air tables (former Table 310.17), or using
the 90°C column because they were using THHN wire.   

 

So, given the above, you either size a standard branch circuit with
receptacles and luminaires as prescribed in Article 210.  But, if you have
dedicated loads, you need to consider whether your loads are continuous or
not, size the branch circuit for the sum of the non-continuous loads plus
125% of the continuous loads, then consider the temperature ratings of the
terminations, because they are the weak link.

 

Finally, as Pete mentioned, and following the do-as-I-say-not-as-I-do rule
in the lab, circuit breakers can get very hot to touch at 100% rating, and
they sometimes trip early because of the heat.

 

Best regards,

 

 

DON GIES 
ALCATEL-LUCENT
SENIOR PRODUCT COMPLIANCE ENGINEER
BELL LABS - GLOBAL PRODUCT COMPLIANCE LABORATORY
600-700 Mountain Avenue
Room 5B-104
Murray Hill, NJ 07974-0636 USA   
Phone: +1 908 582 5978
Fax: +1 908 582 0582
[email protected]

MEMBER, ALCATEL-LUCENT TECHNICAL ACADEMY

 

From: Kunde, Brian [mailto:[email protected]] 
Sent: Thursday, May 17, 2012 11:17 AM
To: [email protected]
Subject: Re: Circuit breakers in Europe (Continuous vs. Non-Continuous
Loads)

 

Question, in North America are common branch circuit overcurrent protection
devices (circuit breakers) “listed for operation at 100 percent of its
rating”? If not, I assume you can purchase circuit breakers that are rated
for 100% operation.

 

Like you said, NEC 210-19 specifies the current rating of the conductor, or
wire. Isn’t the wire used in building wiring normally sized to handle 100%
the continuous current rating of the branch circuit? For instance, won’t
14AWG handle 15 amps continuously? 12AWG = 20 amps, 10AWG = 30 amps, and so
on?

 

NEC 210.23 Permissible Loads, states “An individual branch circuit shall be
permitted to supply any load for which it is rated.” The rest of that
section refers to branch circuits supplying more than one outlet, receptacle
or load. So I assume for “individual branch circuits” or a dedicated circuit
seeing a load from a single device, the device can draw 100% continuous
current of the branch circuit rating as long as the conductors and
overcurrent device is so rated. I think this is what Pete was referring to
in his email.

 

Every time this topic comes up I learn something new.

 

Thanks to all.

 

The Other Brian

 

From: Don Gies [mailto:[email protected]] 
Sent: Wednesday, May 16, 2012 12:11 PM
To: Kunde, Brian; [email protected]
Subject: Re: Circuit breakers in Europe (Continuous vs. Non-Continuous
Loads)

 

Other Brian,

 

In the US and Canada, branch circuits and other circuits (e.g. services) are
rated for the sum of the continuous loads plus 125 percent of the
non-continuous loads.  

 

This is stated, for instance, in NEC 210.19 for minimum ampacity of branch
circuit conductor.  “Continuous Load” is in the definitions (Art. 100) as:

 

Continuous Load. A load where the maximum current is expected to continue
for 3 hours or more.

 

Likewise, in the Canadian Electrical Code, Part I, Rule 8-104, maximum
circuit loading is 80% of the rating of the circuit where a fused switch or
circuit breaker is marked for continuous operation at 80% of the ampere
rating of its overcurrent devices (or is unmarked per Appendix B).  A
continuous load is defined in that same rule as:

 

(3) The calculated load in a consumer’s service, feeder, or branch circuit
shall be considered a continuous load unless it can be shown that in normal
operation it will not persist for

(a) a total of more than 1 h in any two-hour period if the load does not
exceed 225 A; or

(b) a total of more than 3 h in any six-hour period if the load exceeds 225
A.

 

Except for the definitions of continuous loads, the requirements are
essentially the same in the US and Canada (though they are stated as
reciprocals in one country versus the other).

 

An easy example to demonstrate continuous and non-continuous loads would be
to compare a standard electric heater to a blow dryer.  The standard
electrical heater plugs into a 120V ac, 15 A receptacle, and is considered a
continuous load.  It is never rated more than 1500W.  Roughly this equates
to 12 A current at 120 V ac, or 80% of the 15 A nominal circuit rating (12.5
actually, but you are normally allowed to exceed the current rating by no
more than 10%).  Blow dryers that plug into 120 V ac, 15 A outlets, on the
other hand, are often rated for up to 1800 W. which equates to a current of
15 A.  Why is this possible?  Because a blow dryer’s use is short-duty or
non-continuous, and will not be used for more than 3 hours in the US or for
more than 1 hour in a 2 hour period in Canada.

 

 

Best regards,

DON GIES 
ALCATEL-LUCENT
SENIOR PRODUCT COMPLIANCE ENGINEER
BELL LABS - GLOBAL PRODUCT COMPLIANCE LABORATORY
600-700 Mountain Avenue
Room 5B-104
Murray Hill, NJ 07974-0636 USA   
Phone: +1 908 582 5978
Fax: +1 908 582 0582
 <mailto:[email protected]> [email protected]

MEMBER, ALCATEL-LUCENT TECHNICAL ACADEMY

 

 

-----Original Message-----
From: Kunde, Brian [mailto:[email protected]] 
Sent: Wednesday, May 16, 2012 10:45 AM
To: [email protected]
Subject: Re: Circuit breakers in Europe

 

Since this topic has been brought up, I'm hoping you experts could clarify
the 80% rule for me for North America (don't forget Canada).

 

I was given the impression that the 80% rule (as we call it) applies to the
maximum continuous current of the plug rating regardless of whether there is
one receptacle or multiple receptacles on that circuit. A product can draw
100% the current rating of the plug for periods of time but not more than
80% average current or continuous current.

 

The reason for the rule is to avoid overheating in the plug/receptacle
connection.

 

Is this right or wrong?

 

So say I have a 30 amp plug on my product and it is wired into a dedicated
receptacle and circuit. My product can be rated and draw up to 30 amps but
it cannot draw more than 24 amps continuous. Correct?

 

If the product is wired direct without the plug/receptacle it can draw up to
100% of the circuit rating continuously. Correct?

 

Please confirm or clarify.

 

We gathered this information from CSA who inspects our products in Canada
and if we rate a product over 80% of the plug rating they require we also
provide an average current and/or continuous current rating for that
product.

 

Thank you.

 

The Other Brian

 

-----Original Message-----

From:  <mailto:[email protected]> [email protected]
<mailto:[mailto:[email protected]]> [mailto:[email protected]] On Behalf Of
Pete Perkins

Sent: Tuesday, May 15, 2012 6:07 PM

To:  <mailto:[email protected]> [email protected]

Subject: RE: [PSES] Circuit breakers in Europe

 

PSNet,

 

        One issue that I'm not sure has been reflected in this thread is
that the NA 80% restriction for utilization circuits is that it is assumed
that there will be a number of duplex plugs wired into each circuit, as
allowed by the NA code.  Therefore, any single product may not use the
entire rated current from the circuit (20A, for instance) but is limited
(80% = 16A) so that other products may be plugged into the same circuit with
out overloading that circuit.

 

        If a product uses the full, rated current from a circuit breaker
then that product must be wired to a 'dedicated ccircuit' meaning that an
electrician must be called to wire in a circuit with only one outlet (not a
duplex outlet) on that breaker. (After getting the required permit, it might
cost as much to wire a new circuit - if it is even possible - as many
commercial electronic products cost.)  It's pretty clear that customers do
not want to hire an electrician to wire a new circuit for a new product thus
the pressure to meet the 80% limit with the products.

 

        Industrial customers deal with rewiring to code better than
commercial or household folks do.

 

        Been there, done that.

 

:>)     br,     Pete

 

Peter E Perkins, PE

 

Principal Product Safety Engineer

 

PO Box 23427

 

Tigard, ORe  97281-3427

 

503/452-1201     fone/fax

 

 <mailto:[email protected]> [email protected]

 

 

 

-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to <
<mailto:[email protected]> [email protected]>

 

All emc-pstc postings are archived and searchable on the web at:

 <http://www.ieee-pses.org/emc-pstc.html>
http://www.ieee-pses.org/emc-pstc.html

 

Attachments are not permitted but the IEEE PSES Online Communities site at
<http://product-compliance.oc.ieee.org/>
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

 

Website:   <http://www.ieee-pses.org/> http://www.ieee-pses.org/

Instructions:   <http://listserv.ieee.org/request/user-guide.html>
http://listserv.ieee.org/request/user-guide.html

List rules:  <http://www.ieee-pses.org/listrules.html>
http://www.ieee-pses.org/listrules.html

 

For help, send mail to the list administrators:

Scott Douglas < <mailto:[email protected]> [email protected]>

Mike Cantwell < <mailto:[email protected]> [email protected]>

 

For policy questions, send mail to:

Jim Bacher:  < <mailto:[email protected]> [email protected]>

David Heald: < <mailto:[email protected]> [email protected]>

________________________________

 

LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this
by mistake, please destroy it and notify us of the error. Thank you.

 

-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to <
<mailto:[email protected]> [email protected]>

 

All emc-pstc postings are archived and searchable on the web at:

 <http://www.ieee-pses.org/emc-pstc.html>
http://www.ieee-pses.org/emc-pstc.html

 

Attachments are not permitted but the IEEE PSES Online Communities site at
<http://product-compliance.oc.ieee.org/>
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

 

Website:   <http://www.ieee-pses.org/> http://www.ieee-pses.org/

Instructions:   <http://listserv.ieee.org/request/user-guide.html>
http://listserv.ieee.org/request/user-guide.html

List rules:  <http://www.ieee-pses.org/listrules.html>
http://www.ieee-pses.org/listrules.html

 

For help, send mail to the list administrators:

Scott Douglas < <mailto:[email protected]> [email protected]>

Mike Cantwell < <mailto:[email protected]> [email protected]>

 

For policy questions, send mail to:

Jim Bacher:  < <mailto:[email protected]> [email protected]>

David Heald: < <mailto:[email protected]> [email protected]>

  _____  


LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this
by mistake, please destroy it and notify us of the error. Thank you. 


-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to